Topic: Grounded B Panel

User: Mega8spark, Location: Usa

Asked on: Thursday, October 31, 2024 at 3:13 pm EDT
Answered on: Thursday, March 6, 2025 at 4:42 am EST

Question: I have worked on some grounded B panels in the past but I have never seen this setup and I was curious if it was legal. At the distribution cabinet the grounded leg is landed on a 3 pole main with the other two legs. The breakers for the feeders out of this panel are obviously also 3 pole breakers that have the grounded leg go through them. Then at the panels where these feeders terminate they are 3 phase panels main lug and the grounded leg is tied onto the "B" phase. All of the other setups I have seen in the past have the grounded leg land on a separate buss bar and 2 Pole breakers for the other two legs. Is this setup I ran into legal? I'm only wondering because our job is to replace the feeders to panels and it doesn't seem right from what I've done in the past.

Okay, this is a very unusual and potentially dangerous setup. Let's break down why

Why This Sounds Problematic

1. Switching the Neutral (Grounded Conductor)

The biggest red flag is that you're saying the grounded (neutral) conductor is being switched by the 3-pole breakers.

This is generally a violation of electrical codes.
The grounded conductor is intended to provide a return path for current under normal conditions and must never be interrupted by a switch or breaker except under very specific circumstances (like a simultaneous disconnect of all conductors). Interrupting the neutral can cause dangerous voltage imbalances and equipment damage.2. Connecting the Grounded Conductor to a Phase (B)

Connecting the grounded conductor to the "B" phase in the sub-panels is highly problematic and almost certainly a code violation and safety hazard. Here's why:

Short Circuit

You're essentially creating a dead short between the grounded conductor (which should be near 0V potential with respect to ground) and the "B" phase (which will have a significant voltage with respect to ground, e.g., 120V or 208V). This would trip the breaker
immediately (if it's working correctly) and could damage equipment.

Fault Current Path

Even if it's not tripping, it's a very dangerous fault condition, since a grounded conductor touching a grounded part of the chassis will now have the potential of the "B" phase voltage on it.3.

3-Pole Breakers for 3-Phase Without Neutral

While 3-pole breakers are used for 3-phase circuits, they are typically used when there is no neutral needed. The presence of the grounded conductor in the breaker pole is what raises concern.

Why It's Almost Certainly Illegal and Very Dangerous
NEC (National Electrical Code) Violations

Numerous sections of the NEC would likely be violated by this setup. For example, NEC 200.10(B) generally prohibits the use of a grounded conductor as an equipment grounding conductor, NEC 240.22 prohibits grounded conductors from being interrupted and NEC 300.3(B) requires that all conductors of the same circuit run together.


Safety Hazard

This creates a severe shock hazard. Equipment connected to these sub-panels could become energized to the voltage of the "B" phase relative to ground, making it extremely dangerous to touch. The chance of equipment damage is also extremely high.

What You Should Do
1. Immediate Action



Do not energize this system.
This setup needs to be corrected before anyone is put at risk.2. Consult a Qualified Electrical Engineer or Master Electrician

You absolutely need a qualified professional to assess the situation, diagnose the problem, and design a safe and code-compliant solution. Explain to them what you've observed.3.

Document Everything

Take detailed pictures and notes of the existing wiring configuration before anything is changed. This documentation will be invaluable to the electrical engineer or master electrician who will be correcting the issue.4.

Proper Wiring Practices



Separate Neutral Bus

The grounded (neutral) conductor should land on a dedicated neutral bus bar in both the distribution panel and the sub-panels. This bus bar must be electrically isolated from the enclosure, except for a single bonding connection to ground in the
service entrance or first disconnecting means.

Equipment Grounding

A separate equipment grounding conductor (typically bare or green insulated) must be run with the feeder conductors to each sub-panel. This equipment grounding conductor connects to the metal enclosures and provides a low-impedance path for fault current to return to the source, tripping the breaker.

3-Pole Breakers (If No Neutral Needed)

If the sub-panels are only serving 3-phase loads that
don't require a neutral (like a 3-phase motor), then a standard 3-pole breaker without the neutral is appropriate.

2-Pole Breakers for 3-Phase with a Neutral

If the sub-panels are serving 3-phase loads that do require a neutral (like a 3-phase wye connected system with 120V lighting connected to the neutral), then there should be a 3-pole breaker, and a dedicated neutral bus in each panel.

In Summary


The configuration you described sounds extremely dangerous and almost certainly violates electrical codes. Do not proceed with the feeder replacements until this system has been thoroughly evaluated and corrected by a qualified electrical professional. Your safety and the safety of others depends on it. Flag for review