Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Splash pad bonding

User: JoeBags, Location: 50317

Asked on: Wednesday, October 23, 2024 at 10:11 am EDT
Answered on: Thursday, March 6, 2025 at 4:18 am EST

Question: As I read 680, it is my understanding that we need a to bond to the rebar at only (4) locations, and add a conductor 24" in from the exterior perimeter of the pad, no matter the size of the splash pad. (Drive a ground rod and connect it to the rebar at each of these locations. Question is why would the number of connections increase based on the size of the splash pad?)

You're referring to NEC 680.26(B)(1)(b) regarding Equipotential Bonding for permanently installed swimming pools (and this would likely extend to splash pads due to the similar shock hazard). Let's break down the requirements and address your questions

NEC 680.26(B)(1)(b): Equipotential Bonding of the Perimeter Surface:
Bonding the Rebar

This section mandates that the reinforcing steel (rebar) of the pool (or splash pad) structure be bonded together to create an equipotential plane.


Minimum Four Points

The code explicitly states that the bonding connection to the rebar must be made at a minimum of four points spaced around the perimeter of the pool/splash pad. This is the "4 locations" you're referring to.

Supplemental Conductor

In addition to bonding the rebar, a solid copper conductor (minimum #8 AWG) must also be installed within the perimeter surface. This conductor has to be within the perimeter of the splash pad (but not directly underneath) and 18-24" from the inside wall of the splash pad perimeter.


Connection to Rebar

This supplemental conductor must be connected to the rebar at least every 10' maximum.

Purpose

The fundamental goal is to minimize voltage gradients within the splash pad area, preventing electric shock hazards.

Addressing Your Questions


Why 4 Connections, Regardless of Size?
The "minimum of four points" requirement is a baseline established by the NEC, to ensure the rebar is considered effectively bonded. Imagine if you only bonded in one location. There could be a significant voltage difference (voltage gradient) at the far end of the rebar network, particularly if the rebar is corroded or poorly connected in some areas. Four well-spaced connections help distribute the bonding effect more evenly across the structure. It's about creating redundancy and minimizing voltage differences.2. Why Would the Number of Connections (Specifically to the #8 supplemental conductor) Increase Based on the Size of the Splash Pad? Because of the 10' maximum separation requirement

The code requires the #8 AWG supplemental bonding conductor must be connected to the rebar grid every 10' maximum. So, for example, if your splash pad is 50' x 50' and the supplemental conductor runs all the way around the perimeter, you would need to bond the supplemental conductor to the rebar at 20 points (200'/10' = 20 connections).


Voltage Gradient Mitigation

Think of a very large splash pad. If you only had four connections to the rebar and a supplemental conductor (which is incorrect, the supplemental conductor must connect at least every 10'), a shock hazard could arise.

Larger Area = Higher Risk

A larger splash pad simply presents a larger area where voltage gradients could develop if not adequately bonded.3.

Ground Rods at Each Connection Point to the Rebar?
Not Required (and Potentially Problematic)

The NEC does not require driving a ground rod at each connection point to the rebar. In fact, driving multiple ground rods and connecting them to the rebar at every location is not recommended.

The Rebar is the Grounding Electrode

The rebar itself, when properly connected, acts as the
primary grounding electrode (encased electrode, per 250.52(A)(3)). It's already in contact with the earth over a large area.

Supplemental Electrodes (if Needed)

You may need a supplemental grounding electrode (e.g., ground rod, plate electrode) if the rebar is not considered sufficient for the grounding electrode system. This is determined based on other parts of the electrical system design (service entrance, grounding electrode conductor size, etc.). You generally only need one supplemental grounding electrode.

Why Multiple Ground Rods are Bad

Having multiple, independent ground rods connected to the same system can sometimes create circulating currents and potential differences, making the situation
worse, not better. It's generally best to have a single, well-established grounding electrode system.

In Summary

You must bond the rebar at a minimum of four locations. You must install a supplemental bonding conductor within the perimeter of the splash pad, 18-24" from the inside wall. You must connect the supplemental bonding conductor to the rebar at a maximum of 10' intervals. The total number of connections to the rebar depends on the size of the splash pad. You do not need to, and should not, install a ground rod at each rebar bonding connection. One supplemental grounding electrode is all that is required.

Important Recommendations


Consult with a Qualified Electrical Engineer or Inspector

Equipotential bonding can be complex. It is absolutely vital to consult with a qualified electrical engineer or local electrical inspector who is familiar with the latest NEC requirements and local codes before starting any work. They can assess your specific splash pad design and ensure that you meet all applicable regulations.2.

Thorough Documentation

Keep detailed records of all bonding connections, materials used, and test results (e.g., continuity testing) to demonstrate compliance with the code.3.

Understand Local Amendments:
Many jurisdictions have local amendments to the NEC. Always check with your local authorities to ensure you are meeting all requirements.Failure to properly bond the rebar and perimeter surfaces can create a serious and potentially fatal electric shock hazard. It is not an area to cut corners or guess. Get expert advice and follow the code to the letter. Flag for review

Previous Question Next Question