Topic: How do I mate conduit neatly to an Underground Pull box?

User: Installer, Location: DesMoines, Washington

Asked on: Tuesday, October 29, 2024 at 11:08 pm EDT
Answered on: Thursday, March 6, 2025 at 4:36 am EST

Question: I have to mate an existing buried 2" Rigid conduit with conductors to a new 8 foot run of buried 2" Schedule 80 PVC. conduit.This is happening in an empty fenced field.The two sections of conduit have to be joined in an underground enclosure. I found this:Carson™ Light Duty Underground Enclosure Assembly, HDPE, 14 x 19 x 12".What fitting do I need to mate the 2" RGS conduit to the box?What fittings do I use to mate the 2" schedule 80 conduit to the Box?Or should i find something better?

Okay, let's break down the fittings you'll need to connect your 2" rigid galvanized steel (RGS) conduit and 2" Schedule 80 PVC conduit to your Carson enclosure, along with some considerations and potential alternatives.

Understanding the Problem Dissimilar Metals

RGS (steel) and PVC are different metals. Direct burial connections between them can lead to galvanic corrosion over time, especially in damp environments. You need to isolate them to prevent this.


Transition

You're transitioning from a threaded RGS system to a potentially glue-connected PVC system.

Underground Enclosure

The Carson box provides a protected space for this transition.


Schedule 80

The heavy-wall Schedule 80 PVC gives you extra physical protection.

Fittings Needed


Here's a breakdown of the fittings you'll need per conduit: For the 2" RGS Conduit



Insulated Grounding Bushing (2")

This is absolutely crucial.

Purpose

Threads onto the end of the RGS conduit. It has an insulated throat to protect the conductor insulation as it enters the enclosure. It also provides a lug for connecting a grounding conductor.


Why it's important

Prevents sharp edges of the RGS conduit from damaging wire insulation, and gives you a solid grounding point.

Example

A 2" grounding bushing listed for use with RGS conduit. Many brands make these (e.g., Thomas & Betts, Appleton, Bridgeport). Make sure it is
insulated.

Male Adapter (2")
: This will thread into the grounding bushing. For the 2" Schedule 80 PVC Conduit



PVC Terminal Adapter (2")

This fitting allows you to adapt the PVC conduit to a female threaded connection.

Purpose

Glues to the end of the PVC conduit, and has male threads on the other end.


Why it's important

It provides a secure and watertight connection to the enclosure.

Example

A 2" PVC Terminal Adapter, Schedule 80. Again, look for reputable brands like Carlon, Cantex, or IPEX.


Locknut (2")

Slides onto the terminal adapter to lock the fitting to the enclosure.

O-Ring (2")

This provides a seal on the male adapter to keep water out of the enclosure.

Assembly Steps (Per Conduit)
1. RGS Conduit

Thread the Insulated Grounding Bushing onto the end of the existing 2" RGS conduit. Tighten securely. Thread the male adapter into the grounding bushing.2.

PVC Conduit

Clean the end of the 2" Schedule 80 PVC conduit and the inside of the PVC Terminal Adapter with PVC cleaner/primer. Apply PVC cement to both surfaces and join the conduit and adapter. Hold firmly until the glue sets (follow the cement manufacturer's instructions). Insert the PVC terminal adapter into the enclosure. Secure with a locknut and O-Ring.3.

Inside the Enclosure



Grounding

Connect a grounding conductor (sized appropriately for your circuit) to the grounding lug on the insulated grounding bushing. This grounding conductor should then be bonded to the enclosure's grounding point (if it has one) and connected to the overall grounding system.

Wire Management

Carefully pull the conductors through the fittings and into the enclosure. Leave enough slack for connections and future maintenance.

Important Considerations and Alternatives
Enclosure Size

The 14x19x12" Carson box is relatively small. Make sure you have enough room to make your splices safely and according to code. Consider a larger enclosure if space is tight. It's always better to have too much space than not enough.

Enclosure Material

HDPE (High-Density Polyethylene) is durable and resistant to chemicals in the soil. However, ensure the enclosure is rated for direct burial and has the appropriate load rating for your application (e.g., if it will be under vehicular traffic).


Direct Burial Splice Kits

Instead of an enclosure, you could consider using direct burial splice kits. These are specifically designed to encapsulate splices in a watertight and corrosion-resistant material. The downside is that once the splice is made, it's very difficult to access again. Examples include resin-filled kits or heat-shrink kits. This is a different approach than using an enclosure, and you'd need appropriate connectors for your conductors.

Grounding Electrode Conductor (GEC)

If the RGS conduit is serving as the grounding electrode conductor (connecting to a ground rod or other electrode), you need to ensure the grounding path is continuous and meets code requirements. Using insulated grounding bushings and properly bonding everything is crucial. Consult with a qualified electrician if you're unsure about this.


Local Codes

Always check your local electrical codes. They may have specific requirements for underground installations, materials, and grounding.

Professional Help

If you're not comfortable with electrical work or grounding requirements, it's best to consult a qualified electrician. Improper wiring can be dangerous.


Conduit Sealant/Duct Seal

Consider using duct seal around the conduit entries to the enclosure after everything is installed. This adds an extra layer of protection against water and debris.

In Summary


Your core components are: RGS Side

Insulated Grounding Bushing, Male Adapter, grounding conductor.


PVC Side

PVC Terminal Adapter, Locknut, O-Ring.*

Enclosure:
Carson box (or a similar direct burial enclosure), properly sized.Make sure all fittings are appropriately sized (2") and rated for underground use. Prioritize safety, proper grounding, and code compliance. If in doubt, consult a qualified electrician. Flag for review