Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: How to tap a parallel feeder

User: Tank11, Location: CO

Asked on: Monday, October 28, 2024 at 2:49 pm EDT
Answered on: Thursday, March 6, 2025 at 4:31 am EST

Question: Example scenario: 600-amp main service so parallel feeder conductors. Want to line side tap a PV inverter (10 KW in this example). Since there are parallel conductors to tap, is the best method to provide a parallel path from the PV inverter as well for continuity across the service feeder?Or does it not matter, and just tap one of the two parallel feeds?

You're asking about a common but potentially complex scenario. Let's break down the best approach for tapping a PV inverter onto parallel service conductors.

Understanding the Concerns

The primary concern with tapping parallel conductors is maintaining equal current distribution across them. Unequal current distribution can lead to: Overheating

One conductor carries more current than it's rated for, leading to heat buildup and potential failure.


Voltage Drop

Uneven load distribution can cause voltage imbalances.

Nuisance Tripping

Protection devices might misinterpret current imbalances as faults.

The Code Perspective (NEC - National Electrical Code)


The NEC has specific requirements for paralleled conductors, aimed at ensuring equal current sharing. Key sections to consider are:
NEC 310.10(H)

This section outlines the general requirements for paralleled conductors. It stipulates that they must: Be the same length. Be of the same conductor material. Be the same size in circular mil area. Have the same insulation type. Be terminated in the same manner.

NEC 705 (Interconnected Electric Power Production Sources)

This article specifically covers requirements for connecting PV systems and other distributed generation. 705.12 is where connection methods and the 120% rule and 100% rule live.

NEC 230 (Services)

While dealing with service equipment, this article indirectly affects your connection by defining the parameters of the main service.

The Preferred Method: Parallel Tap for the PV Inverter
Yes, the best and generally recommended method is to provide a parallel path from the PV inverter, mirroring the parallel conductors of the service feeder.

Here's why:
Ensures Balanced Current

By tapping both parallel conductors, you help ensure that the PV inverter's output current is distributed proportionally across both conductors. This is crucial for maintaining the integrity of the paralleled conductor system.

Complies with NEC Intent

While the NEC doesn't
explicitly mandate paralleling the PV tap in this specific scenario, it's the method that best aligns with the overall intent of maintaining equal current distribution in parallel conductors.

Reduces Risks

Minimizes the risk of overheating, voltage imbalances, and nuisance tripping due to unequal load sharing.

How to Implement a Parallel Tap
1. Determine PV Output Current

Calculate the maximum output current of the PV inverter. For a 10kW inverter at 240V (split phase), the AC output current would be approximately 41.67 amps (10,000 W / 240 V). (assuming unity power factor)2.

Size the Tap Conductors

The tap conductors from the PV inverter to the parallel service conductors must be sized according to NEC 310, based on the inverter's output current. You'll also need to consider ampacity correction/adjustment factors based on ambient temperature and the number of conductors in a raceway.3.

Use Listed Tap Connectors

Crucially, use listed and labeled tap connectors that are specifically designed for connecting to parallel conductors. These connectors are available from various manufacturers and are designed to ensure a reliable and safe connection. Some are also specifically listed for multiple conductors in a single barrel.4.

Equal Lengths

As much as reasonably possible, keep the tap conductor lengths from the PV inverter to each of the parallel service conductors the same length. This helps further ensure balanced current distribution.5.

Overcurrent Protection

Provide overcurrent protection for the tap conductors at the point where they connect to the parallel service conductors. This is usually done with appropriately sized fuses or circuit breakers. The size of the overcurrent protection will be based on the ampacity of the tap conductors.6.

Location of Connection

The location where you tap the PV inverter into the service conductors will determine the rules you must follow in NEC 705.12. Line side connections typically follow a 100% rule.

Why Not Just Tap One Conductor?


Tapping only one conductor is generally not recommended and can be problematic for the following reasons: Unequal Current

It forces all of the PV inverter's output current to flow through only one of the parallel conductors, potentially overloading it and unbalancing the system.


Increased Risk

Significantly increases the risk of overheating, voltage drop, and nuisance tripping.

Potential Code Violation

While not a direct violation of the letter of the NEC in some cases, it violates the
intent of the paralleled conductor requirements and could be flagged by an inspector.

Important Considerations and Caveats
AHJ Approval

Always consult with your local Authority Having Jurisdiction (AHJ) before making any connections to a service. They may have specific interpretations or requirements.

Engineering Review

For larger PV systems or complex installations, it's always best to have a qualified electrical engineer review the design to ensure it meets all applicable codes and standards.


Load Calculations

Ensure your overall load calculations account for the additional current from the PV inverter, considering both supply-side and load-side limitations.

Service Equipment Rating

Verify that the service equipment (main breaker, busbars, etc.) is adequately rated for the combined load of the existing loads and the PV inverter output.


Feeder Sizing

Ensure that the feeder conductors are adequately sized for the combined load of the existing loads and the PV inverter output. This may require upsizing the feeders.*

Rapid Shutdown

Consider Rapid Shutdown requirements for the PV system based on NEC 690.12 and the AHJ's requirements.

In Summary


When tapping a PV inverter onto parallel service conductors, the best practice is to mirror the parallel configuration and provide a parallel tap for the inverter. This ensures balanced current distribution, reduces the risk of problems, and aligns with the intent of the NEC's requirements for parallel conductors. Always consult with your local AHJ and consider an engineering review for complex installations. Flag for review

Previous Question Next Question