Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: emt spaced off exterior of commercial building?

User: croyfish, Location: lake station, IN

Asked on: Monday, October 21, 2024 at 11:23 pm EDT
Answered on: Thursday, March 6, 2025 at 4:15 am EST

Question: had a buddy call me saying his boss chewed him out because he installed EMT on an exterior wall of a commercial building and secured the EMT with 1 hole straps. his boss said it was against code because moisture would build up between the wall and the EMT and cause issues. I've looked through article 110, 300, and 358 and found nothing stating such a thing. has anyone around the Chicagoland area heard of such a thing and if so can you provide the code reference or atleast the location of this information.

You are correct, there is no specific code in the NEC that outright prohibits using EMT with one-hole straps on exterior walls due to moisture buildup. Your buddy's boss is likely operating under a combination of best practices, local amendments, and possibly incorrect assumptions. Here's a breakdown of the likely reasoning and where you might find supporting information

Why the Boss Might Be Concerned (Even if not explicitly code):
Corrosion

While EMT is galvanized, prolonged exposure to moisture, especially if the galvanization is damaged, can lead to rust. Trapped moisture between the EMT and the wall, combined with temperature fluctuations, could accelerate this process. This is especially true in Chicagoland with its harsh winters.


Aesthetics

Some owners and inspectors frown on EMT running exposed on exterior walls. It can be seen as visually unappealing, especially on a commercial building. While not a code issue per se, it can lead to rework demands.

Potential for Damage

EMT, especially when secured with only one-hole straps, is more vulnerable to physical damage on an exterior wall. Things like weather, landscaping equipment, or accidental impact can damage the conduit.


"Workmanlike Manner" (NEC 110.12)

While vague, this section is often used to justify demands for neat and professional installations. A poorly supported EMT run on an exterior wall could be argued as not being installed in a workmanlike manner, especially if corrosion is likely.

Where the Boss Might Be Getting Some Basis (Even if It's a Stretch)



Local Amendments



This is the most likely culprit.
Many jurisdictions, including those around Chicago, adopt and amend the NEC. It is possible that the local jurisdiction has an amendment specifically addressing exterior EMT installations. Your buddy and you need to check with the local electrical inspector or building department to see if there are any local amendments to the NEC that address this issue. Call the AHJ (Authority Having Jurisdiction). Manufacturer's Instructions

Some manufacturers of EMT and associated fittings may provide specific instructions or recommendations regarding installation practices, including spacing of supports and suitability for exterior use. While not code itself, these instructions can influence interpretations.

Engineering Judgement/Best Practices

Some engineers and experienced electricians develop their own best practices based on their knowledge of local conditions and past experiences. The boss might be operating under such a principle.


300.6 Protection Against Corrosion

While this section doesn't specifically mention EMT on exterior walls, it does require raceways to be suitable for the environment. The boss might argue that using only one-hole straps in a high-moisture environment doesn't adequately protect the EMT from corrosion.

314.15 Damp, Wet, or Hazardous (Classified) Locations

This section deals with boxes, conduits and fittings in damp or wet locations and requires that they are approved for those locations. The boss may be arguing that the connection to the box is exposed and susceptible to water ingress, requiring a watertight fitting.

What to Do


Check Local Amendments

This is the most important step. Contact the local electrical inspector or building department in the specific jurisdiction where the building is located and ask about any amendments related to exterior EMT installations.2.

Ask the Boss for the Code Reference

Politely ask the boss to provide the specific code reference that prohibits the installation. This will force him to either produce a valid code or admit he's operating on something else.3.

Review Manufacturer's Instructions

Check the manufacturer's documentation for the EMT and fittings being used.4.

Document Everything

Keep a record of all conversations, research, and findings.5.

Consider Alternatives (If Possible)

If the issue is aesthetic or related to potential damage, consider suggesting alternative wiring methods like:


Rigid Metal Conduit (RMC)

More durable and corrosion-resistant than EMT.

Liquidtight Flexible Metal Conduit (LFMC)

Provides a flexible, watertight raceway.


PVC Conduit

Non-metallic and resistant to corrosion.*

Wiring inside the building

Run the wire inside the building and penetrate the wall at the last moment. This will reduce the exposed length of the wire and thus reduce the liklihood of damage.6.

Diplomacy

Try to resolve the issue amicably. If the boss is adamant, and there's no clear code violation, sometimes it's easier to just comply to avoid further conflict, especially if it's not a major expense or safety concern.

In summary, there's likely no direct NEC code violation. The boss's concerns are probably based on a combination of local practices, potential for corrosion, aesthetics, and a desire for a more robust installation. The key is to research local amendments and engage in a respectful conversation to find a solution.
Flag for review

Previous Question Next Question