Topic: Service Disconnect(s) location

User: alixenos, Location: Florida

Asked on: Monday, November 4, 2024 at 10:53 am EST
Answered on: Thursday, March 6, 2025 at 4:48 am EST

Question: Hi,I have one service new service that provides is being tapped from a wireway that provides power to two electrical rooms. Picture attached.Should I provide a surge protection for one main or two mains? Why or why not?Thanks.

Okay, let's analyze your situation and determine the best approach for surge protection.

Understanding the Situation Single Source

You have a single wireway feeding
two electrical rooms. This means any surge entering the wireway will likely propagate to both electrical rooms.

New Service Tap

You're adding a new service, which, depending on its nature, could introduce or be vulnerable to surges. More information of the purpose of this new service would be helpful.

Analysis and Recommendations
1. Assess the Risk



Surge Prone Loads

Consider the types of equipment in each electrical room. Are there sensitive electronics like computers, PLCs, data servers, specialized medical equipment, or critical process controllers? These are
very susceptible to damage from surges. Motor drives are also vulnerable. If the load is basic lighting, and general motor loads, surge protection is less critical, but still recommended, as a preventative measure.

External Sources

How exposed is your facility to external surges? Are you in an area prone to lightning strikes? Is your utility power supply known to be unreliable with frequent voltage spikes?2.

Single Main vs. Two Mains



Two Mains

This is the
highly recommended and generally superior approach.

Reasoning



Zone of Protection

Installing surge protection at each main panel provides a
localized zone of protection. It protects everything downstream of that panel.

Redundancy

If one SPD (Surge Protective Device) fails, the other still provides protection.

Reduced Let-Through Voltage

Multiple SPDs in a cascaded arrangement (as described below) can provide better overall surge protection.


Isolation

It limits surges from spreading between the two rooms. Imagine a surge originating within one room (e.g., from a motor starting). A surge protector in that room can help contain it from propagating to the other room.

Single Main (at the Wireway Tap)

While not ideal, you
could consider this if your budget is severely limited, and you're willing to accept a higher risk profile.

Reasoning

It protects any downstream surges, but not from within the electrical rooms.

Cons



Single Point of Failure

If that single SPD fails, both electrical rooms are unprotected.

Limited Protection

A single SPD may not adequately suppress surges that originate within either of the electrical rooms.


Voltage Let-Through

A single SPD might have a higher "let-through voltage" than a cascaded system. Let-through voltage is the voltage level that the SPD allows to pass through to the protected equipment. Lower is better.3.

Cascaded Surge Protection (Best Practice)

The best practice is a cascaded approach:1.

Main SPD

Install a robust SPD at the point where the wireway taps to your new service. This is your first line of defense against external surges. This is typically installed a service entrance.2.

Sub-Panel SPDs

Install SPDs at the main panels in
each electrical room. These provide localized protection and further reduce let-through voltage.3.

Point-of-Use SPDs

For particularly sensitive equipment, consider "point-of-use" SPDs (power strips with surge protection) right at the equipment.4.

Grounding

Make sure your grounding is very good as surge protection diverts surges to ground and a properly installed ground will make this process more effective and safer.

Specific Recommendations



Install SPDs at the Main Panels of BOTH Electrical Rooms.
This is the minimum recommended approach. Consider a Cascaded System

If you have a medium to high risk profile, implement the full cascaded approach with an SPD at the wireway tap
and SPDs in each electrical room.

Choose the Right SPDs

Select SPDs with appropriate Surge Current Capacity (measured in kA). The higher the kA rating, the better the SPD can handle large surges. Also, look for SPDs that are UL 1449 Listed.*

Professional Installation

Have a qualified electrician install the SPDs to ensure proper wiring and grounding.

In summary:
Surge protection at both main panels is highly recommended. If possible, use cascaded surge protection. Flag for review