Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Residential load calculation placement

User: nizak, Location: Berkeley, CA

Asked on: Wednesday, October 23, 2024 at 10:01 am EDT
Answered on: Thursday, March 6, 2025 at 4:18 am EST

Question: Can the following loads be subject to de rating or should they be entered with their nameplate full load amps?- Lawn irrigation pump- Septic tank lift pump- Well pump- Sauna heat pumpAll off these are permanently connected items .Thank you

Generally, permanently connected motors like those you listed can and sometimes must be subjected to derating or have other considerations taken when calculating the load for electrical service and feeder sizing. You cannot simply use the nameplate full load amps (FLA) in all cases. Here's a breakdown: Lawn Irrigation Pump, Septic Tank Lift Pump, Well Pump



Continuous vs. Non-Continuous

The first, most important question is:

Are these loads considered continuous?
A continuous load is defined as a load where the maximum current is expected to continue for 3 hours or more. Non-Continuous

Most residential irrigation pumps, septic lift pumps, and well pumps operate
intermittently. They are cycled on and off by timers, float switches, or pressure switches. Because they usually do not run for 3 hours or more at a time, they are generally considered

non-continuous
loads. Continuous

It's possible these could be continuous if, for example, a commercial irrigation system ran nearly constantly, or a well pump had to run for hours to fill a large reservoir. However, for a typical residential application, they are likely non-continuous.

If Non-Continuous

For non-continuous motor loads, the NEC (National Electrical Code) generally allows you to use the nameplate FLA for load calculations, subject to the considerations below.


If Continuous

For continuous motor loads, NEC 210.20(A), 215.3, and 220.18 require that the branch circuit and feeder conductors be sized no less than 125% of the continuous load.

Largest Motor Rule

NEC 430.24 requires that when calculating feeder or service size, if you have multiple motors, the largest motor's FLA must be multiplied by 125% and added to the sum of the other motor loads. Even if a single motor is
not a continuous load on its own, its contribution to the feeder calculation is increased due to this rule if it's the largest motor.

Overload Protection

Motor overload protection (separate from short-circuit protection) must be provided. The specifics of this depend on the motor type (e.g., whether it has built-in thermal protection), but generally, overload protection is sized to protect the motor from running too hot due to an overload condition.

Locked-Rotor Amps (LRA)

For sizing the branch-circuit short-circuit protective device (fuse or circuit breaker), you will need to know the motor's LRA (Locked-Rotor Amps). This is the current the motor draws when it is first starting. The code allows for higher values of overcurrent protection to permit the motor to start without tripping the breaker due to the inrush current. The specific rules for LRA are in NEC 430.52. This is particularly important for pump motors, which can have high starting currents.


Voltage Drop

Consider voltage drop in the circuit conductors, especially for long runs. Pumps can be sensitive to voltage drop, which can reduce their performance and lifespan.

Sauna Heat Pump



Likely Continuous

A sauna heat pump is more likely to be considered a

continuous load
, especially if it's designed to maintain a high temperature for extended periods. 125% Rule

As a continuous load, NEC 210.20(A) mandates that the branch-circuit conductors and overcurrent protection be sized at 125% of the
continuous load.

Nameplate Ratings

Check the heat pump's nameplate carefully. It should list both the minimum circuit ampacity (MCA) and the maximum overcurrent protection (MOP) size. These values are provided by the manufacturer and often incorporate the 125% continuous load factor.

Manufacturer's Instructions

Always* follow the manufacturer's instructions for installation, including wiring and overcurrent protection.

In summary


Determine if the load is continuous (3 hours or more).
2. If continuous, apply the 125% factor.3. For feeder calculations, apply the "largest motor" rule (125% of the largest motor FLA, even if that individual motor is not continuous).4. Use the motor's LRA to select the appropriate branch-circuit short-circuit protective device.5. Ensure adequate overload protection for each motor.6. Consider voltage drop, especially for long runs to pumps.7. Follow the manufacturer's instructions for all equipment.Crucially, consult the National Electrical Code (NEC) and local codes, and consult with a qualified electrician to ensure your electrical installations are safe and compliant. This advice is for informational purposes only and should not be considered a substitute for professional electrical engineering services. Flag for review

Previous Question Next Question