Topic: Min sizing of Motor Termination Box per NEC and or MG-1

User: Dale001289, Location: Georgia

Asked on: Wednesday, October 23, 2024 at 9:57 am EDT
Answered on: Thursday, March 6, 2025 at 4:18 am EST

Question: I've got a large induction 460V, 3Ph AC motor that is being fed by 3-1/C 600kCMIL cable. The motor term box from the Vendor seems to be vastly undersized. What is the best way to calculate the min size required

You're right to be concerned about an undersized motor terminal box. A too-small box can cause serious issues: Overheating

Inadequate space inhibits heat dissipation from terminations, leading to overheating, insulation breakdown, and potential failures.


Code Violations

The NEC (National Electrical Code) has specific requirements for box fill and conductor bending space. Violations can result in fines and safety hazards.

Installation Difficulties

Trying to cram large conductors into a small box makes connections difficult, increasing the risk of loose or improper terminations.


Reliability Issues

Poor connections and thermal stress reduce motor reliability and lifespan.Here's a breakdown of how to determine the minimum size required for your motor terminal box, incorporating NEC references:

1. Determine the Motor's Full Load Amps (FLA)



Motor Nameplate

This is the
primary source. Find the FLA directly on the motor nameplate for 460V, 3-phase.

NEC Table 430.250

If the nameplate is unavailable or illegible, use NEC Table 430.250 to look up the FLA based on the motor's horsepower and voltage. Be aware this is a general table, and the nameplate value always takes precedence.

2. Adjust FLA for Overcurrent Protection



NEC 430.52 (Motor Branch-Circuit Short-Circuit and Ground-Fault Protection)

Your branch-circuit protection device (circuit breaker or fuses) determines the maximum allowable conductor ampacity. This is
not necessarily the motor FLA. The size of the overcurrent protection device will determine the minimum conductor size. This is critical because larger overcurrent protection allows for larger conductors, which in turn necessitate a larger terminal box.

Motor Starting Method

Consider the motor starting method (e.g., across-the-line, reduced voltage). Reduced voltage starting methods may allow for smaller conductors, but you need to ensure that the motor is protected under all operating conditions.

3. Determine the Conductor Size



NEC Table 310.16 (Allowable Ampacities of Insulated Conductors)

Based on the adjusted FLA from Step 2, and taking into account the termination temperature rating on the motor, use Table 310.16 to determine the minimum conductor size. Your 600 kcmil is likely already sufficient, but confirm.



NEC 110.14(C)(1)

This section is
critical. Pay careful attention to the termination temperature rating of the motor terminals (typically 60°C or 75°C). You must use the corresponding column in Table 310.16. Using the 90°C column and assuming your terminations are rated for that temperature when they are not is a common and dangerous mistake. Use the lowest rated termination temperature for the conductor, motor terminal, and equipment. If the motor termination is rated for 75C, then you must use the 75C column in the NEC.

Derating Factors (NEC 310.15)

Apply derating factors if necessary, such as:

Ambient Temperature

If the ambient temperature is higher than 30°C (86°F), you must derate the conductor's ampacity.


Number of Conductors in a Raceway or Cable

If more than three current-carrying conductors are in a raceway or cable, you must derate the conductor's ampacity. In your case, you likely have only three, so this may not be a factor.

4. Calculate Minimum Box Size



NEC Article 314 (Outlet, Device, Pull, and Junction Boxes; Conduit Bodies; Fittings; and Manholes)

This is the
key section for determining box size. You'll be using these sections:

NEC 314.16(A) (Box Volume Calculations)

This section covers the volume of the box required based on the number and size of conductors and devices. You'll need to calculate the total volume required for:

Conductor Fill

Each conductor entering the box counts towards the fill requirement. Each conductor is counted once and is given a volume from

Table 314.16(B)(1). For example, a #6 AWG conductor requires a volume of 2.25 cubic inches. A 600 kcmil conductor will require 1500MCM 400 cubic inches


Conductor In, Conductor Out (Splices, etc.)

Each wire entering and exiting the box requires volume.

Devices (e.g., ground lugs)

Any devices inside the box also have a volume allowance.


Equipment Grounding Conductors

These also count towards the fill.

NEC 314.28(A) (Minimum Size)

This section is vital when dealing with large conductors (e.g., 4 AWG or larger). This section has to do with fitting larger conductors and bending them into the terminal box.


Straight Pulls

If the conductors enter one side of the box and exit directly opposite, the box length must be at least eight times the trade diameter of the largest raceway entering or leaving the box.

Angle or U Pulls

If the conductors enter one side of the box and exit from another side that makes an angle of 90 degrees or more, the distance from the raceway entry point to the opposite wall of the box must be at least
six times the trade diameter of the largest raceway, plus the sum of the diameters of all other raceways on the same wall of the box.

Conductor Bending Radius

NEC 314.24 requires conductors to be bent to the manufacturer's specifications. Ensure that the box provides enough room to accommodate the conductor's minimum bending radius without damaging the insulation.

5. Select a Suitable Box



Material

Choose a box material appropriate for the environment (e.g., steel for industrial settings, non-metallic for corrosive environments).


Construction

Ensure the box is robust enough to withstand the mechanical stresses of the installation.

Listing

The box
must be listed by a recognized testing laboratory (e.g., UL, ETL) and marked with its volume in cubic inches.

Dimensions

Check with the vendor the dimensions to ensure the box is capable of accommodating the conductors and all necessary components.

Practical Steps and Considerations


Gather Data

Collect the motor nameplate information, overcurrent protection device size, conductor type, termination temperature ratings, and any other relevant data.2.

Document Everything

Keep a detailed record of all calculations and code references. This is essential for inspections and future maintenance.3.

Consult the Manufacturer

Contact the motor manufacturer for guidance on their recommended terminal box size. They may have specific requirements or recommendations based on their design.4.

Oversize if Possible

When in doubt, err on the side of a larger box. It's better to have too much space than not enough. A larger box can also make future modifications easier.5.

Consider a Junction Box

If the motor terminal box is simply too small to accommodate the conductors, consider installing a separate junction box adjacent to the motor. This allows you to make the connections in a larger, more accessible space. This is a common practice.6.

Engineering Judgement

While the NEC provides minimum requirements, you should also use your engineering judgement to ensure a safe and reliable installation. Consider factors such as ease of maintenance, future expansion, and potential for conductor damage.7.

Local Codes and Regulations

Be aware of any local codes or regulations that may supplement or supersede the NEC.

Example (Simplified)

Let's say your 460V, 3-phase motor has an FLA of 100 amps. Your overcurrent protection device is sized at 125 amps. The motor terminals are rated for 75°C.1.

Conductor Sizing

Using NEC Table 310.16 (75°C column), you might select 1/0 AWG conductors (ampacity of 150 amps, assuming copper). Since you're using 600kcmil, you far exceed that requirement.
2.


Box Size

This is where it gets complex. You'd need to consider: The volume required for each 600 kcmil conductor entering the box. The volume required for grounding conductors. Any additional devices within the box. The raceway trade size. The pulling method (straight, angle, etc.).This calculation would likely dictate a very large terminal box or the need for a separate junction box. Because of the large conductor size, you will likely be most constrained by 314.28(A) which has to do with pulling the conductors in with adequate bending radius.

In summary, accurately calculating the minimum size for a motor terminal box involves a thorough understanding of the NEC and careful consideration of the specific motor and installation conditions. When dealing with large conductors like 600 kcmil, the bending radius requirements of NEC 314.28(A) often become the dominant factor in determining the minimum box size.
* If you're unsure, consult with a qualified electrical engineer. Flag for review