Topic: Separate grounding system

User: joshfromoshoto, Location: Wyoming

Asked on: Monday, October 21, 2024 at 11:07 pm EDT
Answered on: Thursday, March 6, 2025 at 4:15 am EST

Question: This may seem like a dumb question, but I am unable to test it. Will you read voltage from a hot leg, to a completely separate grounding system or neutral? My thought is say you were to drive a ground rod and not bond it to anything, if you were to put voltage to the ground rod it would not cause an arc nor would it likely trip any breaker, and from the hot leg to the ground rod you shouldn’t show any voltage. But if we take it further and have an entirely separate grounding system, not bonded at any point to the source voltage would the voltage read on a meter?

That's not a dumb question at all! It gets into some fundamental electrical concepts. The answer is nuanced and depends on several factors. Let's break it down

Understanding the Key Concepts
Hot Leg (Line)

This carries the electrical potential (voltage) from the power source (transformer).


Neutral

In a typical residential power system (split-phase), the neutral is the return path for current and is bonded to ground at the service entrance (and often at the transformer).

Grounding System

This is a network of grounding electrodes (ground rods, ground plates, etc.) and conductors designed to provide a low-impedance path to earth. Its primary purpose is safety – to provide a path for fault current to flow in case of a short circuit, allowing overcurrent protection devices (breakers or fuses) to trip.


Bonding

This is connecting metallic parts of a system (enclosures, conduit, etc.) to the grounding system to ensure they are at the same electrical potential, minimizing shock hazards.

Voltage

A difference in electrical potential between two points. A voltmeter measures this difference.


Impedance

Opposition to the flow of alternating current (AC). This is a combination of resistance, capacitance, and inductance.

Scenario 1: Hot Leg to an Isolated (Unbonded) Ground Rod
Will it cause an arc? Highly unlikely in most situations. An arc needs a substantial current flow. Without a return path (i.e., a low-impedance connection back to the source neutral), the current will be very limited. Will it trip a breaker? No, because there's practically no return path for the current. A breaker trips when there's an overcurrent condition. Will you read voltage? Potentially, YES, but it will likely be a very low and unstable reading. Here's why: Capacitive Coupling

There's always some level of capacitive coupling between conductors and the earth, and between the hot wire and the ground rod. This coupling acts like a very tiny capacitor, allowing a tiny amount of AC current to flow. Your voltmeter is a very high-impedance device. It requires very little current to register a voltage. The tiny current flowing through the capacitive coupling will be enough for the Voltmeter to register a Voltage.

Stray Voltages

There can be other sources of voltage in the environment (radio frequency interference, static electricity, etc.) that could influence the reading.


Dirty Ground

The earth itself isn't a perfect conductor. There are variations in soil conductivity that can lead to slight voltage differences between different points in the earth.

Leakage Current

There may be slight leakage current from the hot wire due to insulation imperfections.


Important Note

The voltage reading is unreliable. The isolated ground rod is not a suitable reference point. A stable, reliable reading requires a low-impedance return path.

Scenario 2: Hot Leg to a Completely Separate, Unbonded Grounding System


This is similar to Scenario 1, but with the grounding system now potentially consisting of multiple electrodes and connected metal objects. Will it cause an arc? Even more unlikely than Scenario 1. Will it trip a breaker? No. Will you read voltage? Potentially, YES, for the same reasons as above, but the reading is still unreliable. The capacitive coupling effects and stray voltages will still be present. The grounding system, even if isolated, might accumulate some charge from the environment. The Voltage you might read is due to potential differences in the ground itself and capacitive coupling. It is NOT a safe or reliable reading.

Important Considerations and Dangers

Ungrounded Systems are Dangerous

This thought experiment highlights the importance of bonding and grounding. Ungrounded systems can allow voltages to float to dangerous levels, creating shock hazards.


Do Not Create Intentional Ungrounded Systems

It is extremely dangerous and a code violation to intentionally create an ungrounded electrical system.

Voltmeters are High-Impedance

A voltmeter requires very little current to display a voltage reading. A reading on a voltmeter does NOT necessarily mean that a circuit can deliver significant power.

In Summary
While you might* read a voltage between a hot leg and an isolated grounding system (or an unbonded ground rod), the reading would be unreliable and likely very low. The key takeaway is that a properly grounded and bonded system is essential for safety and reliable operation. The purpose of grounding is to provide a low impedance path back to the source neutral, allowing overcurrent protection devices to trip in the event of a fault. Without that, the fault current will be limited, preventing the breaker from tripping and creating a potential shock hazard. Flag for review