Question: Am having a bit of a hard time reading furnace nameplates in residential dwellings. Found this one yesterday that made me do a double take.Assuming all conductors run from the main panel to the furnace are sized correctly, can someone please help me figure out what size breaker to use for this furnace?Thank you!
Okay, let's break down how to determine the correct breaker size for that furnace based on what's typically found on a furnace nameplate. I'll outline the typical process and what the values you're looking for mean. However, I can't give you a definitive answer without the nameplate data itself. Please provide it if you have it.
Here's the general process and what to look for on the nameplate
Find the "Minimum Circuit Ampacity (MCA)" or "Minimum Ampacity"
This is the most important number on the nameplate for sizing the circuit conductors and sometimes the breaker. The MCA is the minimum amount of current the circuit must be capable of handling.2.
Find the "Maximum Overcurrent Protection (MOCP)" or "Max Fuse/Circuit Breaker Size"
This is the maximum size breaker or fuse you're allowed to use. This is the most important number on the nameplate for breaker sizing. Using a breaker larger than this rating is a safety hazard and a code violation.3.
Find the "Rated Voltage"
The furnace will be designed to operate at a specific voltage (e.g., 120V, 240V). Make sure you're using the voltage that corresponds to your electrical service.4.
Find the "Full Load Amps (FLA)" for the blower motor
This is the current drawn by the blower motor when operating at its rated voltage and load. It is not as important as the MCA and MOCP ratings.5.
Find any other motors or components listed: The nameplate may show the amp draw of other components, like an induced draft fan motor, ignitor, or control transformer.
How to Determine Breaker Size
If the MOCP is Listed
Use the
MOCP (Maximum Overcurrent Protection) value directly. This is the largest breaker you can use. You can use a smaller breaker, but never a larger one. If the MOCP is NOT Listed (Less Common)
Use the
MCA (Minimum Circuit Ampacity) value as a starting point. The breaker must be rated at least to carry the MCA rating. Consider motor starting characteristics
Furnace blower motors can have a high inrush current when they start. The breaker must be able to handle this temporary surge without tripping. If the MCA value is very close to a standard breaker size, you might need to go to the next larger standard size to avoid nuisance tripping.
The NEC (National Electrical Code) allows for some flexibility in breaker sizing for motor circuits. However, the breaker must not exceed the maximum allowed by the NEC. A qualified electrician will know the specific rules and calculations.
Example Scenario (Hypothetical Nameplate Data)
Voltage: 120V Minimum Circuit Ampacity (MCA): 12 Amps Maximum Overcurrent Protection (MOCP): 15 Amps Blower Motor FLA: 10 AmpsIn this case, you must use a 15 Amp breaker, and must not exceed 15 Amps.
Important Considerations and Warnings
Always consult a qualified electrician. Electrical work can be dangerous, and improper breaker sizing can lead to fire hazards. A licensed electrician will be able to accurately assess the situation, perform the necessary calculations, and ensure the installation meets all applicable codes. Don't guess or assume. Rely solely on the nameplate data and the advice of a professional. Verify wire size. The wire size must be appropriate for the breaker size you select. Again, an electrician can verify this. Nuisance Tripping
If a breaker trips frequently, it's a sign of a problem (overload, short circuit, or a failing breaker). Do not simply replace it with a larger breaker without diagnosing and fixing the underlying cause.
In summary, find the MCA and MOCP on the nameplate. Use the MOCP if it's there. If not, use the MCA as your minimum, and consult an electrician to determine if a slightly larger breaker is needed to handle motor starting currents. Prioritize safety and code compliance above all else. Providing the nameplate data will allow me to provide much more specific guidance. Flag for review