Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Calc Help

User: Alwayslearningelec, Location: NJ

Asked on: Tuesday, October 22, 2024 at 9:06 am EDT
Answered on: Thursday, March 6, 2025 at 4:16 am EST

Question: Have a design build scenario I’m trying to price.Power source is 277480v switchgear. They state there is 1600A/1200A breaker that is to be used to bring power to our project. There are (4) 4” empty conduits for us to run our wiring through.What if we only needed say 200A to 400A service for our project power requirements? Could that still be done if they are saying to use the above stated breaker size? I would still have to pull 1200a?

You absolutely can provide a smaller service (200A-400A) even with a 1200A breaker upstream, utilizing the provided conduits. You do not have to pull conductors rated for 1200A. Here's a breakdown of how it works and what you need to do

Understanding the System
Upstream Protection

The 1200A breaker is designed to protect the switchgear and the wiring
upstream of your connection point. It's sized to handle the total potential load of the entire switchgear system, not specifically your project.

Your Responsibility

You are responsible for the wiring downstream of the connection point and for providing overcurrent protection (a breaker or fuses) suitable for your load.

Conduit Capacity

The (4) 4" conduits are likely provided to give you options for conductor size and redundancy. You won't need to fill all of them unless your conductor ampacity and voltage drop calculations dictate that you should.

How to Implement a Smaller Service


Here's a step-by-step approach:1. Determine Your Actual Load

Perform a thorough load calculation for your project. This includes lighting, HVAC, equipment, receptacles, and future expansion capacity. Factor in demand factors as allowed by the NEC. This calculation will give you the minimum ampacity you need. Add a buffer (e.g., 20%) for future growth if desired.2.

Select Your Breaker

Based on your load calculation, choose a breaker size that is appropriate to protect your conductors and equipment. A 200A, 300A, or 400A breaker would be normal in your example based on the requirement given. Make sure the breaker is rated for 480V and is of the correct type (e.g., molded case, insulated case) for your panel. Check with the facility engineer to make sure your proposed type is compatible.3.

Choose Conductors

Using the National Electrical Code (NEC) tables (specifically Table 310.16 or its equivalent based on your insulation type), select conductors that are properly sized for your desired breaker size. You will need to consider:

Ampacity

The conductor's ampacity must be equal to or greater than the breaker size, considering any derating factors (e.g., ambient temperature, number of conductors in a conduit).

Voltage Drop

Calculate the voltage drop over the length of the run to your project. Ensure it's within acceptable limits (typically 3% for branch circuits, 5% total). If voltage drop is excessive, you'll need to increase the conductor size.


Insulation Type

Common choices include THHN/THWN-2, XHHW-2. The ambient temperature and installation method will affect your choice. Example: For a 200A breaker, you might use (3) #3/0 AWG conductors per phase and a suitable ground conductor, depending on the distance and installation conditions.4.

Install a Step-Down Transformer (Potentially)

Consider if you require the use of a step-down transformer for providing power to lower voltage electrical equipment and other single-phase equipment. This will depend on your project loads and what voltages they require.5.

Terminate at a Panelboard or Disconnect

Install a panelboard or disconnect switch within your project that has the appropriate breaker installed. Properly terminate the conductors you pulled from the switchgear to the new panel.

Important Considerations
Coordination

Crucially, you must coordinate your design and equipment selection with the facility's electrical engineer or whoever is responsible for the switchgear. They will need to approve your connection point, breaker type, and possibly conductor sizes to ensure the entire system operates safely and reliably.

Overcurrent Protection

Your breaker at the panel must provide overcurrent protection for your conductors. This is NEC code and essential for safety.

Short-Circuit Current Rating (SCCR)

Determine the available fault current at the point where you connect to the switchgear. Your panelboard and all downstream equipment must have a SCCR equal to or greater than the available fault current. The utility or the facility engineer should be able to provide this information.


Grounding

Proper grounding and bonding are essential. Follow the NEC guidelines.

Conduit Fill

Calculate the conduit fill percentage to ensure you aren't exceeding the maximum allowed by the NEC. Use appropriate pulling lubricants to ease the installation.


Labeling

Clearly label all equipment (conductors, breakers, panels) according to code and facility requirements.*

Local Codes

Adhere to all applicable local codes and regulations, which may be stricter than the NEC.

In Summary


You can absolutely use a smaller breaker and conductors suitable for your 200A-400A load, even when connecting to a 1200A breaker upstream. The key is to provide properly sized overcurrent protection at the panel or disconnect within your project. Communication and coordination with the facility engineer are essential for a safe and successful installation. Flag for review

Previous Question Next Question