User: jes25, Location: Midwest
Asked on: Friday, November 1, 2024 at 9:39 am EDT
Answered on: Thursday, March 6, 2025 at 4:43 am EST
Question: This section of the code as shown in the graphic doesn't "feel" right to me. How is it I can have a single EGC entering a cabinet all itself with parallel cables? I can't get over entering an EGC though a metal enclosure without grouping. Could someone explain why this is OK?What if the parallel cables pass though pipe nipples with the single EGC not grouped. Does that change anything?
You're right to question the "feel" of this situation. It's important to remember that electrical installations need to adhere to the National Electrical Code (NEC) to ensure safety and proper functionality. Your concern stems from the fundamental principle of maintaining impedance and providing a reliable low-impedance path for fault current.Let's break down why this might seem okay, and then why it often isn't ideal, and finally how to handle it correctly
Why it Seems Okay (Potentially Misleading):
NEC 250.130 (Single Equipment Grounding Conductor)
This section of the NEC allows a single EGC to be run with multiple circuits/cables under specific conditions. However, the allowance is not intended for parallel conductors. The main purpose here is to add/extend an existing circuit/ground.
NEC 250.122 (Equipment Grounding Conductor Sizing)
This section allows you to size the EGC based on the overcurrent protective device protecting the circuit. However, this only addresses the ampacity of the EGC, not the impedance considerations when running parallel conductors.
Why it's Often Not Ideal (and potentially violates the spirit of the NEC)
Impedance and Fault Current Path
When you parallel conductors, you are reducing impedance, which allows for more fault current. The whole point of paralleling is to get lower overall impedance so that it will have less voltage drop. This means you must size and install the EGC so it can also carry more fault current!
Inductive Reactance
A single EGC running outside the raceway/cable containing the phase conductors will have significantly higher inductive reactance compared to the phase conductors. This higher impedance chokes the fault current flow. The higher the reactance, the less fault current.
Fault Clearing Time
The higher impedance of the EGC path will increase the fault clearing time. The longer the fault exists, the more energy is released, leading to equipment damage, potential fire hazards, and increased risk of electric shock.
Enclosure Heating
Higher impedance in the EGC path means more energy is dissipated in the path itself. This can cause overheating of the enclosure and the EGC itself.
How to Handle Parallel EGCs Correctly (NEC Requirements)
NEC 250.122(F) (Parallel Conductors)
This is the key section. It explicitly states: "Where conductors are installed in parallel in multiple raceways or cables as permitted in 310.10(H), the equipment grounding conductors shall also be installed in parallel. Each equipment grounding conductor shall be sized on the basis of the overcurrent protective device protecting the circuit conductors in the raceway or cable in accordance with Table 250.
122."
In simple terms: For each set of parallel phase conductors in a raceway or cable, you MUST have a full-sized EGC.2. NEC 310.10(H) (Conductors in Parallel)
This section outlines the requirements for paralleling conductors. It's crucial to follow these rules, which include: All parallel conductors must be the same length. All parallel conductors must have the same conductor material. All parallel conductors must have the same insulation type. All parallel conductors must be the same size. All parallel conductors must be terminated in the same manner.3.
Group the EGC with its Phase Conductors
As you mentioned, the EGC must be run in the same raceway or cable as its corresponding phase conductors. This minimizes the impedance of the ground fault path, allowing for a faster and more effective fault clearing.
Answering Your Specific Questions
"How is it I can have a single EGC entering a cabinet all itself with parallel cables?"
You generally cannot do this and be code-compliant when you have parallel conductors. The NEC requires parallel EGCs run with their respective phase conductors. "What if the parallel cables pass though pipe nipples with the single EGC not grouped. Does that change anything?"
Yes, it makes the situation worse. The inductive reactance increases with separation between the phase conductors and the EGC. Running the parallel phase conductors through separate nipples with a single EGC routed separately creates a very high-impedance ground fault path. This is highly undesirable and a code violation.
In Summary
When paralleling conductors, you must parallel the EGCs as well, and each EGC must be run with its corresponding phase conductors in the same raceway or cable. This is crucial for providing a low-impedance fault current path, ensuring proper operation of overcurrent protective devices, and preventing safety hazards.
Always consult the latest edition of the NEC and local electrical codes for specific requirements in your jurisdiction. When in doubt, consult with a qualified electrical engineer or licensed electrician. Flag for review