Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: FMC code question

User: nl3designz, Location: MI

Asked on: Thursday, October 24, 2024 at 10:34 am EDT
Answered on: Thursday, March 6, 2025 at 4:20 am EST

Question: I found this in a facility recently and I have some code questions about. There is a 480V breaker panel connected to a distribution point on a wall via FMC. The 480v panel is attached to a 19 inch rack (IT style server rack) which is on casters/wheels. I believe this to be not correct due to 348.12(7). What are your thoughts? Is anyone aware of other codes this does or may violate so I can create a sensible argument to get this changed?Image of FMC in questionAlso, I know I'm new here and I will only use the feedback to help form my own opinion and argument for changing this. I just want to make sure I have a decent amount of code to cite in my argument to secure the funding for a fix.

Okay, let's break down this situation and analyze the code implications. You're right to be concerned; this installation raises several red flags.

Understanding the Situation

You have a 480V breaker panel mounted to a mobile IT server rack on casters. The panel is fed by FMC (Flexible Metal Conduit) from a distribution point on the wall.

Key Code Concerns


NEC 348.12(7) - Uses Not Permitted

This is the most direct and likely violation. It states:> "FMC shall not be used ... (7) Where subject to physical damage."The question here is:

Is this FMC installation subject to physical damage?
I would argue YES, absolutely. Consider the following points to support the claim: Mobility

The rack is on casters. This means it will be moved, bumped, and possibly subjected to strain on the FMC connection. Each movement creates potential for damage.


Server Rack Environment

Server rooms often have equipment moved in and out, creating opportunities for accidental contact and damage to the exposed FMC.

Vibration

Server racks often vibrate. This vibration can fatigue the FMC and its connectors over time, leading to failure.2.

NEC 408.3(A) - Support and Arrangement of Switchboards and Panelboards - Unsupported Equipment
This is likely a violation as the distribution point is on the wall and the panel is mounted on a rack.> Panelboards and switchboards shall be adequately supported and arranged so the weight of the equipment is not supported by the supply conductors.3. NEC 408.36 - Minimum Wire-Bending Space

This is likely a violation as well.> The wiring space within enclosed panelboards and switchboards shall comply with 312.6.
4.


NEC 110.3(B) - Installation and Use

Equipment must be installed and used per its listing and labeling. If the panelboard is not rated to be mounted to a mobile structure then it cannot be used in this way.> Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.5.

NEC 250.118 - Types of Equipment Grounding Conductors

There is a reasonable case that FMC is not suitable as the only EGC for 480V, especially on a mobile rack.> Equipment grounding conductors of the wire type shall be installed in accordance with 250.130(C) where any of the conditions in 250.92(B)(1) through (B)(4) exist.
6.


NEC 250.4(A)(5) - Effective Ground-Fault Current Path

This is a fundamental principle that the grounding path must be low impedance and capable of safely carrying fault current. A potentially damaged or loose FMC connection could compromise this path.> Electrical equipment and wiring shall be installed in a manner that creates a low-impedance circuit facilitating the operation of the overcurrent device. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the source supply equipment. The earth shall not be considered as an effective ground-fault current path.7.

NEC 408.5 - Overcurrent Protection

480V on a server rack seems dangerous.> Panelboards shall be protected from overcurrent in accordance with 408.36.
8.


NEC 408.54 - Component Parts.
Panelboard shall consist of 1 or more panelboard cabinets, or assembles, for the purpose of the 480v panel in a rack (not a panelboard).> Panelboard shall be listed and consist of or include a panelboard cabinet or assembly that is factory wired and equipped with the overcurrent devices.9. NEC 314.29 - Boxes, Conduits, or Raceways to Be Accessible. This is not accessible, but it would be if it was in the rack with an access panel.> Boxes, conduits, or raceways shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating more than is necessary to expose the box, conduit, or raceway.10. NEC 110.16 - Flash Protection. 480V on a rack requires PPE.> Electrical equipment, such as switchboards, panelboards, industrial control panels, meter socket enclosures, and motor control centers, that are in other than dwelling units, and are likely to require examination, adjustment, servicing, or maintenance while energized, shall be field marked to warn qualified persons of potential electric arc flash hazards. The marking shall be located so as to be clearly visible to qualified persons before examination, adjustment, servicing, or maintenance of the equipment.11. NEC 300.11 - Securing and Supporting. The panel must be secured in place to the rack and not moving or under load.> Raceways, cable assemblies, boxes, cabinets, and fittings shall be securely fastened in place. Support wires that do not provide secure support shall not be permitted as the sole support.

Argument Strategies



Safety First

Emphasize the potential for electric shock, arc flash, and fire hazards. 480V is not something to take lightly. Make sure the decision-makers understand the risk of a failure.

Code Compliance

Clearly outline the specific NEC violations. Local inspectors can shut down the installation if it's not compliant.


Long-Term Reliability

Argue that the current setup is likely to fail prematurely due to the stresses of movement and vibration. A proper installation will be more reliable and cost-effective in the long run.

Best Practices

Even if some aspects are technically "legal," argue that they are not
best practices for a safe and reliable electrical system in a server environment.

Manufacturer's Instructions

As listed above, the manufacturer of the equipment may be able to specify approved installation.

Possible Solutions



Relocate the Panel

The best solution is probably to permanently mount the 480V panel on a wall or other fixed structure.


Transition to Rigid Conduit

Use rigid metal conduit (RMC) or intermediate metal conduit (IMC) for the final connection to the panel. This is far more robust than FMC. Use a short length of flexible conduit ONLY for vibration isolation if needed.

Use Suitable Flexible Conduit

If flexibility is absolutely required, consider Liquidtight Flexible Metal Conduit (LFMC). This provides better protection against moisture and physical damage than standard FMC, but it needs appropriate fittings.


Grounding Conductor

Ensure a dedicated equipment grounding conductor (EGC) is run inside the conduit in addition to relying on the conduit itself for grounding. This is essential for a reliable ground fault path.

Strain Relief

Use proper strain relief connectors for the conduit at both ends to prevent stress on the conductors and terminations.

Important Notes



AHJ (Authority Having Jurisdiction)

The final word rests with your local electrical inspector. Discuss your concerns and proposed solutions with them before making any changes.

Qualified Electrician:
Any modifications to the electrical system must* be performed by a licensed and qualified electrician.By presenting a well-reasoned argument backed by code references, you'll have a much stronger chance of getting the necessary funding to correct this potentially dangerous installation. Good luck! Flag for review

Previous Question Next Question