User: Chancelong, Location: Wisconsin
Asked on: Thursday, October 24, 2024 at 3:55 pm EDT
Answered on: Thursday, March 6, 2025 at 4:22 am EST
Question: I have an air handling unit that has 120 volt motor starter. The customer wants a button to press that will shut the unit off for 20 minutes then turn back on, but also once the button is pressed, the button needs to be deactivate for an hour to stop the air handler from being off for extended periods of time. What is the best way to go about this? A few time delay relays?
You're on the right track with time delay relays. Here's a solution using readily available components and a clear explanation
Components Needed:
Momentary Push Button
A standard normally open (NO) momentary push button.
Time Delay Relay (TDR) - Off Delay (Retentive)
This relay will energize immediately when power is applied and will de-energize after a set time delay once the power is cut. We need a "retentive" or "memory" type because we need it to continue the timing sequence even after the momentary button is released. You will need to be able to set this to 20 minutes.
Time Delay Relay (TDR) - On Delay
This relay will energize after a set time delay once power is applied. You will need to be able to set this to 60 minutes (1 hour).
Control Relay
A standard relay with a 120V coil.
Wiring Diagram (Conceptual)120V Hot
TDR - Off Delay (20 min) - Input Power (A1, A2)Momentary Push Button (NO) ----TDR - Off Delay - Normally Open (NO) Contact----
----Control Relay (86) - Normally Closed (NC) Contact----|----Control Relay (86)| Coil (A1, A2)| Contact (NO) - Wired to| AHU Starter Coil
TDR - On Delay (60 Min) -| Input Power (A1, A2)|Neutral
Explanation of Operation
Normal Operation
Initially, everything is at rest. The AHU is running because the control relay is energized.2.
Button Press
When the momentary push button is pressed: It energizes the TDR - Off Delay relay (20min). The TDR - Off Delay relay immediately closes its normally open (NO) contact, which energizes the Control Relay coil and the TDR - On Delay relay (60min). The Control Relay opens its normally closed (NC) contact de-energizing the TDR - On Delay relay (60min). Because we're using a retentive TDR - Off Delay relay, it starts its timer.3.
20-Minute Shutdown
After 20 minutes, the TDR - Off Delay relay de-energizes, opening its normally open (NO) contact. This de-energizes the Control Relay, and its normally open (NO) contact to AHU Starter Coil opens, shutting down the AHU motor. The Control Relay closes its normally closed (NC) contact allowing the TDR - On Delay (60min) to be energized.4.
AHU Restart and Lockout
After 60 minutes, the TDR - On Delay relay (60min) energizes. This completes the circuit and energizes the Control Relay, which closes its normally open (NO) contact to AHU Starter Coil, restarting the AHU motor. The Control Relay opens its normally closed (NC) contact de-energizing the TDR - On Delay relay (60min), so the circuit is ready for another cycle.5.
Repetitive Button Presses During Lockout
If the button is pressed again within the 60-minute lockout period, it does nothing because the TDR - Off Delay relay is already de-energized and the circuit for the TDR - On Delay relay is not complete.
Important Considerations
Safety
This circuit must be installed and wired by a qualified electrician. It involves working with 120V, which is dangerous. Proper wiring practices, grounding, and overcurrent protection are essential. Include a clear label near the button stating "Emergency Shutdown - Do Not Press Repeatedly."
Enclosure
All components should be housed in a suitable electrical enclosure rated for the environment.
Reliability
Use industrial-grade relays for long-term reliability.
Testing
Thoroughly test the circuit after installation to ensure it functions as intended.
AHU Starter Coil
Confirm the voltage and current requirements of the AHU's motor starter coil and choose a control relay with contacts rated to handle that load.
Maintenance: Regular inspections and testing of the system will maintain the reliability of the emergency shutoff button and the air handling unit.This design achieves the desired functionality: a 20-minute shutdown with a 60-minute lockout. Remember to prioritize safety and consult with a qualified electrician for proper installation and wiring. Flag for review