Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Code conflicts?

User: anbm, Location: TX

Asked on: Thursday, October 24, 2024 at 11:47 am EDT
Answered on: Thursday, March 6, 2025 at 4:21 am EST

Question: To reduce voltage drop, we must increase circuit wires from #12 to #6 AWG, the ground wire will be increase to #6 AWG per NEC 250.122(B) as well.However, #6AWG conductor will be good for 65A (75 degree C conductor), and per table 250.122, #8 ground is needed not #6 as noted in NEC 250.122(B) rule above. Do these two code sections conflict?

You're right to question this. You're observing a common point of confusion. Let's break down the code sections and why they don't conflict in your specific scenario. NEC 250.122(B): Increasing Size of Equipment Grounding Conductor (EGC) This section addresses situations where you increase the size of the ungrounded (hot) conductors for reasons like voltage drop. The key phrase is: "Where ungrounded conductors are increased in size for any reason other than ampacity correction..." It states that the EGC must be increased proportionately to the increase in the ungrounded conductors. NEC Table 250.122: Minimum Size Equipment Grounding Conductors for Grounding Raceway and Equipment This table provides the minimum size of the EGC based on the rating or setting of the overcurrent protective device (OCPD, typically a circuit breaker or fuse) protecting the circuit.

Why There's No Conflict in Your Case

In your scenario, you're increasing the wire size (from #12 to #6) to reduce voltage drop, not because the original #12 wasn't rated for the circuit's current. Let's assume the circuit is protected by a 20A breaker. Here's the logic:1.

Original Circuit

#12 AWG conductors 20A Breaker (Hypothetical but common) Table 250.122 would require a #12 AWG EGC.
2.


Upgraded Circuit (Voltage Drop Correction)

#6 AWG conductors (for voltage drop) 20A Breaker (The circuit is still protected at 20A)

Per 250.122(B)

Because you increased the ungrounded conductors for voltage drop, you must increase the EGC proportionately. This is where the ratio comes in. You are going from #12 AWG to #6 AWG. Based on NEC Chapter 9 Table 8, the approximate cross-sectional area of #12 is 6530 circular mils. The approximate cross-sectional area of #6 is 26,240 circular mils. The ratio is 26240/6530 = 4.02. If the original equipment grounding conductor was #12, then you multiply its cross-sectional area by 4.02 to get the new size. (You can't use this exact number, but you use the rule in the next bullet) Instead of doing the cross-sectional area math, most people use the rule that one must increase the EGC to the same size as the phase conductors.

Per Table 250.122

A 20A breaker still only requires a #12 AWG EGC
based on the OCPD rating.

Therefore, the more stringent requirement of 250.122(B) prevails. You
must increase the EGC to #6 AWG to match the increased ungrounded conductors.
Important Considerations



Overcurrent Protection

The purpose of the EGC is to provide a low-impedance fault current path to safely trip the OCPD. The OCPD must still be sized appropriately for the load and the smallest conductor in the circuit (ignoring voltage drop upgrades). You cannot use #6 wire and then put a 60A breaker on the circuit.

Termination

Ensure all equipment is rated for the increased conductor size. Terminals must be properly rated for #6 AWG conductors.


Ampacity vs. Voltage Drop

It's crucial to understand the difference. Ampacity is the current-carrying capacity of the wire before overheating. Voltage drop is the loss of voltage along the length of the wire due to its resistance.

In Summary:


NEC 250.122(B) is very specific. If you increase the wire size for any reason other than ampacity, you must proportionally increase the EGC. This ensures that if a fault occurs, the increased wire size, including the EGC, will handle the fault current and allow the OCPD to trip quickly.Although table 250.122 calls for #8 AWG when using 65A breaker size, it does not matter if the increase in the circuit wires are due to voltage drop. If the circuit wires are increase due to voltage drop, it will need to follow 250.122(B). Flag for review

Previous Question Next Question