Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: ATS sizing

User: cppoly, Location: New York

Asked on: Monday, November 4, 2024 at 4:04 pm EST
Answered on: Thursday, March 6, 2025 at 4:49 am EST

Question: If you have a 100 amp continuous load, is a 100 amp ATS sufficient or is the rating of the ATS required to be sized at 125%?

The rating of the Automatic Transfer Switch (ATS) is required to be sized at 125% of the continuous load, as per NEC Article 700.5(B) for emergency systems.Therefore, for a 100 amp continuous load, a 100 amp ATS is not sufficient. You would need an ATS rated for at least 125 amps (100 amps 1.25 = 125 amps).

Why 125%?

The 125% requirement is in place to prevent overheating and potential failure of the ATS when subjected to a continuous load. Continuous load, by definition, is a load that operates at its maximum current for three hours or more.

Important Considerations



NEC Article 700.5(B)

This section of the National Electrical Code specifically addresses sizing emergency system equipment.

Continuous Load Definition

Understand the definition of a continuous load. If the load isn't continuous, the 125% rule might not apply, but it's always best to err on the side of safety.


Local Codes and Regulations

Always check with your local electrical inspector or authority having jurisdiction (AHJ) for any specific requirements in your area. Some local codes may have stricter requirements than the NEC.*

Manufacturer's Specifications

Consult the ATS manufacturer's specifications for their recommendations on sizing.

In summary, to safely and code-compliantly handle a 100 amp continuous load, you need an ATS with a minimum rating of 125 amps.
Flag for review

Previous Question Next Question