User: Aistobasbistoc9, Location: Texas
Asked on: Thursday, October 24, 2024 at 9:49 am EDT
Answered on: Thursday, March 6, 2025 at 4:20 am EST
Question: I am curious as to whether I should apply Table 310.15(B)(3)(a) to the load on a feeder for a bussed gutter system. I have 2 sets of (4)#350 and the bussed gutter is estimated at a demand load of 560A for a 600A service. The calculations for the demand load on the individual panels on this service were done per NEC. The continuous loads were calculated at 1.25, the non-continuous loads were calculated at 1.00, etc.With that table, I would cap the full calculated demand load at about 488A (80%), correct? Do I assume that all 4 feeders are carrying current, including the neutral because it is most likely a non-linear load?Thank you
Okay, let's break down whether you can apply Table 310.15(B)(3)(a) (formerly Table 310.16 Note 5) to your bussed gutter feeder situation.
Understanding the Table 310.15(B)(3)(a) Rule (Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway or Cable)
This table is designed to reduce the ampacity of conductors when they are bundled together in a way that prevents efficient heat dissipation. The more conductors carrying current in close proximity, the greater the reduction.
Here's the critical part
The table applies when you have multiple current-carrying conductors in a raceway or cable.
Your Situation: Bussed Gutter
A bussed gutter (wireway) is not the same as a conduit or cable. Wireways are designed to provide more space and better ventilation than conduits. While you have multiple conductors inside the wireway, the conditions are generally less restrictive than in a tightly packed conduit.
Analysis and Application
Are the conductors in a raceway or cable? No. You're using a bussed gutter/wireway.2. Does 310.15(B)(3)(a) apply? Generally, no, it does not automatically apply just because you have multiple conductors in the wireway. The assumption is that the larger size of the wireway and the provided ventilation negate the need for automatic adjustment factors.
Important Considerations and When Adjustment Might Be Necessary
Wireway Fill
The NEC limits the percentage fill of a wireway. If you are exceeding the fill limits specified in Article 376, then heat dissipation can become a problem, and adjustment factors could become necessary. Calculate the conductor fill based on Article 376.
Excessive Heat
The most common reason for adjusting is a 30C environment around your bussed gutter. Bussed Gutters are usually located close to the service panels and sometimes don't have adequate ventilation for the heat generated from the conductors inside.
Specific Manufacturer Instructions
Some wireway manufacturers may specify ampacity derating factors in their product literature based on fill or other conditions. Always check the manufacturer's instructions for the wireway itself.
Engineering Judgement
As the designer/installer, you are ultimately responsible for ensuring the installation is safe and meets the intent of the code. If you have a gut feeling (based on experience, unusual ambient conditions, or a particularly dense conductor arrangement) that heat could be an issue, it's always prudent to apply a more conservative approach and derate.
Addressing Your Specific Questions
"With that table, I would cap the full calculated demand load at about 488A (80%), correct?" If 310.15(B)(3)(a) did apply (which it likely doesn't in your case), with 8 current-carrying conductors, you would use an adjustment factor of 70%, not 80%. (See Note 3 to the table which indicates you will need to use 70% for over 6 current-carrying conductors). "Do I assume that all 4 feeders are carrying current, including the neutral because it is most likely a non-linear load?" Yes, you should assume the neutral is a current-carrying conductor for the purposes of 310.15(B)(3)(a) if the neutral carries a substantial portion of the load (as with significant non-linear loads). This is clarified in 310.15(B)(5):> "A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions of 310.15(B)(3)(a)."However, since you suspect non-linear loads, the neutral is likely carrying a significant portion of the current, and therefore should be counted as a current-carrying conductor.
In Summary
Start by determining if 310.15(B)(3)(a) needs to be applied. If the wireway fill is within limits and there is no obvious excessive heat, it likely does not.2.
Check the wireway manufacturer's instructions. They might have specific derating requirements.3.
If you have reason to believe heat is an issue, perform a more thorough analysis or simply apply a conservative adjustment factor. Remember that Table 310.15(B)(3)(a) is a minimum requirement, not a maximum.
Recommendation: Double-check the wireway fill calculations. Ensure adequate ventilation around the wireway. Monitor the temperature of the conductors and wireway under full load conditions (if possible). Document your reasoning and calculations for future reference.* Consult with a qualified electrical engineer if you have significant doubts.By following these steps, you can ensure a safe and code-compliant installation. Flag for review