User: photonboy, Location: Berkeley, CA, USA
Asked on: Monday, October 28, 2024 at 1:56 pm EDT
Answered on: Thursday, March 6, 2025 at 4:31 am EST
Question: The only code section I can find that specifically discusses bonding a metal raceway on both ends is 250.64(E) and that seems to only refer to the GEC from a main panel to the Earth.The scenario we encounter every day is a roof j-box with EMT or metallic flex as the home run. Sometimes these can be long runs, over multiple roof planes, many couplings/conduit bodies before arriving at the combiner or inverter down below.We have been asking for these longer runs to be bonded on both ends, in the inverter or combiner AND inside the j-box..We have been getting pushback saying that bonding on only one end is sufficient. My thinking, and my experience, is that some of those conduit connections along the way can be loose (I used to find couplings that the installer forgot to tighten A LOT when doing O&M) and this can compromise the bonding, potentially leaving one side of a run improperly bonded in case of a fault. This can get someone hurt or killed.Wanted to get the thoughts on this subject from other experienced installers, O&M techs and even any inspectors who might be on the forum.Thanks.
You've hit on a common point of confusion and debate in the solar PV industry. Here's a breakdown of the relevant code, best practices, and rationale to help clarify the situation
Understanding the Applicable Code:
250.64(E) is NOT Directly Applicable
As you correctly pointed out, 250.64(E) specifically addresses the Grounding Electrode Conductor (GEC), which runs from the service equipment (main panel) to the grounding electrode (e.g., ground rod). It's about grounding to earth, not bonding metal raceways.
250.92 Bonding of Services
This section applies to metallic raceways that enclose service conductors. While technically not applicable to the PV DC wiring, it serves as a model for good practice. It requires bonding to ensure electrical continuity and low impedance.
250.96 Bonding Other Enclosures
This is your key section. 250.96(A) states: "Metal raceways, cable trays, cable armor, cable sheath, enclosures, frames, fittings, and other metal non-current-carrying parts that are likely to become energized shall be bonded together into an effective ground-fault current path." This is the general requirement for bonding metal enclosures, including raceways used in PV systems.
250.4(A)(5) Electrical Impedance and Clearing Faults
This section highlights the purpose of bonding: to create a low-impedance path for fault current to return to the source, allowing the overcurrent device (fuse or breaker) to operate and clear the fault quickly.
Why Bonding at Both Ends is Generally Preferred (and Often Required)
Effective Ground-Fault Current Path
The core reason for bonding is to provide a low-impedance path for fault currents. Multiple points of bonding ensure that even if one connection becomes loose or corroded, a reliable ground-fault path remains.2.
Mechanical Connections and Conductivity
EMT and metallic flex rely on mechanical connections (couplings, connectors, set screws) to provide electrical continuity. As you've experienced: These connections can loosen over time due to vibration, temperature changes, and improper installation. Corrosion can develop at the joints, increasing resistance. Even when tight, the contact area at these connections can be relatively small, resulting in higher impedance than a solid conductor.3.
Long Runs and Impedance
In longer runs of raceway with multiple couplings, the cumulative impedance of those connections can become significant. Bonding at both ends provides a shorter, more direct path back to the source, lowering the overall impedance.4.
Voltage Drop and Touch Potential
A high-impedance fault path can result in a voltage drop along the raceway. If someone touches a faulted raceway, they could be exposed to a hazardous voltage (touch potential). Good bonding minimizes this risk.5.
Code Interpretation and AHJ Discretion
While the NEC doesn't explicitly mandate bonding at both ends for all metal raceways, the intent of 250.4(A)(5), 250.96(A), and good engineering practice support it. The Authority Having Jurisdiction (AHJ - your inspector) has the final say and can require it based on their interpretation of the code and site-specific conditions.
Arguments Against Bonding at Both Ends (and Why They Don't Always Hold Up)
"One end is sufficient if the raceway is properly installed." While true in a perfect world, real-world installations are rarely perfect, and things change over time. Relying solely on the integrity of every single connection for the life of the system is risky. "It creates ground loops." This is a common concern but often misunderstood. In a properly designed and installed system, bonding at multiple points shouldn't create problematic ground loops. The impedance of the ground path should be low enough to prevent circulating currents from causing issues. Using star grounding techniques and avoiding excessive grounding can help mitigate this risk. "It's too expensive." The cost of adding a few extra bonding jumpers is minimal compared to the potential liability and safety risks of an inadequately bonded system.
Practical Recommendations
Specify Bonding at Both Ends
Your insistence on bonding at both ends is a good practice, especially for longer runs. Clearly specify this requirement in your design documents and installation procedures.
Use Listed Bonding Locknuts/Bushings
When connecting raceways to enclosures, use UL-listed bonding locknuts or bushings. These provide a reliable, low-impedance connection.
Dedicated Bonding Jumpers
For critical applications or when using flexible metal conduit, consider using a dedicated bonding jumper inside or outside the raceway, in addition to the mechanical connections. This provides an extra layer of protection.
Proper Torque and Inspection
Ensure that all connections are properly torqued according to the manufacturer's specifications. Inspect connections during and after installation, and periodically during maintenance.
Continuity Testing
Perform continuity testing (using a low-resistance ohmmeter) to verify the integrity of the ground path. Measure the resistance between various points along the raceway to identify any high-resistance connections.
Consult with the AHJ
If you encounter resistance from installers or have questions about code interpretation, consult with the AHJ (inspector) early in the project. Get their approval for your bonding methods to avoid problems later.
In summary:
While the NEC might not always explicitly require bonding metal raceways at both ends in every situation, the principles of safety, code intent, and best practices strongly favor it, especially for long runs and critical applications like solar PV systems. The small additional cost and effort are well worth the peace of mind and increased safety. By specifying bonding at both ends and ensuring proper installation, you're creating a safer and more reliable system. Flag for review