Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Step and Touch Voltage Calculations for Grounding

User: timm333, Location: Minneapolis, MN

Asked on: Friday, October 25, 2024 at 3:34 am EDT
Answered on: Thursday, March 6, 2025 at 4:24 am EST

Question: I am trying to figure out that as per NEC/IEEE: when do we need to calculate the step/touch voltages for grounding. For an industrial plant, the incoming 25kV is stepped down to 4.16kV. Step/touch voltages are calculated for 25kV substation. However there are also 4.16kV motors and transformers inside the industrial plant.Is it required to calculate the step/touch voltage for 4.16kV motors and 4.16kV transformers inside industrial plant? Thanks

Yes, generally, you are required to consider and likely calculate step and touch potential for the 4.16kV equipment in your industrial plant. Here's the breakdown of why: Safety is Paramount

The primary goal of grounding is to protect personnel from electrical shock hazards. Step and touch potential calculations are a critical part of ensuring that the grounding system is adequate to limit these hazards.


NEC & IEEE Stance



NEC (National Electrical Code)

While the NEC doesn't explicitly mandate step and touch potential calculations in every situation, it emphasizes the need for a robust grounding system that limits voltage to safe levels during ground faults. Article 250 (Grounding and Bonding) is the relevant section. NEC mandates effective grounding and bonding to minimize voltage rises.


IEEE (Institute of Electrical and Electronics Engineers)

IEEE standards, particularly IEEE Std 80 (IEEE Guide for Safety in AC Substation Grounding), provide detailed methodologies for calculating step and touch potentials and designing grounding systems to meet safe limits. While IEEE 80 is specifically written for substations, the principles and methods are applicable and often adopted for other electrical installations, including those within industrial plants.

Fault Current Considerations

A fault on the 4.16kV system can result in significant ground fault current. The magnitude of fault current, combined with the soil resistivity and grounding grid impedance, determines the ground potential rise (GPR). Step and touch potentials are directly related to the GPR. Even though the voltage is lower than the incoming 25kV, the available fault current at 4.16kV can still be substantial, potentially creating hazardous step and touch potentials if the grounding system is inadequate.

Accessibility

The likelihood of personnel being exposed to step and touch potentials near 4.16kV equipment is high. Maintenance personnel, operators, and even accidental passersby could be at risk if a fault occurs.

Where to Apply the Calculations

You'll need to consider step and touch potential calculations around:


4.16kV Motors

Especially larger motors.

4.16kV Transformers

On both the primary (4.16kV) and secondary (lower voltage) sides, although the primary side is typically the greater concern.


4.16kV Switchgear and Distribution Panels



Any other 4.16kV equipment
that personnel might come into contact with or be in the vicinity of. How to Approach the Calculations


Determine Fault Current

Calculate the maximum ground fault current that could occur at each location (4.16kV motors, transformers, switchgear, etc.). This requires a short circuit study.
2.


Soil Resistivity Measurement

Measure the soil resistivity at the site using a four-point (Wenner) method or similar.3.

Grounding System Design

Analyze the existing grounding system (ground grid, ground rods, connections to equipment).4.

Calculate GPR

Determine the Ground Potential Rise (GPR) during a fault.5.

Calculate Step and Touch Potentials

Use the GPR, grounding grid characteristics, and IEEE 80 equations to calculate step and touch potentials.6.

Compare to Allowable Limits

Compare the calculated step and touch potentials to the allowable limits specified in IEEE 80 or other relevant standards. These limits depend on the duration of the fault current and the body resistance of a person.7.

Mitigation (if Required)

If the calculated values exceed the allowable limits, you'll need to improve the grounding system. Possible mitigation strategies include: Adding more ground rods or expanding the ground grid. Installing equipotential grids around equipment. Using surface layer materials (e.g., crushed rock) with high resistivity. Improving bonding of equipment enclosures. Reducing clearing time of the protective devices.

Documentation

Keep thorough records of your grounding system design, soil resistivity measurements, fault current calculations, step and touch potential calculations, and any mitigation measures implemented.

In summary:
While it might seem like extra work, considering step and touch potentials for your 4.16kV equipment is a crucial safety measure and generally required to comply with industry best practices and potentially local regulations. It is vital for a safe industrial electrical installation. A qualified electrical engineer with experience in grounding system design should perform these calculations and analyses. Flag for review

Previous Question Next Question