Question: I work for a company that repairs all kinds of equipment for the financial industry. Alarms, cameras, safes, locks, and also drive up equipment. Most banks have an electric drawer on lane one of the drive up for transactions, and the remote lanes are a pneumatic system that a carrier moves through tubing to send in transactions and to send receipts back out. I'm a PLT guy, and am having trouble finding something in the code book that would relate to the equipment I install and service.All of the pneumatic systems work with a series of blower motors that are mounted in the unit at the customer side. The "teller" side is strictly controls that operate the customer unit in regards to moving the carrier and also the audio/video systems that work along with the product. The blower motor packages have large AC motors and a valve that can move from pressure (or blowing) to vacuum (sucking), to move the carrier. Pressure to blow it into the bank, and vacuum to pull it back to the customer unit.With newer systems installation, a licensed electrician is required to mount a receptacle in the customer unit that allows for a standard plug from the customer unit to provide power for the system. This makes a convenient disconnect point for servicing the unit to ensure we're not exposed to high voltage. The older systems, have the mains wires from the breaker panel hooking directly to a circuit board inside with no external shut off points. My question is - what does code say about these systems (in regards to not having an easy disconnect point for servicing like HVAC units)? I have been using a lock out/tag out system on the breaker panel for each customer lane when needing to disconnect the high voltage blower package in order to replace worn out motors.Thank you.Chris G

Chris,You've hit a common problem: finding the right code section can be tricky when dealing with specialized equipment. Here's a breakdown of what code sections likely apply, and how to approach the disconnect issue.

Relevant NEC Articles



Article 430: Motors, Motor Circuits, and Controllers

This is a
major section for you. Since you're dealing with AC motors, Article 430 will govern much of the wiring and overcurrent protection. Pay close attention to:

Part IX: Overload Protection

This details how you protect the motors from overheating due to overloads. Look for proper sizing of overload relays or other protective devices.

Part XI: Motor Control Circuits

This covers the control wiring that operates the motors and valves.


Part X: Disconnecting Means

This is the critical section for your question. It specifies the type and location of disconnecting means (disconnect switches) for motors.

Article 440: Air-Conditioning and Refrigeration Equipment

This article
might be relevant. Even though you're not dealing with refrigeration, the pneumatic systems often use similar motor/blower technology as HVAC. This is helpful to review since it has similar requirements for service disconnects.

Article 100: Definitions

Make sure you understand terms like "Disconnecting Means," "Readily Accessible," and "Accessible." These terms have specific legal meanings within the NEC.

Article 110: Requirements for Electrical Installations

This is a general article, but it lays out the basic rules. Pay attention to:


110.25 Lockable Disconnecting Means

If a disconnecting means isn't readily accessible, it needs to be lockable for safety.

110.26 Spaces About Electrical Equipment

This ensures there is adequate space to safely work around electrical equipment, including the motor and control panels.


Article 620: Elevators and Similar Equipment

While it doesn't sound like it directly applies, sometimes you can find parallels. This article covers the control and safety aspects of elevators, which also use motors and controls for movement.

Regarding the Disconnect Issue

The core issue is the lack of a readily accessible disconnecting means for older systems. Here's what the NEC likely requires, and how to address it:1.

NEC 430.102 Location

Disconnecting means should be within sight from the motor controller (the circuit board/controls that operate the motor) and the motor itself. This means it shouldn't be necessary to go around corners or through doors to reach the disconnect. If it's not in sight, it needs to be lockable per 110.25.
2.


NEC 430.109 Type

The disconnecting means must be a switch (or a circuit breaker) that's horsepower-rated or suitable for motor disconnecting duty. A standard light switch is not acceptable.3.

NEC 430.107 Readily Accessible

Ideally, the disconnect should be readily accessible. This means it can be reached quickly without climbing over obstacles or using tools (other than possibly a key or a latch).

Applying the Code to Your Situation



Older Systems (No External Disconnect)

These are the problem. They likely violate current code. Your lock-out/tag-out procedure is good practice,
but it's not a substitute for a proper disconnect.

Recommendation

Push for upgrades on these older systems.

The safest and best solution is to install a properly sized disconnect switch near the blower motor package.
This switch should be horsepower-rated or suitable for motor disconnecting duty, and should be readily accessible. You may be able to install a small enclosure with a disconnect switch on the unit itself. Alternatively, a disconnect switch could be installed near the unit, but still within sight of the motor and controls. If a disconnect cannot be readily accessible, it must be lockable per 110.25. Newer Systems (Receptacle as Disconnect)

The receptacle approach can be compliant, IF the plug and receptacle are horsepower rated, and accessible. Here are some important points: The receptacle MUST be horsepower-rated for the motor. Standard receptacles are not rated for motor disconnecting. The plug/receptacle MUST be accessible. If the equipment is cord-and-plug connected, the plug and receptacle can serve as the disconnecting means, per 430.109(F).

Documentation

Document your findings and recommendations. If you identify systems that are non-compliant, provide a written report to your company and to the customer, outlining the code violations and recommending corrective action.

Coordination with Electricians

Since a licensed electrician is involved in the installation, work closely with them to ensure all installations meet code. They are ultimately responsible for the electrical safety of the installation.

Important Considerations



Local Amendments

Always check with the local Authority Having Jurisdiction (AHJ) for any local amendments to the NEC. Some jurisdictions may have stricter requirements.

Liability

If someone is injured while servicing a non-compliant system, your company (and potentially you) could be held liable.


Customer Education

Explain the importance of electrical safety to your customers. Many bank managers may not understand the risks associated with non-compliant equipment.*

Training

Ensure your technicians are properly trained on electrical safety procedures, including lock-out/tag-out, and the requirements of the NEC.

In summary, your best course of action is to


Thoroughly review NEC Articles 430 and 440.
2. Document all non-compliant installations.3. Recommend the installation of proper disconnect switches on older systems.4. Ensure newer systems using receptacles are compliant with NEC 430.109(F) and that the receptacles are horsepower-rated.5. Work with a licensed electrician and the local AHJ to ensure all installations meet code.

By taking these steps, you can improve the safety of your work environment and reduce your company's liability. Good luck! Flag for review