Topic: Roof Heat Tape tripping Breaker

User: scarroll, Location: Park City, UT

Asked on: Sunday, October 20, 2024 at 2:42 pm EDT
Answered on: Thursday, March 6, 2025 at 4:12 am EST

Question: Just moved into a house and while the inspection didn't catch this issue (roof was dry during inspection) we just had a first snow so I turned on the heat tape to see if it all was working. the breaker immediately buzzed and tripped. two 20A breakers are dedicated to the system and there are two lighted switches on the wall to turn on the system.I'd love to hear advice on how to go about finding the problem. . .

Okay, a tripping breaker on a dedicated heat tape circuit after the first snow is a common and frustrating problem. Here's a breakdown of how to troubleshoot the issue systematically and safely

1. Safety First!
Turn off the breakers. Before doing anything else, turn both 20A breakers serving the heat tape circuits completely OFF at the breaker panel. Double-check with a voltage tester to confirm the circuits are de-energized at the switch locations. Work in dry conditions. Don't work in the rain or snow if possible. Electricity and water don't mix.2. Understand the System How many Heat Tape Runs? Are there two runs of heat tape? One for each switch? How old is the Heat Tape? Heat tape has a lifespan. If it's been installed for many years, the insulation can degrade, leading to shorts. What type of Heat Tape? There are several types: constant wattage, self-regulating, and mineral-insulated. Self-regulating is the most common. Total length of Heat Tape? This is critical for calculating the expected current draw (see step 5).3. Visual Inspection Inspect the Heat Tape Runs

Carefully examine the entire length of the heat tape (as much as you can access safely from the ground or with a ladder). Look for:

Physical damage

Cuts, cracks, abrasions, melted spots, or kinks in the heat tape.

Water intrusion

Areas where water might be getting inside the heat tape.


Overlapping

Heat tape should never overlap itself, especially with constant wattage heat tape. This creates a concentrated heat buildup and can cause a fire.

Proper installation

Is the heat tape properly attached to the roof/gutters? Is it making good contact? Is it properly spaced according to the manufacturer's instructions?


End caps

Inspect the end caps of the heat tape. Are they properly sealed and intact? A damaged or missing end cap is a common entry point for water.

Inspect the Connections

Check the wiring connections at the switches. Are they tight and secure? Look for any signs of corrosion or loose wires. Check the connections at the breaker panel. Are the wires securely attached to the breakers?

Inspect the Switches

Look for any signs of damage or overheating on the switches themselves.

Inspect the Wiring

Look at the wiring between the switch and the heat tape power cable. Look for damage to the insulation.

4. Initial Tests with the Breakers OFF
Continuity Test (Heat Tape Circuit)

Disconnect the heat tape from the wiring at the connection point near the switch (safely isolate the heat tape runs). Using a multimeter set to continuity (or resistance), test each heat tape run individually.

Test 1: Center core to outer jacket

Place one multimeter lead on one of the wires of the heat tape (the core) and the other lead on the metal or plastic sheathing surrounding the heat tape (outer jacket). You should
not have continuity (infinite resistance). Continuity indicates a short circuit to ground.

Test 2: Core to Core

Place one multimeter lead on one wire of the heat tape (the core) and the other lead on the other wire of the heat tape (the core). You should have continuity, but low ohms of resistance. If there is no continuity, you have a break in the wire.

5. Calculate Expected Current Draw (Amperage)
Find the Heat Tape Specs

The most crucial step. Find the manufacturer's information for your heat tape model. Look for the
watts per foot rating. This information is essential for calculating the expected current draw. It might be printed on the heat tape itself.

Calculate Total Wattage

Multiply the watts per foot by the total length (in feet) of each heat tape run.

Calculate Amperage

Divide the total wattage by the voltage (120V in most US residential circuits). `Amperage (Amps) = Wattage / Voltage`


Compare to Breaker Size

The calculated amperage should be significantly less than the 20A breaker rating. A general rule of thumb is to load a circuit to no more than 80% of its breaker rating. So, for a 20A breaker, the continuous load should be no more than 16A. If your calculated amperage is close to or exceeds 16A for each circuit, that's a problem. You may have too much heat tape on one circuit.

Example

Heat Tape: 5 watts per foot Heat Tape Length: 100 feet Total Wattage: 5 watts/foot 100 feet = 500 watts Amperage: 500 watts / 120 volts = 4.17 amps

6. Testing with the Breakers ON (Proceed with Extreme Caution!)
Only after completing steps 3-5 and addressing any identified issues. Start with One Circuit

Turn on
only one of the 20A breakers. Observe carefully. Does it trip immediately? Does it trip after a few seconds or minutes?

Clamp Meter

Use a clamp meter (ammeter) to measure the actual current draw on the circuit. Clamp the meter around one of the wires feeding the heat tape (not both – that will give you a zero reading). Compare the measured current draw to your calculated amperage. If it's significantly higher than expected, there's still a problem.

Repeat for the Second Circuit

If the first circuit appears to be working correctly, turn it off and repeat the testing process with the second circuit.

Common Problems and Solutions



Short Circuit to Ground

Water intrusion is the most common cause. Replace damaged heat tape. Ensure end caps are properly sealed.

Too Much Heat Tape on a Circuit

Reduce the length of heat tape on each circuit. You may need to add a new dedicated circuit.


Damaged Heat Tape

Replace the damaged section or the entire run.

Faulty Switch

Replace the switch.


Loose Wiring Connections

Tighten all connections.

Faulty Breaker

This is less common, but it's possible. If you've ruled out everything else, try replacing the breaker.


GFCI Protection

If you're using a GFCI breaker, nuisance tripping can occur due to the inherent leakage current in heat tape. Consider a standard breaker (but only if the heat tape is not required to be GFCI protected by code - check with a qualified electrician).

Important Considerations



Local Codes

Check your local electrical codes. There may be specific requirements for heat tape installation, including GFCI protection.


Professional Help

If you are not comfortable working with electricity, or if you cannot diagnose the problem, hire a qualified electrician. Electricity is dangerous.*

Heat Tape Installation Instructions

Always follow the heat tape manufacturer's installation instructions.

Troubleshooting Checklist


Safety First!
Breakers OFF.2. Visual Inspection (Heat Tape, Connections, Switches).
3. Continuity Tests (Heat Tape – Core to Jacket and Core to Core).4. Calculate Expected Amperage.
5. Test with One Breaker ON (Clamp Meter).6. Address Any Identified Issues.
7. Consult a Professional if Needed.By systematically working through these steps, you should be able to identify the cause of the tripping breaker and get your heat tape system working safely and effectively. Good luck! Flag for review