Question: We had an inspector fail us for a particular situation and I'm trying to find the code reference as they neglected to site it. The inspector is an absolute hard-a$$ and while I believe this is a design issue, I'm inclined to not bother the guy because he's that bad.The building has a back-up generator that essentially serves all of the loads, even the normal lighting. The inspector said that if the utility source is gone and the building is on generator, all emergency & egress lighting must be lit. The only way the lighting control system can determine that there's an issue is when the UL924 devices sense a loss of "normal" power. Since the normal power for lighting is backed up by a generator, it doesn't "know" it's in an emergency condition. The issue arose in areas that have emergency lights but may be locally switched off because of one or another (no occupancy, timed out, turned off on purpose, etc.). The AHJ wants all emergency lighting on in every area, regardless of occupancy, in the event of primary source loss and the generator turning on because it is an emergency situation.I've been trying to find specific code references for this but I can't seem to find anything definitive. How would you achieve it after the lighting system has been installed, programmed, etc.? We installed it as designed so if we spend any money doing this, it's going to be a CO. I just would like a little NEC code help here if it has to go that far.
Okay, this is a tricky situation, and you're right, finding a single, explicitly worded NEC section covering this specific scenario is difficult. The inspector's interpretation is based on a combination of the spirit of emergency lighting requirements and the specific wording of several sections, leaning on the principle of providing reliable emergency illumination during a power outage.Here's a breakdown of the relevant considerations and how to approach this
Key Code Sections & Their Interpretation:
NEC 700.12 (G)(1)
This section discusses the generator, that it shall be started automatically upon failure of the normal source and be capable of supplying power within 10 seconds.
NEC 700.16 (b)
This section talks about emergency illumination shall be provided to permit safe exiting of the building.
NEC 700.16
This is a primary section. It mandates emergency lighting be arranged to provide illumination "automatically" in the event of a power supply failure. The AHJ is likely interpreting "automatically" to mean that all emergency lights should be on, regardless of local control, during a generator-backed outage.
NEC 700.26 Coordination with Fire Alarm System
Coordination is achieved if the emergency lighting system is activated as per a power failure and not dependent of the fire alarm system to enable egress lighting.
The Inspector's Argument (and Why It's Tricky)
The inspector is arguing that the intent of the code is to ensure safe egress under any power failure condition. Even though the generator provides power, it's still an emergency situation. The fact that areas can have emergency lights switched off under normal conditions defeats the purpose of guaranteed emergency lighting. His logic is this:1. Power Failure = Emergency: The activation of the generator signifies a failure of the primary power source, which constitutes an emergency situation per the code.2. Emergency = All Emergency Lights On: During an emergency, all emergency lights must provide automatic illumination for safe egress.3. Local Switching Defeats the Purpose: Allowing local switching to turn off emergency lights defeats the purpose of guaranteed emergency lighting during an emergency.
Why It's Not Explicitly Covered
The NEC typically focuses on the source of power and the transfer to emergency power. It doesn't explicitly dictate how emergency lights are controlled after the transfer. The assumption is that once on emergency power, they remain on. The rise of sophisticated lighting control systems complicates this.
How to Address the Situation (Realistically)
Re-examine the Lighting Control System Programming
This is the first and most likely solution.
Override Function
The ideal solution is to reprogram the lighting control system to have an override function. When the generator is running (detectable via a signal from the generator control system), all emergency lighting circuits are forced to 100% output, bypassing local switches, occupancy sensors, and timers. This is the most compliant solution.2.
Explain and Negotiate (Carefully)
This depends on the inspector's personality.
Document and Explain
Prepare a clear document outlining how the system currently functions, how it complies with the code as you interpret it, and the safety features that are in place.
Propose Alternative Compliance
If a full override is difficult, propose an alternative that still enhances safety. For example, if you can't override all local switches, perhaps you can set a minimum "emergency" light level that can't be dimmed or switched off locally.
Escalate if Necessary (But Carefully)
If the inspector remains inflexible, consider escalating to their supervisor or the local electrical authority. However, be absolutely certain you have a solid understanding of the code and your arguments before escalating.
Practical Considerations
Cost
Be prepared for the cost of reprogramming the lighting control system. This could involve significant programming hours.
Documentation
Keep detailed records of all communications, code interpretations, and modifications made to the system.
Communication
Clearly communicate the situation and proposed solutions to the building owner and the inspector.
Future Design
For future projects, incorporate the emergency lighting override feature into the initial design specifications.
In conclusion: While there is no single perfect NEC section that mandates this interpretation, the inspector's viewpoint is rooted in the core principle of providing guaranteed illumination for safe egress during a power failure. The most effective solution is likely a software update to override switches. Flag for review