User: blueheels2, Location: Raleigh, NC
Asked on: Thursday, October 24, 2024 at 10:55 am EDT
Answered on: Thursday, March 6, 2025 at 4:21 am EST
Question: Hey I’ve got a multi family service, 4 200 amp meter/mains over 1 wireway. Largest ungrounded conductor to each is 4/0 so I size the the gec to the metal water pipe off of the kill area of the 4/0 x 4 wires to get the size. 4/0 is 211,600, so 211,600 x 4 = 846,400 KC mil.In 250.66 if I use AL wire the size would be 4/0 correct.That’s the first question. If I’m wrong can you lead me to the right answer.Second question. The water lines are 1/2 or 3/4 inch copper. Do they make a water bond clamp for that small of a pipe that will accept 4/0 wire. I’m not finding it. I don’t think split bolting to the 4/0 and reducing at each pipe to a wire size they would accept would be correct?Thanks
Okay, let's break down your questions about grounding electrode conductor (GEC) sizing and water pipe bonding.
Question 1: GEC Sizing
You're on the right track with the overall concept, but there are some important details to clarify. You're right that the GEC size is based on the total ungrounded conductor area for the service. You correctly calculated the total circular mils: 4 wires 211,600 CM/wire = 846,400 CM. Applying 250.66 for Aluminum
Looking at Table 250.66, and using your calculated 846,400 CM, you will see that a copper GEC would require 2/0 wire, but an aluminum GEC would require 4/0 AL wire.
So your final answer that you would need a 4/0 AL is correct.Key Considerations and Clarifications
Service Entrance Conductors vs. Load Conductors
You are dealing with Service entrance conductors. This means you size the GEC directly from Table 250.66 based on the total area of the service entrance conductors.
Parallel Conductors
When service conductors are run in parallel (as they are in your case), the GEC size is based on the combined area of the parallel conductors. You've already correctly addressed this in your calculation.
Question 2: Water Pipe Bonding
You've hit a common snag. Let's address the issues and potential solutions: Clamp Size
You're right; finding a listed clamp that accepts a 4/0 AWG conductor and fits directly on a 1/2" or 3/4" copper water pipe is going to be extremely difficult, if not impossible.
Reducing the Conductor Size at the Clamp (Using Split Bolts)
This is generally
not permitted for the primary grounding electrode conductor. The NEC 250.64(A) requires that the GEC be continuous without splices or joints, unless made by irreversible compression connectors listed as grounding and bonding equipment. This is designed to ensure the integrity of the grounding path. Split bolts aren't usually listed for direct burial applications. You would also be required to apply anti-oxidant to the splice connection. Acceptable Method for Reduction (Bonding Jumpers)
The correct and code-compliant method is to install a
supplemental GEC (bonding jumper) from the meter enclosure and a suitable grounding electrode connection point on the water pipe, and you'd size that conductor according to Table 250.66.
Here's a step-by-step breakdown of the recommended approach for the water pipe bond
Determine the Total Required GEC Size (You already did this)
In your case, you've correctly determined you need a 4/0 AWG aluminum GEC.2.
Run the 4/0 GEC
Run the 4/0 AWG aluminum GEC from your service equipment/wireway to a location on the water pipe before any plumbing unions or non-conductive sections (e.g., plastic pipe, dielectric unions).3.
Mechanical Protection
If the GEC is exposed to physical damage, it needs to be adequately protected (e.g., conduit, raceway).4.
Install A Supplemental GEC (Bonding Jumper)
You'll run a supplemental bonding jumper from the 4/0 GEC to the water pipe connection.
Important Considerations
"Accessible" vs. "Readily Accessible"
Make sure the connection to the water pipe is accessible for inspection and maintenance.
Local Amendments
Always check with your local electrical inspector for any local amendments or interpretations of the NEC that might affect your installation.
In summary
1. You correctly sized your required GEC at 4/0 AL based on the total CM area of your service entrance conductors.
2. Directly connecting a 4/0 conductor to a small water pipe is impractical and may not be possible with listed clamps.3.
Use a supplemental bonding jumper, sized from Table 250.66, to make the actual connection to the water pipe. Run the main GEC (your 4/0 AWG) to a more robust grounding location if necessary. Flag for review