Question: I am looking at the series rating chart. I am confused by the "poles" column I drew in red:Why does some fuse say 2,3 poles while others just have 3?HQS and QRH2 are both 2 pole breakers yet it says 2 and 2,3 respectfullyLet's say I wanna series rate HQS breaker below with class T fuses. It only says "2" for poles as shown in chart below. Does this mean upstream fuse must only have 2 fuses and that I cannot use 3-phase upstream?
Okay, let's break down the "poles" column in series rating charts and address your specific concerns.
Understanding "Poles" in a Series Rating Context Meaning
The "poles" column in a series rating chart refers to the minimum number of poles that MUST be protected upstream for the series rating to be valid. It doesn't necessarily limit you, it defines the minimum configuration for that rating to apply.
2 vs. 3 vs. 2,3
"2" poles
This means the series rating is valid only if at least two poles are protected upstream. This is common for single-phase and three-phase, 3-wire systems (where there's no neutral).
"3" poles
This means the series rating is valid only if all three poles are protected upstream. This is typically for three-phase, 4-wire systems where all three phases need to be cleared simultaneously for the series rating to apply.
"2, 3" poles
This indicates the series rating is valid if either two poles or three poles are protected upstream. This is a more flexible situation. The manufacturer has tested the series rating with both two-pole and three-pole upstream protection and found it to be acceptable. This often happens when the downstream breaker is robust enough to handle the let-through energy from either configuration.
Addressing Your Specific Questions
HQS and QRH2 Discrepancy
The difference between "2" and "2,3" for seemingly similar 2-pole breakers (like HQS and QRH2) comes down to the specific testing and certification done by the manufacturer. The manufacturer of the QRH2 likely tested and certified the series rating with both two-pole and three-pole upstream protection. The manufacturer of the HQS only certified it with two-pole upstream protection.2.
Series Rating HQS Breaker with Class T Fuses (2 Poles)
Your Question
"If it only says '2' for poles, does this mean the upstream fuse must only have 2 fuses and that I cannot use 3-phase upstream?"
Answer
No, it does not mean you cannot use a 3-phase upstream fuse. It means that if you do use a 3-phase upstream fuse, you must have a fuse element in at least two of the poles to apply the series rating. The manufacturer is saying is that the series rating only applies if at least 2 poles are protected upstream.
Important Considerations
Neutral Conductor
The presence of a neutral conductor is important.
NEC Compliance
Always adhere to the National Electrical Code (NEC) and other applicable local codes.
Manufacturer's Instructions
Follow the specific instructions and ratings provided by the manufacturers of both the circuit breaker and the fuse. The series rating chart is just one piece of the puzzle.
Qualified Person
This type of electrical work MUST be performed by a qualified and licensed electrician who understands electrical systems, codes, and safety procedures. Series ratings are very specific and should only be implemented by someone who fully understands the implications.
In summary, the "poles" column tells you the minimum configuration required for the series rating to be valid, not the maximum or exclusive configuration. Flag for review