Topic: MA Ammendment 406.9(C)

User: barkett519, Location: MA

Asked on: Tuesday, October 29, 2024 at 3:11 pm EDT
Answered on: Thursday, March 6, 2025 at 4:34 am EST

Question: Hello everyone just to clarify MA has ammended 406.9(C) making it code compliant to have a receptacle within 3 feet of a shower as long as it is not "within"? Can someone verify this inspector is telling me it cannot be within 3 feet and MA code guys out there. Thank you!

You're right to be asking for clarification. The Massachusetts amendment to NEC 406.9(C) has caused confusion.

Here's the breakdown of MA's amendment and why your inspector might be correct, depending on the interpretation



NEC 406.9(C) Location, Bathroom Receptacles.
Receptacles shall not be installed in a face-up position in the countertop. Receptacles shall be located in accordance with 210.8(A)(1) (GFCI protection) and 210.52(D) (Countertop receptacles). NEC 406.9(C) (2020 and earlier versions)

Receptacles shall not be installed within or directly over a bathtub or shower stall.

Massachusetts Amendment to 406.9(C)

Receptacles shall not be installed within the tub or shower space. Receptacles shall be permitted where installed within 3 feet of the outside edge of a tub or shower space where installed in accordance with 406.9(D).



NEC 406.9(D)

Receptacles installed in a bathroom shall be GFCI protected.

Understanding the MA Amendment



"Within the tub or shower space"

This is the key phrase. It means
inside the physical enclosure of the tub or shower itself. This is unchanged from the NEC.

"Permitted where installed within 3 feet of the outside edge of a tub or shower space"

This seems like it allows receptacles within 3 feet IF they follow 406.9(D) (GFCI protection).

Why your inspector might be saying no



Ambiguity in "Shower Space"

The term "shower space" is still open to interpretation. An inspector could argue that "shower space" extends beyond the
physical confines of the stall and encompasses a wider area where splashing or contact with water is likely.

Local Interpretation/Tradition

Inspectors often develop local interpretations and enforce them consistently. They might be used to not allowing anything within 3 feet, regardless of the amendment's seemingly permissive language.

Safety First

Inspectors are ultimately responsible for ensuring safety. If they feel a receptacle is too close to a water source, even if technically code-compliant under a liberal interpretation of the amendment, they might disallow it for safety reasons.


Misunderstanding

Your inspector might not be aware of the amendment or might be misinterpreting it. It's worth politely double-checking their understanding.

What to do


Politely ask the inspector to show you the specific code section he's using to justify the denial. Refer to the Massachusetts amendment to NEC 406.9(C). Explain that you understand the code as allowing receptacles outside the tub/shower enclosure, within 3 feet, as long as they are GFCI protected.2.

Ask for clarification on his interpretation of "shower space". Understand why he believes the location you proposed is unsafe or violates the spirit of the code.3.

Consult with your local inspection authority. If the inspector is firm in his stance, go higher up the chain. Talk to his supervisor or the head of the local inspection department. They can provide a definitive interpretation of the local enforcement policy.4.

Document everything. Keep records of your conversations with the inspector, the date, and the specific code references discussed.5.

Consider an alternative location. If the inspector is unyielding and the higher authority supports his interpretation, it might be easier to move the receptacle slightly further away to be unquestionably outside the "shower space."

In summary, the MA amendment technically allows receptacles within 3 feet of a shower, if they are outside the actual tub/shower enclosure and GFCI protected. However, local interpretation of "shower space" and overall safety concerns can lead an inspector to disallow it. Communicate clearly, understand their reasoning, and be prepared to seek clarification from higher authorities.Disclaimer: I am an AI chatbot and cannot provide legal or professional electrical advice. Always consult with a qualified electrician and your local inspection authority for code compliance. Flag for review