Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Splicing grounds

User: walterhelton21, Location: Alabama

Asked on: Friday, October 25, 2024 at 5:41 pm EDT
Answered on: Thursday, March 6, 2025 at 4:25 am EST

Question: So I have a GE powermark plus load center, the neutrals are double tapped with most of the grounds on the left bus bar. Is there any code against splicing the grounds and running them to the right bus bar? I would appreciate any information. Thanks

Okay, let's break down the situation with your GE PowerMark Plus load center and the grounds/neutrals.

Understanding the Issue Double-Tapped Neutrals

Generally, double-tapping neutrals under a single terminal screw is a

violation
of the National Electrical Code (NEC) and is unsafe. Neutrals carry the return current from the circuit. Having multiple neutrals under one screw can lead to a loose connection, arcing, overheating, and potentially a fire hazard. Also, if you remove one neutral from under the screw, the other circuit will become non-functional and could become energized.
Grounds on the Left Bus Bar

Grounding conductors (equipment grounding conductors - EGCs) connect the metal parts of appliances, devices, and enclosures back to the main grounding electrode system (ground rod, etc.) at the service panel. Their purpose is to provide a low-impedance path for fault current to trip a breaker quickly in the event of a short circuit, thus protecting people from electrical shock.

Desire to Move Grounds to the Right Bus Bar

You want to move grounds from the left bus bar to the right bus bar, presumably to better organize the wiring, free up space, or address some other issue.

NEC Considerations and Requirements


Here's what the NEC says (generally – local codes can be stricter, so always check with your local electrical inspector):
NEC 110.3(B) Installation and Use

"Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling." This means you must follow the manufacturer's instructions for your GE PowerMark Plus load center. The instructions will specify how many conductors are allowed under each terminal screw for both neutrals and grounds.

NEC 408.41 Grounded Conductor Terminations

This section requires that each neutral conductor be terminated at an individual terminal that is properly identified and insulated. The neutral terminals cannot be used for more than one conductor unless designed and listed for such use.


NEC 250.8 Connection of Grounding and Bonding Equipment

This section generally requires that grounding and bonding conductors be connected in a manner that ensures a reliable electrical connection.

NEC 250.130 Equipment Grounding Conductor Connections

This section covers the methods allowed for grounding equipment, but it doesn't directly address splicing within a panel for the purpose of moving the ground to a different bar.


NEC 312.8 Enclosures for Splices and Taps

In general, enclosures can contain splices if the wiring space is not filled to more than 75% of the cross-sectional area of the enclosure. If the load center is not designed to accommodate a large number of splices, it can overcrowd the panel.

What You Can Do
1. Consult the Load Center's Labeling and Instructions

This is the most important step. Look inside the panel door and/or the manufacturer's documentation. It should explicitly state: The maximum number of conductors allowed under each terminal screw for both the neutral bar(s) and the ground bar(s). Whether the ground bars are electrically connected. (In many panels, they are, but you need to confirm.)2.

Correct the Double-Tapped Neutrals

This MUST be addressed. The proper way to fix this issue is with a listed and labeled method for splicing neutrals within the panel. Acceptable methods include:

Pigtailing

Use a short length of wire (a "pigtail") and a wire connector (such as a wire nut or a push-in connector) to connect the two (or more) neutral wires to the pigtail. Then, connect the pigtail to a
single terminal on the neutral bar. Make sure the wire connector is properly sized for the number and gauge of wires you're connecting.

Using a Listed Multi-Tap Connector

There are terminal blocks and other connectors specifically designed for multiple neutral connections. These must be listed (UL, ETL, etc.) for this purpose and rated for the appropriate amperage and voltage.

Adding a Neutral Bar

If there isn't enough room on the existing neutral bar, you can add an additional neutral bar, provided it is listed for use in your panel and properly bonded to the existing neutral bar and enclosure.


Replacing the Breakers

Replace tandem breakers with single pole breakers, allowing additional space for other circuits.3.

Grounding Conductors (EGCs)



Splicing Grounds

Generally, yes, you can splice grounding conductors within the panel to move them to a different ground bar. However, the splice must be made with a listed and labeled method (wire connector) and must be accessible. This is where the 75% fill rule comes into play. If splicing will cause the enclosure to be over-filled, then it is not permitted. Also, the ground bar on the right side must be properly bonded to the enclosure.

Verify Ground Bar Isolation

If the ground bar on the right side is isolated (not electrically connected) from the panel enclosure, then you CANNOT simply move grounds there. It must be properly bonded to the enclosure.4.

Adding a Ground Bar

Adding a ground bar is usually the best option. However, you must purchase a ground bar made for your panel. They are usually designed to screw into the side of the panel. Once you have the ground bar installed, you can connect the grounds from both sides of the panel.

Important Considerations and Warnings
Never put a neutral and a ground under the same terminal screw. This is a dangerous and serious code violation. Torque Specifications

Many breakers and terminal screws have specific torque requirements. Use a torque screwdriver or wrench to tighten the screws to the specified torque. Under-tightening can lead to loose connections, and over-tightening can damage the terminal.


Wire Fill

Do not overcrowd the panel with wires. The NEC has rules about conduit and enclosure fill. Overcrowding can make it difficult to work in the panel and can lead to overheating.

Professional Help

If you are not comfortable working with electricity or unsure about any of these steps,

hire a qualified, licensed electrician.
Working with electrical panels can be dangerous, and mistakes can be costly or even fatal.

In Summary1. Safety First

Turn off the main breaker before working inside the panel. Use appropriate personal protective equipment (PPE), such as insulated gloves and safety glasses.2.

Consult Instructions

Read and follow the manufacturer's instructions for your GE PowerMark Plus load center.3.

Correct Neutrals

Fix the double-tapped neutrals using a listed and labeled splicing method.4.

Grounds

You can
usually* splice grounding conductors to move them to a different ground bar, but only with listed connectors and if it doesn't overcrowd the panel. Verify the ground bar on the right is properly bonded to the enclosure.5.

When in Doubt, Call a Pro:
If you have any doubts or concerns, consult a qualified, licensed electrician.This information is for general guidance only and should not be considered a substitute for professional advice from a qualified electrician. Electrical work can be dangerous, and you are responsible for ensuring that all work is performed safely and in accordance with all applicable codes and regulations. Flag for review

Previous Question Next Question