User: batese, Location: Pennsylvania

Asked on: Wednesday, October 30, 2024 at 12:12 pm EDT
Answered on: Thursday, March 6, 2025 at 4:38 am EST

Question: Does anyone have any experience using flex cord in accordance with section 501.140 of the NEC? In particular I am looking to use flexible fieldbus (RS-485) cable in a C1D1 location but have not had any luck in understanding what cable would be acceptable/suitable. Is there a special cable for 501.140 that I should be looking into? I found some good information about MC-HL, ITC-HL and TC-ER-HL cables for haz loc, but I was not able to find much information for cabling acc to 501.140. Any help would be much appreciated.

You're diving into a complex and often misunderstood part of the NEC. Section 501.140, "Flexible Cords, Class I, Division 1," is indeed restrictive, and finding the right cable for Fieldbus (RS-485) in a Class I, Division 1 location requires careful consideration. Let's break down the key points and address your concerns

Understanding 501.140: The Strict Requirements

The intent of 501.140 is to minimize the use of flexible cords in Class I, Division 1 locations. It acknowledges that sometimes you need to use a flexible cord, but it severely restricts the types allowed: Approved for Extra-Hard Usage

The cord
must be approved for extra-hard usage. This is typically identified by markings like "S," "SO," "ST," "STO," "SE," "SEO," "SEOO," "SJ," "SJO," "SJOW," "SJE," "SJEO," "SJEOO," "SV," "SVO," "SVTOO," or similar designations found in Article 400.

Grounding Conductor

The cord must contain an equipment grounding conductor (green wire).

Terminations

The cord
must be terminated with fittings approved for Class I, Division 1 locations. This is a critical point and often overlooked.

Attachment Plugs

Attachment plugs and receptacles, if used, must be approved for Class I, Division 1 locations, be of the interlocking type, and prevent plugs from being inserted or withdrawn while the circuit is energized.

Why Finding a "Special" Cable is Difficult (and Likely Unsuccessful)


The challenge you're facing is that there's no specific "501.140 cable." The NEC relies on the existing cable markings and standards (like the "S" type cords) and then requires that the entire assembly (cable + fittings) be approved for the location. Standard RS-485 cable will typically not qualify. Normal RS-485 cable, or even shielded RS-485 cable, doesn't usually have the "extra-hard usage" rating required by 501.140. Fittings are Key

Even if you could find an RS-485 cable that somehow met the extra-hard usage requirement, finding suitable Class I, Division 1 fittings for small-diameter RS-485 cable is a major obstacle. Most Class I, Div 1 fittings are designed for larger power cables.

Your Options (and Why They're Limited)


Eliminate the Need for Flexible Cord

This is the best option if at all possible. Can you run rigid conduit all the way to the device? Can you use a junction box close to the device and run a short, approved flexible conduit with explosionproof fittings to the device?2.

Consider ITC-HL

You mention ITC-HL. This might be a better route than trying to shoehorn RS-485 cable into 501.140. If you can find an ITC-HL cable that meets your data transmission needs, you could run it as described in Article 727, up to the point where you need a flexible connection. Then, you still face the 501.140 challenge for that short flexible section. Note: ITC-HL is for instrumentation only, not a general signal cable.3.

MC-HL Cable (with a very short flexible section)

Similar to ITC-HL, you might be able to use MC-HL for the main run and then have a very short section of approved flexible cord (with proper fittings) only for the final connection. However, finding MC-HL cable suitable for data transmission is also unlikely.4.

Intrinsically Safe Systems (Article 504)

If possible, the best solution is to use an intrinsically safe (IS) RS-485 system. This requires specific IS barriers and IS-rated devices but eliminates the need for explosionproof enclosures and the restrictions of 501.140. IS systems are specifically designed for hazardous locations and provide a much safer and often more cost-effective solution in the long run.
5.


Purged/Pressurized Enclosures (Article 502)

If you need to use standard (non-IS) RS-485 equipment, you can consider housing it in a purged and pressurized enclosure. This technique keeps the hazardous atmosphere out of the enclosure, allowing the use of ordinary wiring methods inside.

Key Considerations for Any Approach



Authority Having Jurisdiction (AHJ)

Always consult with your local electrical inspector (AHJ). They have the final say on what's acceptable in your location. Get their feedback early in the design process.

Documentation

Thoroughly document your design, including cable specifications, fitting certifications, and compliance with the NEC.

Manufacturer's Instructions

Follow the cable and fitting manufacturer's instructions
exactly.

In Summary:


Using flexible cords in Class I, Division 1 locations per 501.140 is difficult for data cables like RS-485. A
much better approach is to try to eliminate the need for a flexible cord altogether, or use an intrinsically safe system. If you absolutely must use a flexible cord, focus on: Finding the shortest possible flexible cord section. Ensuring the cord is approved for extra-hard usage. Using Class I, Division 1 rated fittings designed for the specific cord type.* Consulting with your AHJ early and often.Good luck! Let me know if you have further questions. Flag for review