Question: In Massachusetts code says all 15 and 20 amp circuits supplying outlets or devices "in" dwelling units require afci. Would a garage qualify or is this still only GFCI. The NEC definition of dwelling unit no way describes a garage.
You're right to question this. Here's the breakdown based on Massachusetts Electrical Code and common interpretations: Massachusetts Electrical Code (Based on NEC)
Massachusetts adopts the National Electrical Code (NEC) with some state-specific amendments. Therefore, you need to reference both.
AFCI Protection for Dwelling Units (NEC 210.12)
The NEC (and likely the Massachusetts version) does require AFCI protection for 15A and 20A, 120V branch circuits supplying outlets and devices
installed in dwelling units. Definition of Dwelling Unit (NEC Article 100)
The NEC defines a "dwelling unit" as "a single unit, providing complete and independent living facilities for one or more persons, including permanent provisions for living, sleeping, cooking, and sanitation." This definition does not inherently include a garage.
Garages and GFCI Protection
Garages typically require GFCI protection for 125-volt, 15- and 20-ampere receptacles (outlets) based on NEC 210.8(A)(2). GFCI protection is intended to protect against electrical shock hazards in damp or wet locations.
Conclusion
Based on a strict interpretation of the NEC definition of "dwelling unit," a garage is generally NOT considered part of the dwelling unit itself. Therefore, unless the Massachusetts amendments specifically state otherwise, AFCI protection is typically not required for 15 and 20 amp circuits in a detached garage.
Important Considerations and Caveats
Attached Garage
If the garage is attached to the house and has direct access to the living space without going outside, it's more likely to be considered part of the dwelling unit for AFCI purposes, depending on how the local inspector interprets the code and how the garage is wired. The presence of a door to the main living space blurs the line.
Massachusetts Amendments
Crucially, you MUST check the Massachusetts amendments to the NEC. Massachusetts may have added language that expands the AFCI requirements to include attached garages, even if the NEC doesn't explicitly require it. These amendments take precedence over the base NEC.
Local Inspector
The local electrical inspector's interpretation is the final authority. Their interpretation of the code is what matters for compliance.
Best Practice
Even if not required, AFCI protection in a garage is still a good safety practice. Garages are often used for power tools and other equipment that can potentially cause arc faults.*
Combination AFCI/GFCI
It's becoming common to use combination AFCI/GFCI circuit breakers, which provide both types of protection in one device. This simplifies wiring and provides a higher level of safety.
Actionable Steps
Review the Massachusetts Electrical Code Amendments
Find the official Massachusetts amendments to the NEC and carefully read the sections pertaining to AFCI requirements. Look for any language that might include attached garages within the definition.2.
Consult with the Local Electrical Inspector
This is the most important step. Call your local building department and ask to speak to the electrical inspector. Explain your situation (attached or detached garage) and ask for their interpretation of the AFCI requirements in your specific case. They will provide the definitive answer for your area.3.
Consult a Qualified Electrician
A licensed electrician familiar with the Massachusetts Electrical Code can also provide valuable insight and ensure your wiring complies with all applicable regulations.
In summary, while the NEC definition of dwelling unit generally excludes a garage, you must check the Massachusetts amendments and consult with your local electrical inspector to determine the specific AFCI requirements for your garage. Failing to do so could result in failed inspections and rework. Flag for review