Question: In this case the motor term box is being replaced since it’s undersized. The T leads and incoming feeder are 500kCMIL. A single 4” conduit enters the side of terminal boxI’m think the depth of the box is more important here according to 312.6, since the T leads come they the back of the box. So that would be one terminal per cable or 6” deep enclosure and height/width would still be 6x 4” or 24”Is this correct?
Let's break this down and clarify the requirements. You're dealing with a junction box (terminal box) for large conductors, and the key is understanding how the NEC applies in this situation.
Assumptions
You're referring to NEC Article 312 (Cabinets, Cutout Boxes, and Meter Socket Enclosures). While technically a motor terminal box could fall under 430 Part C, the emphasis on conductor size and termination points strongly suggests 312 is the primary concern. "T leads" are likely referring to the motor termination leads being connected to the incoming 500 kcmil feeder conductors within the box. There are three phases (A, B, C) entering and three motor leads that need to be spliced
Analysis
312.6 Minimum Wire Bending Space at Terminals
You are correct that 312.6 is crucial here. Specifically, 312.6(B) applies because you're dealing with conductors entering from the back of the enclosure, directly opposite the terminals. This is the `one terminal per conductor` scenario.
2.
Depth Calculation
Table 312.6(B) is your go-to. You need to determine the minimum bending space for one 500 kcmil conductor entering opposite the terminal. The wire type (THHN, XHHW, etc.) is important here. Let's assume it's THHN for now (check your conductor insulation type). Table 312.6(B) indicates a minimum bending space of 12 inches for one 500 kcmil conductor. Therefore, the minimum depth of your enclosure, based solely on conductor bending space per 312.6(B) is 12 inches. Your initial thought of 6 inches is incorrect for 500 kcmil conductors.3. Width and Height Calculation (314.28)
While 312 is crucial, you've likely also got 314.28 (Pull and Junction Boxes and Conduit Bodies) in play, particularly 314.28(A)(1) for straight pulls. This section dictates the minimum dimensions based on the conduit size.
Straight Pulls
You have one 4" conduit entering and exiting on opposite walls of the box. Therefore, the minimum distance between raceway entries, where the raceways contain conductors of size No. 4 AWG or larger, shall not be less than eight times the trade diameter of the largest raceway. The minimum distance, for a straight pull, would be 8 X 4", or 32".
Angle or U Pulls
Since the conductors are coming from the back of the enclosure, there is a possibility for angle or U pulls. The minimum distance from the raceway entry to the opposite wall of the box shall not be less than six times the trade diameter of the largest raceway, plus the sum of the diameters of all other raceways on the same wall or row. This is 6 X 4", or 24", so it is not governing.
Raceway Diameter Considerations
Since all conduits are on the same wall, we only have to worry about the largest conduit which is 4" and has a diameter of 4".
Summary of Pullbox Dimension
Length
32" (From 314.28(A)(1) for straight pulls)
Width
While the straight pull calculation determines the length of the box, you still need adequate width. Consider the physical space needed to properly terminate the six 500 kcmil conductors (three feeders + three motor leads). 24" might be sufficient, but carefully assess the terminal spacing of your connectors and the overall layout.
Depth
12 inches (From Table 312.6(B) based on bending space).
4.
Important Considerations
Conductor Fill
Ensure the box has enough volume to meet conductor fill requirements (314.16). While the box might be large enough dimensionally, excessive conductor fill can still be a problem. This is often overlooked! You are splicing 6 X 500 kcmil conductors in the box, so conductor fill will be an issue.
Connectors
Use appropriately sized connectors rated for 500 kcmil conductors. Make sure they are UL-listed and suitable for the application. The physical size of these connectors contributes to the space required within the box.
Working Space
Don't forget working space around the enclosure (Article 110).
Manufacturer's Instructions
Always follow the manufacturer's instructions for the connectors and any other equipment being used.
Grounding
Ensure proper grounding and bonding of the enclosure and all equipment.
In Conclusion
Your initial assessment was partially correct, but incomplete. The depth is indeed crucial and is dictated by 312.6(B) and the bending space requirements. With 500 kcmil conductors, 12 inches of depth is a good starting point. But 314.28 (A)(1) mandates 32" of length for straight pulls. Remember to verify the conduit fill calculation in 314.16 and working clearance in Article 110.
Recommendation
Based on the information you've provided, a box that is at least 32 inches in length, 24 inches in width and 12 inches in depth is appropriate. A 36" X 24" X 12" pullbox would be a good choice.Before finalizing the box selection, create a detailed layout of the conductors, connectors, and conduit entries. Ensure everything fits comfortably, leaving adequate working space within the box. It's often a good idea to err on the side of a larger enclosure if space permits.
Disclaimer: Always consult with a qualified and licensed electrician for any electrical work. This response is for informational purposes only and should not be considered a substitute for professional advice. Flag for review