Topic: Service feeder to 6 disconnect rule

User: Jpflex, Location: Victorville

Asked on: Monday, November 4, 2024 at 12:48 pm EST
Answered on: Thursday, March 6, 2025 at 4:48 am EST

Question: I was wondering that if you met the qualifications to allow yourself to install 6 service disconnects, then if the main building to be served were set for a 200 ampere service and you select a feeder for this, would it make sense to add 5 more service disconnect panels rated also for 200 ampere?It seems this is how it's done but paralleling moree services may increase amps beyond the service feeder

You've hit on a really important point about understanding service disconnects and feeder calculations! Let's break down why installing six 200A service disconnects for a building designed for a 200A service generally doesn't make sense and can violate the NEC

Understanding the Issues

1. Feeder Size vs. Aggregate Disconnect Ratings

This is the heart of the matter. The purpose of the service feeder is to bring the calculated load of the building into the building. You calculate the load based on Article 220. If that load is 200A, that's the size of the feeder you need. Adding six 200A disconnects doesn't change the actual demand of the building. Think of it like a water main. If your house needs a flow rate of 20 gallons per minute, you don't put in six separate taps, each capable of 20 GPM, and expect that the water main won't be overloaded. The water main supplies the total demand.2.

Overcurrent Protection

The overcurrent protection at the
service entrance is designed to protect the feeder conductors from overloads and short circuits based on that feeder's ampacity. If you have a single 200A feeder, the main breaker (or fuses) will be rated at 200A. If you allow six 200 amp breakers to share the 200 amp feeder, and they all draw their full rated current (which they shouldn't, but could), you are exceeding the capacity of the feeder, causing an overload.3.

NEC Violations (Likely)

What you are describing generally violates the NEC.


230.90(A) General

The overcurrent protection must be "suitable for use in accordance with the provisions of this article".

230.90(B) Not Larger Than Service-Entrance Conductors.
This is a hard and fast rule. The overcurrent protection cannot be larger than the ampacity of the service-entrance conductors (the feeder). Feeder Demand Factors and Diversity

Electrical design relies heavily on the concept that not everything runs at its full capacity all the time. That's why we use demand factors and diversity factors in load calculations (Article 220). Installing six 200A disconnects implies you believe the building could potentially draw 1200A, which defeats the entire purpose of using demand factors in the first place.

When Multiple Disconnects Are Allowed (and How They Work)


The NEC does allow multiple service disconnects under certain circumstances (230.71). However, these scenarios are still about serving the calculated load of the building and don't change the fundamental need for proper feeder sizing and overcurrent protection. Six Disconnect Rule (230.71)

The NEC generally allows up to six service disconnects. This is
not an automatic right to install six disconnects, each rated to the entire calculated load.

Large Buildings with Distributed Loads

Imagine a large manufacturing facility. It might have several distinct areas with their own electrical needs. You might have six disconnects serving different sections, but the main feeder to the building is still sized based on the total calculated load of the entire facility, taking into account demand factors. Each disconnect would be sized appropriately for the portion of the load it serves.

Individual Buildings on a Property

If you have a main building and detached garages or accessory structures, each building can have its own service disconnect,
but the feeder to each individual building is still sized based on its calculated load (using Article 220 and demand factors if applicable).

A More Realistic Example


Let's say you have a small office building.1. Load Calculation

You perform a load calculation according to Article 220 and determine the total calculated load to be 150A.2.

Service Feeder

You select a feeder with an ampacity of at least 150A (e.g., #1/0 AWG copper).3.

Service Disconnect

You install
one 150A service disconnect. OR, if desired, you could install up to six smaller service disconnects, as long as the total of their individual loads does not exceed 150A (after demand factors have been applied).

In Summary


You can't simply install multiple service disconnects, each rated to the full service size, and expect it to be safe or compliant with the NEC. The key is that the
feeder to the building must be sized appropriately for the total calculated load* of the building, and the overcurrent protection must be sized to protect that feeder. You can have multiple disconnects as long as the sum of their individual demands (after demand factors are applied) doesn't exceed the feeder capacity.It's always best to consult a qualified electrical engineer or licensed electrician to ensure your electrical system is safe and meets all applicable codes. Flag for review