User: Tainted, Location: New York
Asked on: Tuesday, October 22, 2024 at 8:26 am EDT
Answered on: Thursday, March 6, 2025 at 4:16 am EST
Question: In NYC we are stuck with 2008 NEC with amendments.In the updated code 310.15(B)(2)(a) exception it says "Adjustment factors shall not apply to conductors in racewayshaving a length not exceeding 600 mm (24 in.)."However in the 2008 NEC it does not say that. It only gives the exception for nipples and not raceways specifically: "Exception No. 3: Derating factors shall not apply to conductors in nipples having a length not exceeding 600 mm (24 in.)."If I'm under the 2008 NEC, does this mean I still have to derate wires that are less than 24 inches in the raceway?
Yes, you are correct. Under the 2008 NEC, with the wording "Exception No. 3: Derating factors shall not apply to conductors in nipples having a length not exceeding 600 mm (24 in.)," you do need to apply derating factors to conductors in raceways shorter than 24 inches unless those raceways specifically qualify as nipples as defined in the NEC.The critical difference is the word "nipples" versus the broader term "raceways". In the 2008 NEC, the exception is very specific to nipples.
Why this matters
Nipple Definition
A nipple is a short section of conduit (usually rigid metal conduit) used for connecting enclosures, boxes, or other equipment together. It's generally understood to be used for physical protection and connection between devices that are very close together.
Raceway vs. Nipple
A raceway is a general term encompassing many types of channels designed to hold wires (conduit, wireways, etc.). Not all raceways are nipples. Think of a 2-foot section of EMT running between two pull boxes – that's a raceway, but likely not a nipple in the commonly understood sense.
In Summary:
If the raceway is specifically a nipple (meeting the common understanding of its use and likely being rigid metal conduit), then you don't need to derate under 2008 NEC exception 3. If the raceway is any other type (e.g., EMT, PVC, wireway), even if it's less than 24 inches, you do need to apply ampacity adjustment factors (derating) based on the number of current-carrying conductors within it.Therefore, be very careful if you are using a raceway that is NOT a nipple. You WILL need to derate the wire. Flag for review