User: jerry bass, Location: Florida
Asked on: Tuesday, October 29, 2024 at 5:37 pm EDT
Answered on: Thursday, March 6, 2025 at 4:35 am EST
Question: It is generally understood that emergency generators do not require ground rods and nor main bonding jumpers at the disconnect. This becomes a different scenario when 4 ATS switches are involved. Because the building / Utility neutral gets replace with a generator only return current pathway. And the main bonding jumper to the grounding electrode system is now removed from the system as well. Usually found at the point of main disconnect for the utility feed (Service). Now the ground rod. And potentially other present grounding electrodes need to be bonded to a main bonding jumper at the generator disconnect?
You're hitting on a crucial point about emergency generator installations and the complexities that arise with multiple transfer switches and the potential for creating separately derived systems. Let's break it down
The Basic Understanding (and why it's often misinterpreted):
Emergency Generator without Transfer Switch
In a simple setup where the generator directly powers a few critical loads without disconnecting from the utility, the generator is not a separately derived system. The utility's neutral is still the primary neutral for the whole system. In these cases, a ground rod at the generator and a main bonding jumper at a disconnect at the generator are typically
not required. The existing building grounding electrode system handles the grounding. Transfer Switch - Single Generator, Single ATS
With a single automatic transfer switch (ATS), the generator replaces the utility as the power source. However, in a properly installed ATS, the neutral is typically switched. This means the utility neutral is still connected to the load panel's neutral bus when on utility power. When the ATS switches to generator power, the generator neutral is connected to the load panel's neutral bus. Because the utility neutral is always connected to the load panel neutral bus, this is NOT a separately derived system, so the generator does not require a grounding electrode system (ground rods) or a main bonding jumper.
The Complication with Multiple ATS and Separately Derived Systems
The Core Problem
When you have multiple ATS switches and no shared neutral connection between the utility and the generator system when the generator is running, you can inadvertently create a
separately derived system. This is what you're describing, and this is where the NEC requirements get much more stringent. Why it Matters
A separately derived system must have its own grounding electrode system (ground rods, etc.) and a main bonding jumper. Without it, you risk:
Elevated Ground Potential
Fault current has no clear, low-impedance path back to the generator, increasing touch potential and shock hazards.
Improper Operation of Overcurrent Devices
Circuit breakers and fuses may not trip properly in a fault condition, leading to equipment damage and fire risk.
Harmonic Issues
Separately derived systems can exacerbate harmonic problems if not properly grounded and bonded.
The Scenario You're Describing
You have a situation where the utility neutral is completely disconnected by the ATS switches when the generator is running. The generator effectively becomes the sole source of power and the sole neutral reference for the connected loads. This creates a separately derived system.
NEC Requirements (General - Consult a Qualified Electrician!)
250.30 Grounding Separately Derived AC Systems
This is the key NEC section.
Grounding Electrode System
The generator must have a grounding electrode system. This typically involves ground rods, but can also include building steel, underground water pipes, etc., if available and suitable.
Main Bonding Jumper
A main bonding jumper must connect the generator's neutral conductor to the grounding electrode system at the generator.
Neutral Switching
The design must ensure that only one neutral-to-ground bond exists at any time. The most common method is switching the neutral at the ATS.
Addressing Your Specific Question
"Now the ground rod. And potentially other present grounding electrodes need to be bonded to a main bonding jumper at the generator disconnect?" YES, in the scenario you've described (multiple ATSs creating a separately derived system), the generator must have its own grounding electrode system and a main bonding jumper connecting the neutral to that grounding electrode system. The grounding electrodes at the generator must be bonded together, and the neutral must be bonded to those electrodes via the main bonding jumper.
Important Considerations
Neutral Switching is Critical
The ATS design is paramount. If the ATS doesn't switch the neutral, you are almost certainly creating a separately derived system when on generator power and must follow 250.30.
System Design
The entire electrical system design must be reviewed by a qualified electrical engineer or master electrician familiar with emergency generator installations and separately derived systems. Proper coordination of overcurrent protection is also essential.
Local Codes and Inspections
Always adhere to local electrical codes and requirements, and have the installation inspected by a qualified inspector.
Qualified Electrician
Do not attempt this work unless you are a qualified electrician. Incorrect grounding can be extremely dangerous.
In summary, while emergency generators often don't require ground rods and bonding jumpers, the complexity of multiple ATS switches can easily create a separately derived system that does* require them. It is imperative to evaluate the design and apply NEC 250.30 to ensure a safe and compliant installation. Flag for review