User: Grouch1980, Location: New York, NY
Asked on: Sunday, November 3, 2024 at 9:46 am EST
Answered on: Thursday, March 6, 2025 at 4:46 am EST
Question: Do SCCR ratings have published time durations? For example, an unfused disconnect switch usually has an SCCR rating of 10kA. Does this SCCR rating also come with a time duration? I never see it on cutsheets... where does one find this? Another example is SCCR ratings of HVAC units... you'll see 5kA... but I never see information on the time associated with that rating.
You're right, you rarely see the time duration specified directly with SCCR ratings, which can be confusing. Here's the breakdown of why and how to find that information
Why Time isn't Explicitly Stated (Usually):
UL 508A (and other relevant standards)
SCCR testing is primarily governed by standards like UL 508A for industrial control panels. These standards dictate the testing methodology. The core of the SCCR test is to ensure the equipment survives the specified fault current for a short but predetermined time.
"Momentary" Rating Assumption
SCCR ratings are generally considered a "momentary" rating. This implies a very short duration, typically measured in cycles of the AC power system (e.g., half-cycle, 1 cycle, 3 cycles). The exact duration is built into the testing procedure defined by the relevant standard, and it's usually not explicitly stated because it's implied by the standard the component is certified to.
Focus on Survival
The key goal of SCCR is that the equipment withstand the fault current for a short period without causing a cascading failure or presenting a safety hazard. The focus is on structural integrity and containment during the fault. The assumption is that the upstream overcurrent protection device (fuse or circuit breaker) will clear the fault quickly enough to prevent long-term damage or fire.
Where to (Potentially) Find Time Duration Information
UL Standard Details (Most Important)
This is the key. If you need to know the specific duration, you must refer to the relevant UL standard that the component was tested under.
Example
If the disconnect switch is rated under UL 98 (Enclosed and Dead-Front Switches), you would need to consult UL 98 to find the specific time duration used in the SCCR testing procedures. If the component is part of a larger assembly (e.g., a UL 508A panel), you'll want to review that standard as well.
Accessing UL Standards
You typically have to purchase access to UL standards. They are not freely available. UL.com is the official source.2.
Manufacturer Documentation (Less Common)
While rare, some manufacturers might provide more detailed SCCR test information in their product datasheets, application notes, or technical bulletins. This is especially true for more sophisticated components or systems where the SCCR performance is a critical selling point. Look for phrases like "Tested per UL XYZ Standard for X cycles."3.
Testing Lab Reports (Rare)
If the manufacturer used an independent testing lab (e.g., Intertek, CSA, etc.), the lab's test report might contain more detailed information, including the exact duration of the SCCR test. However, these reports are usually proprietary and not publicly available.
Example Scenario: UL 508A and Time
UL 508A deals with the SCCR of industrial control panels. The standard defines the testing procedure. It doesn't explicitly say "the test must be done for X milliseconds." Instead, it outlines a test setup and specifies that the device under test must withstand the applied fault current without: Exploding Catching fire Creating an unsafe conditionThe test's duration is implicitly defined by the test procedure and the characteristics of the test circuit used (e.g., the available fault current, the X/R ratio of the test circuit, etc.). It's assumed the upstream protection will clear the fault quickly (within a few cycles).
Key Takeaways
SCCR ratings are inherently "momentary" ratings. The exact time duration is typically implied by the UL or other relevant standard used for testing. You'll need to consult the applicable UL standard to find specific information about the test duration. Focus on selecting overcurrent protection devices that will clear faults quickly enough to protect the equipment. SCCR is about withstanding the fault for a short time while the protection device operates.
In summary: While the time isn't explicitly stated, it is absolutely part of the SCCR rating. It's embedded in the testing standards. Consulting the relevant standard is crucial for understanding the basis of the rating and its limitations. Flag for review