Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Current thoughts on VFD conductor types

User: Electromatic, Location: Virginia

Asked on: Wednesday, October 30, 2024 at 9:33 am EDT
Answered on: Thursday, March 6, 2025 at 4:37 am EST

Question: I'm reviewing plans for an upfit of a wastewater pump station that will include three 150HP motors run from VFDs. The distance from the drives to the motors is around 100'. What (if any) is the current consensus on conductor types on VFD outputs? I think VFD cable is probably overkill and would be difficult to install in the existing/re-used conduits. I am, though, considering recommending or specifying that XHHW/XLPE be used.

You're right to be thinking critically about conductor types for VFD outputs, especially with a 100' run. While VFD cable might be theoretically the best, practicality often dictates a different approach. Here's a breakdown of considerations and the current (and evolving) consensus

Key Concerns with VFD Outputs:
Reflected Waves (Standing Waves)

VFDs output a rapidly switching PWM (Pulse Width Modulation) signal. This can create voltage reflections on long cable runs, leading to voltage peaks that exceed the motor's insulation rating. These voltage spikes damage the insulation of the motor and create premature motor failure.


Harmonic Distortion

VFDs generate harmonics, which can interfere with other equipment and potentially overheat conductors and transformers.

EMI/RFI

The high switching frequencies can radiate electromagnetic interference (EMI) and radio frequency interference (RFI).


Capacitive Coupling

Long runs of cable create capacitance, leading to leakage currents and potentially increased common-mode voltage.

Grounding

Proper grounding is critical to mitigate the effects of harmonics, EMI, and common-mode currents.

Why VFD Cable is Often Recommended (But Not Always Necessary)



Shielding

VFD cable typically has a braided or foil shield that is designed to contain EMI/RFI and reduce capacitive coupling.

Low Capacitance

VFD cables are often designed with lower capacitance per foot compared to standard conductors.


Voltage Rating

VFD cables are often rated for higher voltages, important for mitigating voltage spikes.

Symmetrical Ground

Most VFD cables incorporate a symmetrical grounding arrangement that provides a low impedance grounding path that is equidistant from each phase conductor.

Why XHHW/XLPE Might Be a Good Compromise



Insulation

XHHW/XLPE insulation is more resistant to heat and moisture than THHN/THWN.

Cost-Effective

It's significantly cheaper than VFD cable.


Easier Installation

It's more flexible and easier to pull through existing conduit than VFD cable.

Adequate for Many Applications

When implemented properly and with supplemental measures (described below), XHHW/XLPE can be sufficient for runs of moderate length (like 100 feet).

Recommendations (If XHHW/XLPE is Used)


Motor Insulation

The most critical step is to verify that the motors are inverter-duty rated. Inverter-duty rated motors have robust insulation systems specifically designed to withstand the voltage stresses caused by VFDs. Look for motors that meet NEMA MG1 Part 31 or Part 30 (for older motors). Do not use motors that are not specifically rated for VFD use!2.

Output Line Reactors/Load Reactors

Installing line reactors on the output of the VFD and
before the conductors to the motor is a good idea for motor runs that are less than 100 feet. However, for motor runs greater than 100 feet, load reactors should be installed at the motor terminals. These will: Reduce voltage rise, which can protect the motor insulation system Reduce motor noise Reduce common-mode voltage Reduce harmonics injected back into the system Reduce dV/dt stresses on the motor windings3.

Output Filters (Sine Wave Filters or dV/dt Filters)

These can be expensive, but they are the most effective way to mitigate voltage reflections and EMI/RFI. They essentially clean up the PWM signal from the VFD to be almost a sine wave. These are typically used on very long cable runs or when interference with sensitive equipment is a major concern. While perhaps overkill for your situation, they should be considered if you encounter issues later. dV/dt filters are effective up to 500 ft.4.

Proper Grounding is Critical



Dedicated Ground Conductor

Run a separate, insulated ground conductor (sized according to code)
along with the phase conductors. Do not rely solely on the conduit for grounding, especially if it's an older system with potentially corroded joints.

Multiple Grounding Points

Ground the VFD enclosure and the motor frame directly back to the main grounding electrode system.

Minimize Ground Loops

Avoid creating ground loops by ensuring that all grounding paths are short and direct.5.

Conduit Fill

Keep conduit fill within code limits to avoid overheating.6.

Keep Conductors Together

Run all conductors (phase and ground) together in the same conduit. This helps to balance the magnetic fields and reduce EMI.7.

Over-Sizing Conductors

While not always required, consider over-sizing the conductors slightly (e.g., going from the minimum size allowed by code to the next larger size). This will reduce voltage drop and provide some extra capacity for harmonic currents. However, remember to verify conductor temperature rating.8.

Check with the VFD Manufacturer

The VFD manufacturer's documentation is often the best place to find information on proper wiring, grounding, and filtering recommendations.

When VFD Cable is Still Recommended/Required



Long Cable Runs

Generally, for runs significantly longer than 100 feet (e.g., 200+ feet), VFD cable becomes more important.

Sensitive Environments

If the installation is near sensitive electronic equipment (e.g., medical devices, precision instrumentation), VFD cable is a good idea to minimize EMI/RFI.


Motor Warranty Requirements

Some motor manufacturers may require VFD cable to maintain the motor warranty.

High-Performance Applications

In applications where precise motor control is critical, VFD cable can help to minimize noise and improve performance.


Manufacturer recommendation for cable type.
In summary

For your 100-foot run, XHHW/XLPE conductors can be a reasonable compromise,

if
: Inverter-duty motors are used. Output line/load reactors are installed.* Proper grounding practices are followed.Your Action Items


Confirm motor insulation rating

Verify that the motors are inverter-duty rated (NEMA MG1 Part 31).2.

Consider Output Reactors

Include output load reactors in the design.3.

Review Grounding Plan

Develop a detailed grounding plan and ensure it is followed meticulously.4.

Consult with a qualified engineer

If you have any doubts or concerns, consult with a qualified electrical engineer who has experience with VFD installations.5.

Check with VFD Manufacturer:
Confirm recommendations for cable type for the VFD that is being used.By carefully considering these factors, you can make an informed decision about the best conductor type for your VFD application and ensure reliable and long-lasting performance. Remember, the goal is to mitigate the potential problems associated with VFD outputs while balancing cost and practicality. Good luck! Flag for review

Previous Question Next Question