User: Will Wire, Location: California: NEC 2020
Asked on: Monday, October 21, 2024 at 8:04 pm EDT
Answered on: Thursday, March 6, 2025 at 4:15 am EST
Question: I recently got a call about an old GE Service Panel on a house built in 1959. The dead front has four separate 2-Pole breaker knockouts. Two of the 2-Pole breaker spots are on the top and labeled #1 and #2, The other two 2-Pole breaker spots are below and labeled 3,4,5,6 and 7,8,9,10, presumably for 2-Pole, Single Pole, or Twin breakers. There is not a main breaker.Is anyone familiar with this old GE Service panel, and knows what it's amp rating is?Thanks
Okay, let's break down what you're describing. You've got an older GE service panel, likely dating back to the late 1950s or early 1960s. The fact that it doesn't have a main breaker and has those specific breaker configurations is a key characteristic.Here's what we can infer and how to figure out the amp rating
Key Characteristics:
No Main Breaker
This is significant. Service panels without a main breaker were common in older installations. The ampacity of the service would be determined by the service entrance conductors and the load calculation.
Two Top 2-Pole Spaces (Labeled #1 and #2)
These are for dedicated 240V circuits. The breakers could be 30A, 40A, 50A, or even higher, depending on what they were feeding (e.g., electric range, water heater, AC).
Two Bottom Multi-Space Sections (Labeled 3-10)
These are the workhorses of the panel. The specific numbering implies flexibility:
2-Pole
A double-width breaker could take up positions 3&4, 5&6, 7&8, or 9&10.
Single-Pole
You could have individual circuits on positions 3, 4, 5, 6, 7, 8, 9, or 10.
Twin (Tandem) Breakers
It might be possible to use tandem breakers in some of those slots (allowing two circuits in a single space), but this depends on whether the panel is designed for it.
Important
Do not automatically assume it's okay to use tandem breakers. Using them in a panel not designed for them is a code violation and a safety hazard.
Determining the Amp Rating
Here's the problem: There's no easy, foolproof way to determine the exact amp rating of the service panel just from the information you've provided. Unlike modern panels, older panels often didn't have a clearly marked ampacity rating on the dead front or inside.
Here's what you MUST DO
Inspect the Service Entrance Conductors
This is the most reliable method.
Location
The service entrance conductors are the large wires that come from the electric meter (or underground feed) and connect to the panel.
Size
Determine the gauge (thickness) and material (copper or aluminum) of these wires.
Ampacity Chart
Consult a National Electrical Code (NEC) ampacity table to determine the maximum allowable ampacity for those conductors based on their size and insulation type. This will give you the maximum potential service ampacity. A good starting point is NEC Table 310.16 (look it up online). Remember to account for the conductor insulation type (e.g., THHN, THWN, etc.)2.
Look for Any Markings Inside the Panel
Carefully examine the inside of the panel (with the power OFF and proper safety precautions). Look for a sticker or stamp that might indicate the ampacity. It could be on the back of the dead front or on the panel enclosure itself. Look for any other identifying information such as the model number. If you find a model number search the Internet for specs on this older GE panel.3.
Load Calculation (Most Accurate, Requires Expertise)
The most accurate way to determine the appropriate service size is to perform a load calculation for the house according to the NEC. This takes into account all the connected loads (lighting, appliances, heating/cooling, etc.) and applies demand factors to estimate the actual maximum load the service will experience. This requires a qualified electrician.
Important Considerations & Warnings
Safety First
Always work on electrical panels with the power completely OFF. If you're not comfortable or experienced working with electricity, hire a qualified electrician. Electricity can be lethal.
Panel Condition
Given the age of the panel, carefully inspect it for any signs of:
Rust or Corrosion
This can compromise the integrity of the panel and its components.
Overheating
Look for discolored or melted insulation on wires or breakers.
Loose Connections
Loose connections can cause arcing and fires.
Damaged Breakers
If breakers are physically damaged or don't trip properly, they need to be replaced.
Code Compliance
The electrical code has changed significantly since 1959. Even if the panel was compliant back then, it might not meet current code requirements.
Insurance
Many insurance companies require electrical systems to be up to code. An older panel like this might raise concerns.
General Guesses (But Don't Rely On These!)
Based on the age and configuration, it could be a 100 amp service. It's unlikely to be higher unless the wiring is significantly oversized, but without seeing the wire size and any markings, this is just speculation. It could be a 60 amp service, which was very common in older homes.
In SummaryYou cannot reliably determine the service ampacity without inspecting the service entrance conductors and/or performing a load calculation. Call a licensed electrician to perform the load calculation and inspect the panel for you. The electrician should be able to advise you on the best course of action regarding the panel. Flag for review