User: Dennis Alwon, Location: Chapel Hill, NC
Asked on: Saturday, October 26, 2024 at 10:43 am EDT
Answered on: Thursday, March 6, 2025 at 4:26 am EST
Question: Can someone explain the difference between these two animals. The system jumper seems to add "at a separately derived system" but aren't all services a separately derived system.Bonding Jumper, Main. (Main Bonding Jumper)The connection between the grounded circuit conductor and the equipment grounding conductor, or the supply-side bonding jumper, or both, at the service. (CMP-5)
Okay, let's break down the difference between a Main Bonding Jumper and a System Bonding Jumper, focusing on the "separately derived system" aspect. The key is the location and purpose of the bond.1. Main Bonding Jumper (MBJ)
Location
At the Service Equipment. This is the main electrical service entrance to a building.
Purpose
Connects the following at the service: Grounded (Neutral) Conductor (if the system is grounded). Equipment Grounding Conductor (EGC), often the metal conduit, enclosure, or a dedicated grounding wire. Supply-Side Bonding Jumper (if present).
Why it's important
The MBJ creates a low-impedance path for fault current to return to the source (the utility transformer) at the service. This helps the overcurrent protection devices (circuit breakers, fuses) trip quickly during a fault, minimizing shock hazards and equipment damage. This is the first essential bond in a building's electrical system.
2. System Bonding Jumper (SBJ)
Location
At a Separately Derived System (SDS). An SDS is an independent electrical power source within a building, derived from the main service or another SDS. Common examples include: Generators (Standby or Emergency) Transformers (Step-Up or Step-Down) Solar Inverters Uninterruptible Power Supplies (UPS)
Purpose
Similar to the MBJ, but within the SDS's equipment. It connects: The SDS's grounded (neutral) conductor (if it's a grounded system) The SDS's equipment grounding conductor (EGC) The SDS's metallic enclosure.
Why it's important
The SBJ creates a low-impedance fault current path within the SDS itself. If a fault occurs within the SDS's equipment, the SBJ helps that fault current return quickly to the SDS's source (e.g., the generator's windings or the transformer's secondary). This ensures overcurrent protection within the SDS works effectively.
The "Separately Derived System" Key
You're right to question if all services aren't separately derived. The crucial point is that the NEC defines an SDS very specifically. It's not just any electrical service. It must meet specific criteria relating to power source separation. It's an electrical source that creates its own neutral within itself or has no direct electrical connection to the primary source's neutral (except through the equipment grounding conductor).Imagine a large building with a main electrical service. Then, a backup generator is installed. The generator is a separately derived system because it can create electrical power independent of the utility. It has its own neutral point and protective devices. The generator needs its own bonding system for safety when running independently.
Why you need both MBJ and SBJ (when applicable)
The MBJ protects the entire building and the service entrance. The SBJ protects the SDS when it's operating independently.
Common Misconception
A common mistake is to think that the grounding conductor connected to the separately derived system (generator, transformer, etc.) is the only grounding necessary. That is incorrect. A properly installed and functioning system bonding jumper will ensure that the protective devices are operational. The earth, is not a good conductor and is not suitable for use as the sole equipment grounding conductor.
In simpler terms
MBJ
"Master" ground bond at the main service entrance.
SBJ
"Local" ground bond at an independent power source within the building.
Example
Think of your house (simplified): The main electrical panel has a neutral busbar connected to the metal panel enclosure. This connection is the MBJ. If you install a backup generator with a transfer switch, the generator becomes an SDS. You would need an SBJ inside the generator's junction box to bond the generator's neutral (if present) to its frame and grounding conductor.
In Summary:
While both jumpers serve a similar function, the MBJ is for the main electrical service, and the SBJ is specifically for separately derived systems (generators, transformers, solar inverters, UPS systems) within a building, to ensure localized fault protection. The "separately derived system" aspect is the key differentiator. Flag for review