Topic: Strobes in a loop

User: JJWalecka, Location: New England

Asked on: Thursday, October 24, 2024 at 6:42 am EDT
Answered on: Thursday, March 6, 2025 at 4:20 am EST

Question: Trying to trace out the FA strobe loop. Is there another way figure out how many strobe's are in a loop beside just poking my head in the ceiling and following itThanks for your time

You're right, physically tracing a strobe loop can be a real pain! Here are a few alternative methods to figure out the number of strobes on a fire alarm loop, ranging from best-case scenario to troubleshooting

1. Best Case: As-Built Drawings and Documentation
Fire Alarm As-Built Drawings

These are the holy grail. They should show the entire fire alarm system layout, including the location of each device (including strobes), the wiring topology, and the loop identification. Look for riser diagrams that trace the circuits. The number of strobes on a given loop should be explicitly shown or easily counted.


Fire Alarm System Programming/Configuration Report

This report, generated from the fire alarm control panel (FACP) programming software, often lists all devices on the system, their addresses, loop assignments, and device types (including strobes). It might also include a total device count per loop.

Panel Documentation

Some panels will have documentation (paper or digital) that lists the addressable devices and loop information.


Fire Alarm Inspection and Testing Reports

These reports often contain information about the system's layout and device counts per loop, especially if the inspector meticulously documented the system.

2. Using the Fire Alarm Control Panel (FACP)



Panel Display/Information

Some modern FACPs can display device information, including the loop to which a device is connected and a total device count for each loop. Look for a "walk test" or "device listing" function in the panel's menu.


Download from the Panel

Some panels let you download the configuration information. You'll need the right software (usually proprietary to the FACP manufacturer) and a connection cable. This downloaded configuration can then be reviewed to see the number of strobes per loop.

3. Address Mapping and Deduction (requires some effort and assumptions)



Device Addressing Scheme

Fire alarm systems using addressable devices often follow a logical addressing scheme. If you understand the addressing scheme used in your system, you might be able to deduce the loop assignments based on the device addresses. For example, addresses 1-50 might be on loop 1, 51-100 on loop 2, etc. Knowing this can help you narrow down the possibilities.


Isolate Strobe Circuits

If you can isolate a circuit breaker powering a portion of the fire alarm system, and if that circuit powers only strobes, you might be able to get a count of the strobes on that isolated circuit.

CAUTION

Only do this if you are absolutely certain you won't disable critical fire alarm functions. And make sure to restore power immediately after your count.

Walk Test/Drill

During a walk test, activate each strobe individually and note its address. Then, by correlating the addresses with the panel's loop information (if you have it), you can build a list of strobes per loop.


Consulting a Fire Alarm Technician/Company

This is often the most reliable solution. A qualified fire alarm technician has the training, experience, and equipment to quickly identify the loop configuration and device counts. They'll also understand the specific nuances of the system you're working with.

Important Considerations and Cautions



NFPA 72 Limits

Keep in mind that there are limitations on the number of devices allowed on a single fire alarm loop, based on NFPA 72 (the National Fire Alarm Code) and the specific FACP's capabilities. The voltage drop of each device should also be considered when designing the loop.


Power Calculation

The strobe loop is a circuit, it will have a maximum capacity. Use the rated voltage of each strobe and the maximum current it pulls, find the VA. VA = VI

Tampering

Do not tamper with the fire alarm system in a way that could compromise its functionality or create a false alarm. Always follow proper safety procedures.

Documentation is Key

If you discover discrepancies or missing information, update the fire alarm documentation to reflect the actual system configuration.


Licensed Professionals

Some fire alarm work requires licensing and certification. Ensure you are qualified to perform the task or hire a qualified professional.

In summary, start with the documentation. If that's not available, the FACP itself might offer clues. If all else fails, consult a fire alarm technician. Safety and accuracy are paramount.
Flag for review