Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Grounding Parallel

User: DasMrDomo, Location: FL

Asked on: Wednesday, October 30, 2024 at 3:20 pm EDT
Answered on: Thursday, March 6, 2025 at 4:38 am EST

Question: Hi Folks,I've ran into a situation with my local building official, and I would love some input on the subject matter.Scenario:400Amp service being fed by (2) Sets of (4-wire) 3/0 Cu.Based off NEC 250.66 and the cross sectional area, should the ground be based on number of sets, thus (2) 3/0 Cu.ORShould it be based on total wires, thus (8) 3/0 Cu.Any and all input would be appreciated.

Okay, this is a common point of confusion and often misinterpreted. Here's the breakdown, referencing the relevant NEC sections and clarifying the reasoning

The Key: The Grounding Electrode Conductor (GEC) Size is Based on the Size of the Service-Entrance Conductors, Not the Total Number of Wires.
NEC 250.66: Grounding Electrode Conductor for AC Systems. This section specifically dictates how to size the Grounding Electrode Conductor (GEC) based on the size of the service-entrance conductors. Crucially, it does not say to multiply based on the number of parallel conductors. NEC 250.64(D): Parallel Conductors

While this section addresses running GECs in parallel under certain conditions, it doesn't change the fundamental principle that the size of the GEC is determined by the service-entrance conductors. It's for situations where you physically need to run a GEC in parallel (e.g., difficult physical routing, extremely high fault current).

How to Determine the Size of the GEC for Your Scenario


Identify the Service-Entrance Conductor Size

You have (2) sets of 3/0 Copper conductors in parallel. Each set constitutes a service-entrance conductor.2.

Use Table 250.66

Look up 3/0 Copper in Table 250.66. The required GEC size for a 3/0 Cu service-entrance conductor is

#4 Copper
.3. Answer

You would need (2) #4 Copper grounding electrode conductors. One for each set of 3/0 conductors.

Why Not Based on Total Wires (8 x 3/0)?
Redundancy

The GEC is sized to carry fault current back to the source. The NEC assumes that a fault will occur in
one set of service-entrance conductors at a time. It doesn't assume a simultaneous fault in all conductors.

Practicality

Imagine the absurdly large GEC that would be required if you had to base the sizing on the total cross-sectional area of all conductors in parallel! It would be impractical and unnecessary.

In Summary

Your Grounding Electrode Conductor (GEC) should be sized based on the size of each service-entrance conductor set (3/0 Cu in your case), not the total number of conductors. Therefore, each set requires a #4 Copper grounding electrode conductor.

Recommendations


Politely and Respectfully Discuss with the Building Official

Explain your understanding of NEC 250.66 and how it relates to parallel conductors. Cite the code sections.
2.


Seek a Second Opinion

If the building official remains unconvinced, consider getting a written opinion from a qualified electrical engineer or a nationally recognized testing laboratory (NRTL).3.

Documentation

Keep thorough records of your communication and the code sections you relied upon.

Important Considerations



Local Amendments

Always be aware of any local amendments to the NEC that may apply in your jurisdiction.


Qualified Electrical Professional:
If you're not a qualified electrical professional, it's always best to consult with one for this type of work.This is a common misunderstanding, and a clear explanation of the code requirements should help resolve the issue. Good luck! Flag for review

Previous Question Next Question