Topic: Sizing Conductors based on nameplate FLA for motor load

User: Mustang125, Location: New Hampshire

Asked on: Wednesday, October 30, 2024 at 7:58 am EDT
Answered on: Thursday, March 6, 2025 at 4:36 am EST

Question: I have heard before that for AC units you can size the wire based on the FLA on the nameplate and not based on OCP, so I needed to know for myself so I started digging and watched some of mikes videos and it does indeed appear that way. (although even with his code references I still cant find where is clearly states this) but beside that, my current situation is a compressor load which id consider a motor load and was wondering if the same rules can be applied because it has a nameplate. I went to 430.6 and it seems like if the motor is over 1200rpm then you CANT size the conductors based on the FLA on the nameplate, so id have to size the conductors to the OCP, am I reading this right? I have attached the nameplate in question.

You're on the right track with your thinking and your research. Let's break down how the NEC applies to your compressor motor

Understanding the Code Sections
430.6 Using Full-Load Current

This is the key section you're looking at. It dictates how you determine the current used for calculations.


430.6(A)(1) General Motor Applications

This section says that in general, you use the tables in Article 430 (specifically Table 430.248 for single-phase, Table 430.250 for three-phase, etc.) to determine the full-load current for calculations.

430.6(A)(2) Hermetic Refrigerant Motor-Compressors



THIS IS YOUR APPLICATION.
This section is specifically for hermetic refrigerant motor-compressors. It states: "Currents shall be determined using the rated-load current listed on the nameplate of the motor-compressor assembly."Analyzing the Nameplate

Your nameplate is for a hermetic refrigerant motor-compressor. Key items: RLA (Rated Load Amps)

6.4 Amps


LRA (Locked Rotor Amps)

34.2 Amps

Voltage

208-230V


Phase

1

RPM

Not listed (we'll address this below)

Applying the Code to Your Situation
1. Conductor Sizing (430.22)

For a single motor, the conductors supplying the motor-compressor must have an ampacity of

at least 125% of the rated-load current (RLA) on the nameplate
(430.22(A)). In your case: 6.4 Amps 1.25 = 8 Amps. You need conductors rated for at least 8 Amps. This means you can use #14 AWG copper THHN since it is rated for 15 amps at 90°C.
2. Overcurrent Protection (OCPD) - Short Circuit and Ground Fault Protection (430.52)



430.52(C)(1) Single Motor

Generally, the OCPD should not exceed the values in Table 430.52.


Table 430.52

This table gives you maximum percentages or values based on the motor type and OCPD type. We need to look at the "Hermetic Refrigerant Motor-Compressor" row. Note that it gives a maximum percentage.

Inverse Time Breaker

The maximum is 175% of the rated-load current or branch-circuit selection current (whichever is greater)

In your case: 6.4 Amps
1.75 = 11.2 Amps. You can use a 10 or 15 Amp breaker. The code gives maximum values.


IMPORTANT

The code requires you to use the
smallest OCPD that will allow the motor to start and run (430.52(C)(1) Exception No. 1). If a 10 Amp breaker trips on startup, you can increase to a 15 Amp breaker (provided your wire is rated to handle it).3.

Motor Overload Protection (430.32)

This is separate from short-circuit/ground-fault protection. It protects the motor from running at a sustained overload. This is often built into the motor-compressor assembly itself (an internal thermal overload).

430.32(A)(1)

The overload protection shall trip at no more than 125% of the RLA.
Your motor-compressor will very likely have built-in overload protection so this is more for informational purposes.

Regarding the RPM and the 1200 RPM ExceptionThe exception you are mentioning is for a motor driving a power electronic drive system. The exception is also only applied if the nameplate does not provide RLA for that specific motor, and the exception is applied in 430.6(A)(1). This section does not apply to your motor compressor.

Summary for Your Compressor1.

Conductors

Minimum #14 AWG copper THHN (rated at least 8 Amps).2.

OCPD

10 Amp or 15 Amp breaker. Start with 10A.3.

Overload Protection

Likely internal to the motor-compressor.

Important Notes



Local Amendments

Always check with your local jurisdiction. They may have amendments to the NEC.


Good Workmanship

Ensure all connections are tight and properly made.

Safety First

Disconnect power before working on electrical equipment.By following these steps and understanding the relevant sections of Article 430, you can properly size the conductors and OCPD for your compressor motor.