Topic: Fuse downstream let-through Current

User: kcunningham59, Location: Audubon, NJ

Asked on: Friday, October 25, 2024 at 10:09 am EDT
Answered on: Thursday, March 6, 2025 at 4:24 am EST

Question: I will keep this question quick and short. I know there is a lot out there on this topic but I can't get a straight answer. If there is a fused disconnect on the outside of a building and the available fault current at the switch is say 15k and the let-through is say 8k, can the first panel after the switch be rated at 10k or do we assume 15k is still the worst case passing through the switch to the next device. If it is not allowed, an NEC section would be appreciated. I know there are some UL guidelines as well that may affect this answer.

You cannot rely on the fuse in the fused disconnect to reduce the available fault current for the purpose of determining the required short-circuit current rating (SCCR) of the downstream panel. You must use the available fault current at the line side terminals of the fused disconnect, which in your scenario is 15kA.

NEC Requirement



NEC 110.9 Interrupting Rating

"Equipment intended to interrupt current at fault levels shall have an interrupting rating at nominal circuit voltage sufficient for the current that is available at the line terminals of the equipment."


NEC 110.10 Circuit Impedance, Short-Circuit Current Rating, and Other Characteristics

"The overcurrent protective devices, the total impedance, the component short-circuit current ratings, and other characteristics of the circuit to be protected shall be selected and coordinated to permit the circuit protective devices used to clear a fault to do so without extensive damage to the electrical equipment."

Explanation

NEC 110.9 dictates that equipment (including the panel downstream of the disconnect) must be rated to interrupt the available fault current at its line terminals. The "line terminals" of the downstream panel are directly connected to the load terminals of the fused disconnect. Therefore, if the available fault current at the line side of the fused disconnect is 15kA, then, for the purposes of NEC 110.9, the available fault current at the line side of the panel is also 15kA, regardless of the fuse's let-through current.NEC 110.10 reinforces that the entire system must be coordinated to withstand fault currents without extensive damage. This means that all components in the circuit, including the panel, must have adequate short-circuit current ratings. The fuse's let-through current is a factor in coordination studies, but it doesn't negate the requirement for the panel itself to have a sufficient SCCR.

Why you can't rely solely on the let-through current



Fuse Failure

Fuses can fail, be incorrectly sized, or be replaced with the wrong type of fuse. Relying solely on the let-through current for SCCR calculations introduces a risk if the fuse does not perform as expected.


Coordination Studies

While let-through current is important for coordination studies (determining if the fuse will clear a fault before damaging downstream equipment), the SCCR of the downstream equipment must still exceed the available fault current at its terminals. A coordination study can inform other characteristics of the circuit, as described in NEC 110.10, but does not alleviate the need to meet the minimum SCCR.

UL Standards

UL standards also address SCCR requirements for electrical equipment. They generally require equipment to be rated for the available fault current at its terminals, without relying on upstream current-limiting devices.

In summary

You need a panel with an SCCR of at least 15kA. The fuse's let-through current is important for coordination, but not for determining the required SCCR of the panel.

Important Considerations



Series Ratings

In some cases, you might be able to use a lower-rated panel if it is specifically series-rated with the upstream fuse. This requires the equipment to be tested and listed as a series combination, and the series rating will be clearly marked. Do not assume you can series rate unless the equipment is specifically marked as such. Consult the manufacturer's documentation for specific series ratings.*

Engineering Judgment:
This is a simplified explanation. A detailed short-circuit study should be performed by a qualified electrical engineer to accurately determine the available fault current at all points in the system and to ensure proper coordination of overcurrent protective devices. Flag for review

Previous Question Next Question