User: cola, Location: 620 Tennessee Street
Asked on: Monday, November 4, 2024 at 6:44 pm EST
Answered on: Thursday, March 6, 2025 at 4:49 am EST
Question: I have a Eaton 400 amp HP404040SHF W/split mains in Riverside County California.I'm using the second sub breaker @ 150 amp. Back feed only from solar and 15kw batters. (grid tied)230.71(B)In general, a service should have a single disconnecting means.However, one set of service entrance conductors is permitted tosupply two to six service disconnecting means in lieu of a singlemain disconnect. Both single-occupancy and multiply-occupancybuildings can be provided with one main service disconnect or upto six main disconnects for each set of service-entrance conductors.Conductors from renewable energy sources, such as photovoltaicsystems and wind generators, are feeder conductors.Would this still be a non-compliant install.
Okay, let's break down the situation and the relevant code to determine if your installation is compliant.
Understanding the Setup Eaton HP404040SHF
This is a 400 amp panel with split mains. That means it likely has two main breakers, each rated for a portion of the 400A service (e.g., two 200A breakers).
Riverside County, California
Important because California adopts the NEC with amendments.
150A Sub-breaker (Backfed)
You're using one of the sub-breakers in the panel to backfeed power from your solar and battery system. This is grid-tied.
230.71(B)
This section of the NEC is the core issue. It discusses the number of service disconnects allowed.
The Key Issue: Backfeeding and Service Disconnects
The problem is that 230.71(B) specifically addresses service disconnects. Your solar backfeed is not a service. It is a feeder circuit. Feeder vs. Service
The code distinguishes between service conductors and feeder conductors. Service conductors bring power from the utility to the service disconnect(s). Feeder conductors distribute power from the service disconnect(s) to other panels or loads. Your solar and battery system act as a feeder.
Why it might be non-compliant
Here's where the issue arises:1. Not a Service Disconnect
The 150A breaker you're using for the solar backfeed is a sub-breaker in the panel, not a service disconnect. 230.71(B) primarily concerns the number of service disconnects allowed.2.
Intersolar Rule
Some AHJs will use the intersolar rule, that would be 120% of the bus bar rating. The two main breakers on top, plus the back fed breaker cannot exceed this amount. In this case 400 amps X 120% = 480amps. If the two top breakers are 200 amps each, plus the 150 amp back fed, this would be 550 amps.
Requirements for Solar Backfeed in a Panel
NEC addresses backfeeding solar into panels and it requires the use of specific rules about breaker placement and sizing. 120% Rule (705.12(B)(2)(3)(a))
This is a critical rule when backfeeding power into a panel. The sum of the overcurrent protection (breaker) for the main supply AND the overcurrent protection for the backfed source cannot exceed 120% of the busbar rating of the panel. In your case, a 400A busbar panel allows a maximum of 480A (400A 1.20).*
Breaker Placement
The backfed breaker needs to be located at the opposite end of the busbar from the main breaker to minimize current concentration.
How to Make the System Compliant (Potential Solutions)
Assuming the 120% rule has been violated, here are a few options, although consulting with a qualified electrician is essential:1. Reduce the back feed breaker Size
If the 120% rule is violated, reducing the size of the breaker used for backfeeding the solar can bring the system into compliance. This would limit the amount of power from the solar/battery system.2.
Line side tap
Line side taps are generally used on the load side of the meter. This is a preferred method of connecting to the grid.3.
Use a Sub Panel
Adding a new panel for all branch circuits and moving one of the main breakers to the new panel.
Crucial Steps1. Consult with a Qualified Electrician
This is absolutely essential. A licensed electrician familiar with NEC and local codes in Riverside County can assess your specific setup and provide a compliant solution.2.
Check with the AHJ (Authority Having Jurisdiction)
Your local building department or electrical inspector has the final say on code interpretation. Get their feedback on your proposed solution.3.
Review Panel Labeling
Ensure your panel is correctly labeled to indicate the presence of the backfed solar source.
Disclaimer: I am an AI chatbot and cannot provide legally binding electrical advice. This information is for educational purposes only. Consult with qualified professionals for your specific situation. Electrical work can be dangerous, and improper installations can lead to fire, injury, or death. Flag for review