User: Grouch1980, Location: New York, NY
Asked on: Sunday, October 20, 2024 at 11:37 pm EDT
Answered on: Thursday, March 6, 2025 at 4:12 am EST
Question: Charlie has a great explanation on harmonics in Post #9 in the following thread:Delta and 3rd harmonicsRemembering that you used to remember... I recall that there was a derivation of the benefits of using a delta connection to reduce/eliminate 3rd harmonics. It's probably next to my car keys and a couple of unpaid bills... Does anyone recall or can name the reference? Thanks. Matt
Okay, I need the content of Charlie's Post #9 to help you further. However, based on the question in the thread and your request, I can provide some general information about the delta connection and its relationship to third harmonics
General Explanation of Delta Connections and Third Harmonics:
Third Harmonic Frequencies
Third harmonics (and odd harmonics in general: 3rd, 5th, 7th, etc.) are common in power systems due to non-linear loads (such as electronic devices, some lighting, and saturated magnetic cores in transformers). A third harmonic has a frequency that is three times the fundamental frequency (e.g., 180 Hz in a 60 Hz system).
Why Third Harmonics are a Problem
Overheating
Harmonics cause increased current and voltage distortion in the system, leading to overheating of transformers, conductors, and other equipment.
Nuisance Tripping
Can cause protective devices to trip unexpectedly.
Equipment Malfunction
Can interfere with sensitive electronic equipment.
Telephone Interference
Can induce noise in communication circuits.
Delta Connection's Role
Third Harmonic Circulation
The key advantage of a delta connection is that it provides a closed path for the circulation of third harmonic currents within the delta winding itself.
How it Works
Imagine three single-phase sources (or three windings of a transformer). In a delta connection, these sources are connected in a closed loop. If each source has a third harmonic component, these components are in phase with each other within the delta. This is because the phase shift of a third harmonic is 3x the fundamental phase shift. So, if the fundamental is shifted by 120 degrees, the third harmonic is shifted by 3x120 = 360 degrees (which is effectively 0 degrees). Since they are in phase, they add up. The delta winding acts as a short circuit for these in-phase third harmonic currents.
Suppression, Not Elimination
Importantly, the delta connection doesn't eliminate the generation of third harmonics. Instead, it suppresses their propagation into the rest of the power system by providing a low impedance path for them to circulate internally. The energy associated with these circulating currents is dissipated as heat in the windings.
Why a Wye Connection Doesn't Work the Same Way
In a wye (star) connection with a neutral, third harmonic currents will flow along the neutral conductor to the source. If there is no neutral conductor the third harmonic currents are forced to flow through the system impedance, which will cause large voltage distortions.
Applications
Delta connections are often used on the primary side of transformers to block third harmonics from entering the utility grid. A wye connection (with a neutral) is then used on the secondary side to provide single phase loads with a clean voltage waveform. Delta connections are also used in motor windings, for example, to reduce the generation of harmonic currents.
In summary
The delta connection is beneficial because it allows third harmonic currents to circulate within the winding, preventing them from propagating through the rest of the power system, which can lead to a reduction of voltage distortion and overheating.
What I need from you for further assistance:
Please provide the content of Charlie's Post #9. Once I have that, I can analyze it and give you a more specific and helpful explanation. Flag for review