Question: I have an existing 100 amp split bus panel in a residence. I need to get additional breaker space and am looking to install a sub panel next to it.There is currently the “main lighting” 2 pole breaker feeding the lower bus.In the factory labeled “main disconnect “openings there is a 2 pole breaker for the range and then 2 single pole breakers.Is it code compliant to remove the 2 single pole breakers and install a 2 pole breaker to feed the new sub panel?I could then re feed the 2 single pole loads from the new sub and add my new load.This set up would allow for all power to be disconnected with 3 double pole breakers.It’s a 100 amp service, total connected load with new circuits would be 77A.Thank you.
Okay, let's break down the situation with your split-bus panel and the proposed subpanel installation. I'll focus on code compliance and best practices.
Understanding Split-Bus Panels
Split-bus panels (also sometimes called "Rule of Six" panels) were common in older homes. They have a main bus that is fed from the utility. This bus then is split into 2 sections. The lower section of the bus is fed from a 2 pole breaker that serves as the “main lighting” disconnect. The upper section of the bus is fed from a number of breakers. These breakers combined could serve as the main disconnect.
Code Compliance Issues "Rule of Six" Violations
The biggest potential issue is whether your panel is actually compliant with the "Rule of Six." This rule states that you must be able to disconnect all power to the house with no more than six throws of the hand (breakers). From your description you meet this, but you would want to verify this is the case. If you violate the rule of six that will need to be resolved.
Available Breaker Spaces
You are adding load to a 100 amp service, so available breaker space is definitely a concern.
The Proposed Solution
Your plan to remove the two single-pole breakers in the factory-labeled "main disconnect" section and replace them with a 2-pole breaker to feed the subpanel is potentially acceptable if the following conditions are met:1. Load Calculation is Accurate
Double-check your 77A total connected load calculation. This must include all existing loads in the house and the new loads you plan to add to the subpanel. It's best to slightly overestimate rather than underestimate. The load calculation is how you are determining a 100 amp service is sufficient.2.
Subpanel Ampacity
The subpanel should be rated at or above the ampacity of the breaker feeding it (e.g., if you install a 60A breaker to feed the subpanel, the subpanel should be rated for at least 60A). A higher rating is generally better.3.
Proper Wiring
The wiring from the existing panel to the subpanel must be of the correct gauge for the breaker size you choose. Use the appropriate wire type (e.g., THHN/THWN in conduit, NM-B cable) and ensure all connections are tight and properly made.4.
Grounding and Bonding
This is critical! The subpanel must have a separate grounding bus. The neutral bus in the subpanel must be isolated from the subpanel enclosure (it should not be bonded). Run a four-wire feeder (two hots, neutral, and ground) from the existing panel to the subpanel. The ground wire connects to the grounding bus in the subpanel and the grounding bus in the existing panel.5.
Subpanel Location
The subpanel must be accessible and installed according to code (e.g., proper working clearances).6.
Re-feeding Existing Circuits
When you move the two existing single-pole circuits from the old panel to the subpanel, ensure you use appropriately sized breakers in the subpanel.7.
Labeling
Clearly label everything! Label the subpanel itself, the feeder breaker in the main panel, and all the breakers in the subpanel.
Important Considerations
Local Codes
Your local building codes might have additional requirements or restrictions. Always check with your local building department before starting any electrical work.
Panel Condition
Inspect your existing panel for any signs of damage, corrosion, or overheating. If the panel is in poor condition, it might be better to replace the entire panel rather than adding a subpanel.
Future Expansion
Consider your future electrical needs. It might be worth installing a larger subpanel than you currently need to allow for future expansion.*
Main Panel Disconnect
If any maintenance is ever needed on the main panel, ensure you have a way to disconnect the subpanel from the main panel.
Recommendation
Given the potential complexities and code considerations, I strongly recommend consulting with a qualified electrician. They can assess your existing panel, calculate the load accurately, and ensure that the subpanel installation is done safely and in compliance with all applicable codes. They can also help you determine the best size for the subpanel and ensure that all grounding and bonding are done correctly. This will help prevent safety hazards and ensure your electrical system is working optimally. Flag for review