Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Addition to Existing Building - Service is in Existing Building - Is a UFER required for the addition?

User: Jonny Quest, Location: Illinois

Asked on: Wednesday, October 30, 2024 at 4:14 pm EDT
Answered on: Thursday, March 6, 2025 at 4:38 am EST

Question: An addition is proposed to an existing building, and the existing service is in the existing building. Are we still required to provide a concrete-encased electrode in the footing of the new addition? If so, how is the UFER connected to the existing service?ThanksJQ

Let's break down the requirement for a concrete-encased electrode (Ufer ground) in building additions and how to connect it to an existing service

Is a Concrete-Encased Electrode Required in the Addition?

Generally, yes, a concrete-encased electrode is likely required for a new building addition, if the addition meets the requirements outlined in NEC Article 250.50. NEC 250.50 states that "all grounding electrodes that are present at each building or structure served shall be bonded together to form the grounding electrode system." This means if you're pouring a new concrete footing for the addition, you should include a Ufer.Here's a more detailed look at considerations: NEC 250.50

This section generally mandates the presence of grounding electrodes that are present at each building to be used, and specifically, 250.52(A)(3) describes the concrete-encased electrode (Ufer).


Bonding

The key here is that all electrodes "present" must be bonded. If the addition has a new footing (with the rebar meeting the Ufer requirements), that is a grounding electrode that is present.

Exceptions

There are very limited exceptions to 250.50, such as explicitly permitting the omission of one or more of the grounding electrodes in 250.52(A)(1) through (A)(7) where only one grounding electrode is present. But, if a concrete-encased electrode is present, that doesn't apply.

How to Connect the Ufer in the Addition to the Existing Service


Connecting the new Ufer ground in the addition's footing to the existing service involves running a grounding electrode conductor (GEC) between the two. Here are the typical steps:1. Expose the Ufer Connection Point

The rebar of the Ufer electrode is required to be accessible or have an accessible connection point. There must be an exposed section of the rebar or a listed terminal (such as a rebar clamp suitable for burial in concrete) to which you can attach the GEC. This is usually stubbed out during the pour.2.

Grounding Electrode Conductor (GEC) Selection

Size the GEC according to NEC Table 250.66. This table bases the GEC size on the size of the ungrounded service-entrance conductors or equivalent area for parallel conductors of the
existing service. Important: The GEC size is determined by the existing service conductors, not the size of any feeder running to the addition (if any).3.

Route the GEC

Run the GEC from the Ufer connection point in the addition to the existing service location. The routing method depends on the specific circumstances and local codes. Options include:


Direct Burial

The GEC can be directly buried, provided it is bare copper or a conductor listed for direct burial. The depth of burial will be dictated by local code.

Conduit

Run the GEC in conduit (PVC, EMT, etc.) for physical protection. This is often preferred, especially where the GEC might be subject to damage.4.

Terminating at the Existing Service

At the existing service, the GEC must terminate at one of the following locations, per NEC 250.24(A)(1):


The Grounded Service Conductor

This is the neutral conductor. The GEC connects to the neutral bus in the service panel or meter enclosure.

The Grounding Electrode Conductor

If there is already a GEC in the existing service, you can connect the new GEC to it. However, ensure the existing GEC is sized large enough to accommodate the combined grounding requirements. If not, you might need to upgrade the existing GEC.


The Equipment Grounding Bus (or Terminal Bar)

This is typically bonded to the enclosure and the neutral.

The Enclosure

If the enclosure is suitably grounded, you can connect the GEC directly to the enclosure.5.

Connections

Use listed connectors appropriate for the size and material of the GEC and the connection point (e.g., compression connectors, set-screw connectors). Ensure connections are tight and secure. Use anti-oxidant joint compound on aluminum conductors.6.

Protection

Protect the GEC from physical damage, especially where it exits the ground or enters the service panel. Use conduit or other appropriate means.

Important Considerations



Inspection

All grounding electrode system installations are subject to inspection. Make sure to comply with local codes and obtain the necessary permits.

Existing Grounding System Adequacy

The connection of the new Ufer could impact the overall grounding system. If the existing grounding system is inadequate, it might need to be upgraded to meet current codes.


Voltage Drop

If a subpanel is installed in the addition, consider the voltage drop in the feeder from the main panel. The sizing of the feeder conductors needs to account for this.*

Professional Advice

Consult with a qualified electrician to ensure the installation complies with all applicable codes and is performed safely. Grounding and bonding are critical for safety and proper system operation.

In summary:
You're almost certainly required to install a Ufer in the new addition. The Ufer then needs to be bonded back to the main service, using an appropriately sized GEC. The size is based off the ungrounded conductors of the main service. The key is that it's one grounding electrode system for the entire building, including the addition. Flag for review

Previous Question Next Question