Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Generator installed - shared neutral?

User: cashpoppper, Location: usa

Asked on: Sunday, November 3, 2024 at 7:59 pm EST
Answered on: Thursday, March 6, 2025 at 4:47 am EST

Question: I just paid an electrician to do some work.sub panel in garage, and on the backside of that wall a generator hookup, and back at ground zero an inter-lock kit at the service entrance, and generator supply is ran through the raceways back to service entrance.the bill of materials was cheaper than i thought, and it's from not running a strand of 150ft of wire. Looking in the panel, he didn't pull a 2nd neutral back to the generator. he just tapped into the subpanel's bar.granted the hots and ground are kosher, but shouldn't of he ran a 2nd neutral for the generator circuit?the backup has a floating neutral, and he ran 2 more grounding rods out there next to it 8ft apart 8ft deep, and tied those to the generator's frame as well.i looked through the code book and can't narrow it to any violations, but i thought all 3 had to be broken through a transfer switch? or is that the advantage of the inter-lock it?or maybe this isn't a big deal and i'm trying to make a dangerous mountain out of an ant hill.thanks

Okay, let's break down this scenario. You're right to be questioning this. There are several areas that need careful consideration, and I think you might have a problem, depending on specific circumstances. This is complex, so let's go step-by-step.

Understanding the Components & System Subpanel in Garage

This is your detached garage's electrical distribution point, fed from your main service entrance panel.


Generator Hookup (Back of Garage)

An inlet where you plug in your portable generator.

Interlock Kit (Service Entrance Panel)

A mechanical device installed in your main panel that
prevents the main breaker and the generator breaker from being on simultaneously. This is a key part of a manual transfer system.

Generator Supply Ran Through Raceways

Wires (conductors) from the generator inlet run inside conduit (raceways) back to the service entrance panel.

Generator (Floating Neutral)

This is the important detail. It means the generator's neutral is
not bonded to the generator's frame. The bonding happens at the main service panel.

The Neutral Issue: The Heart of Your Concern


You're right to be concerned about the lack of a dedicated neutral conductor from the generator inlet back to the service entrance panel. Here's why:1. Floating Neutral Generator and Grounding

Your electrician installed two additional grounding rods at the generator location and bonded them to the generator frame. This is crucial with a floating neutral generator.
Because the neutral is floating, the first point of bonding happens at the service panel, which is why he ran a ground wire from the generator hookup back to the service panel.2.

Shared Neutral Risks

By tapping into the subpanel's neutral bar, you are essentially using the neutral conductor that runs from the main panel to the subpanel as the neutral for both the subpanel
and the generator when the generator is running. This can overload the neutral conductor. It also could create voltage imbalances and potentially dangerous situations.3.

Why A Dedicated Neutral is Preferred (and Often Required)

Ideally, the generator would have its own dedicated neutral conductor running all the way back to the service entrance panel. This ensures that the neutral current from the generator doesn't mix with the neutral current from the subpanel's loads.

Is this Code Compliant? It Depends...
NEC and Local Codes

Whether this installation is code-compliant depends on the specific edition of the National Electrical Code (NEC) adopted by your local jurisdiction and any local amendments. The NEC addresses generator installations in Article 702 (Optional Standby Systems) and Article 250 (Grounding and Bonding).

Floating Neutral Considerations (NEC 250.30)

The NEC
permits floating neutral generators but imposes strict requirements for grounding and bonding. The fact that your electrician installed the extra ground rods and bonded them to the generator's frame suggests he was aware of the floating neutral and trying to address it.

HOWEVER
, running the generator neutral through the subpanel's neutral is likely a violation.

The Interlock Kit's Role

The interlock kit is designed to prevent backfeeding. It mechanically ensures that either the utility power
or the generator power can feed your panel, but not both simultaneously. It doesn't solve the neutral problem.

So, What Should You Do?1. Consult a
Different* Licensed Electrician

This is the most crucial step. Get a second opinion from a qualified electrician who is experienced with generator installations and understands the NEC. Show them the installation and explain your concerns. Ask them to specifically evaluate the grounding and neutral wiring for code compliance.2.

Contact Your Local Electrical Inspector

Your local building department or electrical inspector can provide definitive answers regarding code compliance in your area.3.

Review the Generator's Manual

Your generator's manual should provide specific instructions regarding grounding and wiring for various installation scenarios.4.

Consider Running a Dedicated Neutral

The safest and most reliable solution is likely to run a dedicated neutral conductor from the generator inlet back to the service entrance panel. This might require some additional work but would eliminate the shared neutral issue.

In Summary:


While the electrician's intentions might have been good (especially with the additional ground rods), sharing the neutral with the subpanel is likely incorrect and potentially dangerous. A dedicated neutral conductor for the generator circuit is generally preferred and may be required by code. Get a second opinion and consult your local electrical inspector to ensure the installation is safe and compliant. Don't hesitate to do that - your safety and the safety of your home are paramount. Flag for review

Previous Question Next Question