Question: Im being told I cannot phase a white wire (12/2 romex) going to ac disconnect with no neutral required but i understand that as long as is cable,permanently marked with like phase marker we should be good ? 200.7
You are correct in your understanding. According to NEC 200.7, a white or gray wire in a cable can be re-identified as an ungrounded (hot) conductor under specific conditions: Cable Assemblies
This applies specifically to cables (like Romex/NM-B).
Permanent Marking
The white wire must be permanently re-identified to indicate its use as an ungrounded conductor. This is typically done using black or red tape, paint, or other approved means. The marking must encircle the wire and be readily visible.
At Points of Termination and Connection
The re-identification must occur at each point where the conductor is visible and accessible, such as inside the AC disconnect and at the circuit breaker panel.
In your specific scenario (12/2 Romex to AC Disconnect - no neutral needed)
Identify
At both the AC disconnect and the breaker panel, permanently mark the white wire with black or red tape to indicate it's being used as a hot conductor.2.
Connect
Connect the now re-identified white wire as one of the hot legs to the AC disconnect. Connect the black wire to the other hot leg.3.
Ground
Ensure the equipment grounding conductor (bare copper) is properly connected in both the disconnect and the panel.
Important Considerations
Local Amendments
Always check for local amendments to the NEC. Some jurisdictions may have stricter rules or interpretations.
Inspector Approval
It's always a good idea to discuss this with your electrical inspector beforehand to ensure they're on the same page and to avoid any surprises during inspection.
Best Practice
While code-compliant, some electricians prefer to use black or colored conductors for hot wires to avoid any confusion. However, using the re-identification method is perfectly acceptable when done correctly.
Qualified Personnel
This work should be performed by a qualified electrician who understands the NEC and local codes.
Clarity You did not mention where the white wire is being used as a hot/ungrounded conductor. Is this at the AC disconnect only and properly used as a grounded conductor at the panel/breaker?In summary, you are correct in your understanding of NEC 200.7. As long as you properly re-identify the white wire at all termination points, it's acceptable to use it as an ungrounded conductor in your AC disconnect setup (assuming no neutral is required). Flag for review