Topic: When should arc flash label be applied

User: Isaiah, Location: Baton Rouge

Asked on: Wednesday, October 30, 2024 at 9:15 am EDT
Answered on: Thursday, March 6, 2025 at 4:36 am EST

Question: We have a designer who is saying the arc flash labeling can’t be applied until commissions is complete, but the engineering company has already performed the official arc flash StudyIs it really necessary to wait ?

It's generally NOT necessary to wait for commissioning to be completely finished to apply arc flash labels, as long as the arc flash study is based on the "as-built" configuration and operating modes. Here's a breakdown of why and when you might need to wait

Why you usually don't have to wait:
Arc Flash Study is the Key

The arc flash study is the foundation. If it's based on the final, "as-built" electrical system configuration, proper coordination, and representative operating conditions, it provides the necessary data (incident energy, working distance, PPE requirements, etc.) for the labels.


Commissioning Focus

Commissioning is about verifying the system works as designed, including testing and startup of equipment. It doesn't fundamentally change the electrical system design in a way that would invalidate the arc flash study, provided the study accounted for the range of expected operating conditions.

Safety First

Arc flash hazards exist from the moment the system is energized. Waiting to label until commissioning is fully complete exposes workers to unnecessary risk.


Commissioning May Never Be "Done"

Commissioning is often an ongoing process, with systems being fine-tuned and optimized over time. Waiting for that final state would delay labeling indefinitely.

Labeling is a Legal and Ethical Obligation

OSHA (in the US) and similar regulations in other countries require arc flash labeling. Delaying it puts the employer in potential non-compliance.

When you
might need to wait (or, more accurately, re-evaluate)



Significant System Changes During Commissioning

If commissioning reveals substantial deviations from the "as-built" system used for the arc flash study (e.g., changes in protective device settings, unexpected paralleling of transformers, addition of new loads not considered in the study), you must update the study and the labels.

Incorrect "As-Built" Information

If the arc flash study was performed using incorrect or incomplete "as-built" information, the results will be invalid, and labels should not be applied until the study is corrected.


Unusual or Complex System Operations

If commissioning reveals operating scenarios that were not modeled in the arc flash study and could significantly affect arc flash results, further analysis may be required. For example, certain transfer schemes not working as designed could cause higher fault currents.

Temporary System Configurations

If the system will be operated in a temporary configuration during commissioning (e.g., with certain protective devices bypassed), labels appropriate for that configuration should be used
temporarily. Once the system is returned to its normal configuration, the permanent labels can be applied.

Commissioning Includes Protective Device Testing

Protective device testing can show if settings were changed or if devices are non-functioning which can lead to higher incident energy during arc flash events. If this occurs, labels cannot be applied until the protective devices are functional and the system re-studied.

Arguments to Make to the Designer



Propose a Phased Approach

Install labels based on the current arc flash study results. If commissioning reveals changes that impact the study, update the labels accordingly.


Stress the Safety Imperative

Emphasize that delaying labeling puts workers at risk and potentially violates safety regulations.

Review the Arc Flash Study Scope

Confirm with the engineering company that the arc flash study adequately addresses the expected operating conditions and commissioning activities.


Implement Temporary Labeling (if needed)

If temporary system configurations are necessary during commissioning, create temporary labels specific to those configurations.

Get a Written Confirmation

If the designer insists on waiting, get it in writing, along with a clear explanation of the specific concerns and how commissioning will address them. Consult with a qualified safety professional or electrical engineer to assess the validity of the concerns.


Document the Decision

Document the decision-making process, including the rationale for delaying labeling (if that's the ultimate outcome), the mitigating measures taken to protect workers in the meantime, and a plan for when the labels will be applied.

In Summary:


The default position should be to label electrical equipment as soon as a valid arc flash study based on the "as-built" system is available. Only delay labeling if there are concrete reasons to believe that commissioning will significantly alter the system in a way that invalidates the study results. Prioritize safety and regulatory compliance.You need to have a conversation with both the designer and the engineering company who performed the study to fully understand their perspectives. Get clarification on what specific aspects of commissioning the designer is concerned about, and whether those concerns are valid and will impact the arc flash study results. Ultimately, the safety of personnel working on the electrical system should be the primary consideration. Flag for review