User: ctaylo360860, Location: colorado
Asked on: Wednesday, October 30, 2024 at 12:35 pm EDT
Answered on: Thursday, March 6, 2025 at 4:38 am EST
Question: I have to run some underground over to a remote distribution panel in a house. My plan is to set a j box on the rim joist and want to make sure I have it sized correctly.I will be running - 1/0,1/0,1/0 aluminum triplex with a #8 copper egc inside of 2”pvc from 100 amp breaker inside a 200a service disconnect to a 16”x16”x6” j box. I planned on punching a hole in the rim joist coming out the back of the box with a connector and switching to 1/0,1/0,1/0,#2 ser aluminum and getting it inside the existing 100amp panel through the crawl space…This will be and angle pull with 2” being the largest racewayI believe 314.24 explains the j box doesn’t need to be bigger than 6x the largest raceway entering the box. So my minimum size would be 6x2”=12”Looks like I could use a smaller box but don’t want to have trouble putting the cover on. Does this seem like I have an accurate understanding or have I missed something ?Any and all help is appreciated greatly thanks!
You've done a pretty good job outlining the calculation! However, there are a couple of critical details in the NEC that you need to consider that will likely affect your junction box size and the way you transition your conductors.
Here's a breakdown and clarification of the code requirements, along with some practical considerations
1. Junction Box Sizing: 314.28 (Angle or U-Pull) Your understanding of 314.24 is for straight pulls only. You're planning an angle pull, so 314.28 applies. 314.28(A)(2): Angle or U Pulls
The distance between each raceway entry inside the box and the opposite wall of the box shall not be less than six times the trade diameter of the largest raceway in a row or column on the wall or walls of the box from which the pull is made. If angle pulls are made from more than one row or column, the distance between each raceway entry and the opposite wall of the box shall not be less than six times the trade diameter of the largest raceway in the row or column from which the pull is made.
This means the distance from the entry point of your 2" conduit to the opposite wall of the box must be at least 6 x 2" = 12". Since you are pulling at an angle, this will be the minimum diagonal measurement inside your box. 314.28(A)(2)(B): Additional Requirements
The distance between raceway entries enclosing the same conductor shall not be less than six times the trade diameter of the larger raceway. This applies if you have two or more raceways entering the box on the same side.
2. Conductor Sizing
The aluminum conductors can be properly sized by using the 75 degree column of table 310.16. 1/0 Aluminum is good for 100 amps in the 75 degree column. The #8 ground is sufficient for a 100 amp circuit. (250.122)
3. Conductor Termination and Material Compatibility (Important!) Aluminum to Copper Connection
This is CRITICAL. You absolutely CANNOT directly connect aluminum conductors to copper conductors inside the junction box. This dissimilar metal connection is a recipe for corrosion and failure. The same holds true for the grounded conductor! Solution: Listed Connectors. You MUST use connectors specifically listed and labeled for joining aluminum to copper conductors. These connectors typically use a corrosion-inhibiting compound and provide a mechanically sound and electrically reliable connection. Popular brands include Polaris connectors or similar AL/CU rated lugs. Termination at the Remote Panel
The remote 100A panel must be rated for aluminum conductors. Most modern panels are, but double-check the label. If not, you'll need AL/CU lugs in the panel as well.
4. Transition to SER Cable The SER cable is not in conduit. The SER cable, even though is has an overall jacket, is essentially three insulated conductors that are exposed to the elements and physical damage. Therefore you need to transition to a wiring method such as THWN or XHHW conductors installed in a raceway such as PVC or EMT. This is required to meet the requirements of physical protection. The size of the EGC The #2 copper EGC is not sufficient for the remote 100 amp panel. Use table 250.122 to size the ground wire and install inside the raceway.5. Physical Protection The PVC conduit exiting the j box and running down the rim joist will need to be properly strapped to the rim joist in accordance with 352.30Recommendations and Clarifications Increase Junction Box Size
While your 16x16x6 box might technically meet the minimum size requirements, it will be extremely tight. Consider going larger – something like 24x24x6 or larger. This will make your life much easier during installation and allow for better conductor bending radius.
Layout and Connector Placement
Plan the layout of your connectors before drilling any holes. Think about conductor bending radius and how easily you can make the connections.
Aluminum vs. Copper Wire
Is there a specific reason you are switching to copper SER cable? If not, consider staying with aluminum conductors all the way to the panel. This simplifies the connection process and reduces the number of transitions you need to make. Keep in mind that SER is not typically rated for wet locations.
Strain Relief
Make sure your PVC conduit is securely attached to the junction box with a connector that provides strain relief. The SER cable also needs proper strain relief at the point where it enters the crawl space.
NEC Reference
When discussing this with an inspector, be prepared to cite specific NEC articles. They will likely focus on 314.28, 110.3(B) (listed and labeled equipment), and potentially 300.4 (protection of conductors).
Example Scenario
Let's say you stick with aluminum conductors the entire run to the remote panel.1. Install your 2" PVC conduit through the rim joist and into the junction box.
2. Install appropriately sized aluminum conductors (1/0 AWG).3. Terminate the aluminum conductors to appropriately sized AL/CU lugs.
4. Continue the run to the remote panel with THHN Aluminum in a 2" PVC.5. Terminate conductors into the panel using the manufacturer's listed lugs.
IMPORTANT REMINDER: Electrical work can be dangerous and requires adherence to the NEC and local codes. When in doubt, always consult with a qualified electrician. Local jurisdictions may have amendments to the NEC. Check with your local building department.* Always de-energize circuits before working on them.By following these guidelines, you can ensure a safe, compliant, and reliable installation. Good luck! Flag for review