Topic: Step and Touch Voltage Calculations for Grounding

User: timm333, Location: Minneapolis, MN

Asked on: Thursday, October 24, 2024 at 2:11 pm EDT
Answered on: Thursday, March 6, 2025 at 4:21 am EST

Question: I am trying to figure out that as per IEEE: when do we need to calculate the step/touch voltages for grounding. For an industrial plant, the incoming 25kV is stepped down to 4.16kV. Step/touch voltages are calculated for 25kV substation. However inside the industrial plant: there 4.16kV motors and also there are transformers whose primary side voltage is 4.16kV.Is it required to calculate the step/touch voltage for 4.16kV motors and 4.16kV transformers inside industrial plant? Thanks

Yes, according to IEEE standards and best practices, you likely need to calculate step and touch potentials for the 4.16 kV equipment within the industrial plant, even though the primary concern is typically the 25 kV substation. Here's a breakdown of why and when

Why Calculate Step and Touch Potentials for 4.16 kV Equipment?
Personnel Safety

The primary goal of calculating step and touch potentials is to ensure the safety of personnel who may be near grounded equipment during a ground fault. Even at 4.16 kV, dangerous voltage gradients can exist near a fault. A low voltage does not mean that high fault current is not possible.


Fault Current Levels

The magnitude of fault current is a critical factor. Even though the voltage is lower than the substation, a significant fault current flowing through the ground grid can create hazardous voltage gradients. Large motors and transformers connected to a 4.16 kV system can generate substantial ground fault currents.

Grounding System Adequacy

Calculating and comparing the actual step and touch potentials against the allowable values verifies whether the grounding system is adequate to protect personnel. If the calculated values are higher than the allowable values, you may need to improve your grounding system.


IEEE Standards

While not always explicitly stating every scenario, IEEE standards like IEEE Std 80-2000 (Guide for Safety in AC Substation Grounding) provide the methodologies and principles applicable to any facility with energized equipment. The principles of step and touch potential apply to the 4.16 kV system just as they do to the 25 kV system.

Legal and Regulatory Compliance

Local regulations and insurance requirements may also mandate step and touch potential calculations for specific equipment or voltage levels.


Risk Assessment

Perform a risk assessment. Consider the likelihood of faults occurring, the potential consequences (injury or death), and the frequency with which personnel interact with the equipment. If the risk is deemed unacceptable, mitigation (including step and touch potential analysis and grounding system improvements) is necessary.

When to Perform the Calculations (Triggers)

Here are common scenarios when you should calculate step and touch potentials for 4.16 kV equipment:1.

New Installations or Equipment Upgrades

Whenever new 4.16 kV equipment (motors, transformers, switchgear, etc.) is installed or existing equipment is significantly upgraded (e.g., replacing a small motor with a much larger one), recalculate. The fault current contribution will change.
2.


Grounding System Modifications

Any changes to the grounding system itself (e.g., adding ground rods, connecting to a new ground grid, modifying ground conductors) requires a re-evaluation.3.

Changes in Soil Resistivity

Significant changes in soil resistivity due to environmental factors (e.g., seasonal variations, flooding, construction activities) can affect step and touch potentials. Periodically measure soil resistivity.4.

Known Ground Fault Incidents

If there's a history of ground faults in the 4.16 kV system, investigate and perform a step/touch potential analysis.
5.


Periodic Reviews

Establish a routine review schedule (e.g., every 5 years, or more frequently if conditions warrant) to re-evaluate the grounding system and step/touch potentials, even if no changes have occurred.6.

Equipment with High Personnel Interaction

Prioritize step/touch potential calculations for equipment that personnel frequently operate, maintain, or are likely to be near. This includes things like motor control centers (MCCs), switchgear, transformers in accessible areas, etc.7.

High Fault Current Potential

If the 4.16 kV system has a high available fault current due to its configuration and connected sources, step/touch potential calculations are more critical.

What to Consider in Your Calculations



Fault Current Contribution

Determine the maximum possible ground fault current that the 4.16 kV equipment can contribute to the ground grid. Consider contributions from all connected sources (generators, utility, other motors, etc.).


Grounding System Impedance

Accurately model the impedance of the grounding system, including ground conductors, ground rods, and the ground grid itself.

Soil Resistivity

Accurate soil resistivity measurements are crucial. Use appropriate testing methods (e.g., Wenner four-point method) and consider variations in soil conditions.


Clearing Time

The fault clearing time of the protection devices (circuit breakers, fuses) will influence the allowable touch and step voltages. Faster clearing times allow for higher voltages.

Shock Duration

The allowable step and touch voltages are inversely proportional to the duration of the shock. The faster the fault is cleared, the higher the permissible voltage.


IEEE Std 80-2000 (Guide for Safety in AC Substation Grounding)

This is the primary reference document. It provides the equations and methods for calculating allowable touch and step potentials.

IEEE Std 142 (Green Book) - Grounding of Industrial and Commercial Power Systems

This gives general guidelines and best practices.


Location

Equipment indoors is typically concrete floor - which can change the equations for calculating the body resistance. Equipment outdoors is typically soil.

How to Mitigate High Step/Touch Potentials

If your calculations show that step or touch potentials exceed the allowable limits, you'll need to take corrective actions:

Improve Grounding System

Add more ground rods, expand the ground grid, and improve the conductivity of ground conductors.


Equipotential Bonding

Bond all metallic objects (enclosures, handrails, pipes, etc.) together to create an equipotential zone around the equipment.

Insulating Surfaces

Use insulating surfaces (e.g., rubber mats, asphalt paving) to increase the resistance between a person and the ground.


Reduce Fault Clearing Time

Improve the speed of the protection system by using faster circuit breakers or protective relays.*

Physical Barriers

Install fences or other barriers to restrict access to the equipment.

In summary:
Don't assume that because it's a 4.16 kV system, step/touch potential calculations are unnecessary. Due to the potentially high fault current and presence of personnel, it is very important to perform these calculations for the 4.16 kV motors and transformers in your industrial plant. Follow IEEE Std 80-2000 guidelines and consult with a qualified electrical engineer experienced in grounding system design. Flag for review