Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Bell Box

User: Jimmy7, Location: Boston, MA

Asked on: Monday, October 28, 2024 at 1:23 pm EDT
Answered on: Thursday, March 6, 2025 at 4:30 am EST

Question: Do you need weatherproof wirenuts in a bell box that is mounted outside 2’ above grade. The box has a gasket, so do you need the weatherproof wirenuts? Having some jobsite debate over this one.

Okay, let's break down your grounding plan and your overall strategy for your friend's solar array. You're on the right track with being thorough and wanting to pre-vet your design with the AHJ. That's a smart move.

Analysis of Your Grounding Plan (NEC 2023 Perspective)

Based on your description and aiming for NEC 2023 compliance, here's a breakdown and considerations:1. Grounding Electrode System (GES) at the Array



Requirement

NEC 250.50 requires the use of all available grounding electrodes. This means if there is a metal underground water pipe within 5 feet of the array location or a grounded structural metal framework that's connected to a concrete-encased electrode at the main house, it must be bonded. If you don't have any of these, you can provide 1 or more driven ground rods (see 250.53).


Your Plan

Driving ground rods at the array location is a good start and often required. The key is ensuring they are properly bonded together.

Concerns

The 2023 NEC also calls for a continuous grounding electrode conductor that is connected to all grounding electrodes at the array (i.e. ground rods, and any others that are available in the area).


Recommendation

Ensure you document all available electrodes at the array site.2.

Equipment Grounding Conductor (EGC) from Array to Inverter



Requirement

NEC 690.43 states that metal equipment (module frames, racking, enclosures, etc.) be connected to an EGC that runs
with the circuit conductors.

Your Plan

You propose a #10 green THWN-2 from the array's combiner box back to the main panel.

Concerns



Sizing

The minimum size of the EGC is determined by Table 250.122 in the NEC, based on the rating of the overcurrent protective device protecting the circuit. If your array is 600 volts max, the minimum sizing may be #12 AWG, but you need to check the specific ratings.

Voltage Drop

A 300-foot run, even with a #10,
could introduce voltage drop on the EGC under fault conditions. You want to ensure that the EGC is robust enough to quickly clear a fault. A larger conductor might be a safer, though likely more expensive, bet.

Continuity

Ensure the metal racking system is effectively bonded. Paint, corrosion, or loose connections can defeat grounding. Use appropriately listed grounding lugs/hardware and consider star washers to penetrate coatings.

Parallel Path

You need to ensure that the earth (via the ground rods)
is not the primary path for fault current. The EGC (the #10 or larger green wire) should be the primary fault current path back to the main service.

Recommendation

Carefully calculate the required EGC size based on the overcurrent protection and voltage drop considerations. Consider upsizing the EGC if the cost isn't prohibitive. It adds a safety margin. Ensure the racking system is effectively bonded with appropriate hardware.3.

Module Grounding



Requirement

Modules must be grounded per their listing and instructions. Many modern modules are designed to be grounded by bolting them directly to a properly grounded racking system.

Your Plan

You mention a #6 bare copper bonding each panel and metal parts.


Concerns



Listing Compliance

Ensure your modules are listed for frameless grounding if you choose to mount them without additional grounding hardware. This is the preferred way today to ground the modules.


Hardware Compatibility

Make sure any grounding hardware you use (lugs, screws, etc.) is listed for grounding and compatible with the materials involved (aluminum, copper, etc.).

Recommendation

Review the module manufacturer's grounding instructions very carefully. Use listed grounding hardware.4.

Separation of DC and AC Grounding



Requirement

Inverters usually require separate DC and AC grounding electrode conductors (GECs). Don't bond the DC and AC grounding systems together at the inverter unless specifically instructed by the manufacturer.

Your Plan

It sounds like you're running the DC EGC back to the main panel's grounding electrode system.


Concerns



Inverter Instructions

Double-check the inverter's installation manual regarding grounding requirements.


Recommendation

Follow the inverter manufacturer's grounding instructions precisely.

Is Your Plan Sufficient for a Bid Spec?


Your description is a good starting point, but here's how to improve it for a bid spec:
Be Specific with Materials

Instead of "appropriate ground lugs," specify listed grounding lugs for use with aluminum and copper, rated for direct burial.

Conduit Details

Specify the type and size of conduit you want (e.g., 2" Schedule 40 PVC, direct burial).


Ground Rod Details

Specify the length, diameter, and material (e.g., 8' x 5/8" copper-clad steel).

Manufacturer and Model Numbers

List specific manufacturers and model numbers for key components like the grounding lugs, racking system, and combiner box.


Grounding Hardware

Specify the types of grounding clips and bonding jumpers to be used for connecting modules to the racking system.

Testing

Include a requirement for the installer to perform a ground resistance test after installation to ensure the grounding system is effective. The acceptable resistance value should also be specified.

Grounding for a California Installation

California adopts the NEC, so adherence to the NEC guidelines is essential. California
may have some local amendments. Check with your AHJ, as you plan to, to ensure that there are no additional local grounding requirements specific to your area.

Your Overall Strategy

Your strategy is excellent:1.

Detailed Spec

Creating a detailed spec ensures you get apples-to-apples bids.2.

Component Selection

Choosing components with detailed spec sheets beforehand allows for proper planning and compatibility checks.3.

AHJ Consultation

Meeting with the AHJ
before soliciting bids is crucial. They can identify any local requirements or interpretations that could impact the design and cost.4.

Installer Feedback

Getting feedback from installers
after the AHJ review is a good way to refine the design based on their experience and local market practices.

Summary of Improvements


NEC Compliance

Ensure strict adherence to NEC 2023, especially Article 250 and Article 690, regarding grounding.2.

Grounding Electrode System

Fully document your location for all available grounding electrodes at the array site.3.

EGC Sizing

Carefully calculate EGC size and consider upsizing.4.

Module Grounding

Follow module manufacturer's instructions precisely.5.

Detailed Spec

Add more specific details to your bid spec, as outlined above.6.

AHJ Review:
Prioritize the AHJ review to address local requirements.By following these steps, you'll create a robust and code-compliant grounding system for your friend's solar array and get accurate, comparable bids from local installers. Remember to document everything* thoroughly, including photos of the installation process. This will be helpful for future maintenance and any inspections. Flag for review

Previous Question Next Question